Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Screen is black, nothing lights up, SMX1500RM2U

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Re: Screen is black, nothing lights up, SMX1500RM2U
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5027
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
ttan_2017_apc
Crewman ttan_2017_apc
Crewman

Posted: ‎2021-06-30 08:53 PM

0 Likes
7
707
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 08:53 PM

Screen is black, nothing lights up, SMX1500RM2U

This was originally posted on APC forums on 9/28/2016


Hi all,

I have a problem using a SMX1500RM2U. I used to get it online two years ago which worked fine. However, we do not use it since then without charging or doing anything. Recently, we would like to put it back to work, but the module does not respond anything. We plug it to the wall and there is a click sound at the time we plug it in. When pressing the start button, no screen and light come on, just a sound like when it can start. We also check the output voltage which is about 19.5 Vac, the output voltage to the battery which is 8 Vdc and the battery voltage, 2.5 Vdc. I reset the over-current button at the back of the UPS as well, but to no avail. Any comment and help would be appreciated. 

Thanks so much,

Tan

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
ttan_2017_apc
Crewman ttan_2017_apc
Crewman

Posted: ‎2021-06-30 08:54 PM

0 Likes
0
704
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 08:54 PM

This was originally posted on APC forums on 10/7/2016


Just want to update if anyone has the same problem.After changing the battery and reset the date of battery installation, the UPS works fine and the alert disappears.

The problem I have at the first place is that when putting the start button, no light and screen show up. The only thing I can notice is a click sound. What I do is to remove the cover and find that one of the wire connections is loose. I fix it and later turn it on. The UPS is still having an alert showing "Connect Battery". I decide to replace the battery and finally it works great.

 My UPS model is SMX1500RM2U.

Thanks so much, guys!

See Answer In Context

Reply
Replies 7
UnexpectedBill_apc
Captain UnexpectedBill_apc
Captain

Posted: ‎2021-06-30 08:53 PM

0 Likes
0
702
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 08:53 PM

This was originally posted on APC forums on 9/29/2016


I think it's still true that the newer Microlink UPS models (such as your SMX1500RM2U) must have a good battery in place or they will not start up. One thing is for certain: after two years of sitting, the batteries in your UPS are almost certainly dead beyond recovery.

Reply
ttan_2017_apc
Crewman ttan_2017_apc
Crewman

Posted: ‎2021-06-30 08:54 PM

0 Likes
0
702
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 08:54 PM

This was originally posted on APC forums on 9/29/2016


Hi William,

Thanks so much for your reply. I will buy a new battery and see if it can work. 

Reply
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 08:54 PM

0 Likes
0
702
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 08:54 PM

This was originally posted on APC forums on 9/29/2016


On my SMX1500RM2U, the display will respond to button presses even without a battery if the unit is plugged in.

Reply
UnexpectedBill_apc
Captain UnexpectedBill_apc
Captain

Posted: ‎2021-06-30 08:54 PM

0 Likes
0
702
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 08:54 PM

This was originally posted on APC forums on 9/30/2016


I just tested a long-dormant, battery disconnected SMT750 to see what it'd do. Indeed it does power up without a battery attached, though it took a few tries to get the display to light up and respond.

The original poster might be best advised to try a battery from another unit if they have one.

Reply
ttan_2017_apc
Crewman ttan_2017_apc
Crewman

Posted: ‎2021-06-30 08:54 PM

0 Likes
0
701
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 08:54 PM

This was originally posted on APC forums on 9/30/2016


Thanks so much for your response, Voidstar.

Reply
ttan_2017_apc
Crewman ttan_2017_apc
Crewman

Posted: ‎2021-06-30 08:54 PM

0 Likes
0
700
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 08:54 PM

This was originally posted on APC forums on 9/30/2016


Hi William,

Thanks so much, it turned out to be the loose connection inside the main board. I found it after remove the side cover. When plugging it properly, the screen shows up and I still have some troubles seeing the alarm from "Connect battery" which I think I need to replace the battery. 

I really appreciate your help. Thanks!

Have a good weekend!

Reply
ttan_2017_apc
Crewman ttan_2017_apc
Crewman

Posted: ‎2021-06-30 08:54 PM

0 Likes
0
705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-06-30 08:54 PM

This was originally posted on APC forums on 10/7/2016


Just want to update if anyone has the same problem.After changing the battery and reset the date of battery installation, the UPS works fine and the alert disappears.

The problem I have at the first place is that when putting the start button, no light and screen show up. The only thing I can notice is a click sound. What I do is to remove the cover and find that one of the wire connections is loose. I fix it and later turn it on. The UPS is still having an alert showing "Connect Battery". I decide to replace the battery and finally it works great.

 My UPS model is SMX1500RM2U.

Thanks so much, guys!

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc