Schneider Easy UPS 3L / 3M - is it truly modular?

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Haris1389
Cadet
0 Likes
2
328

Schneider Easy UPS 3L / 3M - is it truly modular?

Hi all,

 

My first post in this forum..

 

I am an Electrical engineer working on a hospital project,

 

We are in process of procurement of Modular UPS for one of our projects. Can someone guide (better if from Schneider) whether the Easy UPS range is truly modular or not? also is it scalable by adding modules? can't seem to find this in the brochures/literatures or even manuals

 

Thanks!

Tags (1)
2 Replies 2
al_buffington
Lieutenant JG Lieutenant JG
Lieutenant JG
0 Likes
1
311

Re: Schneider Easy UPS 3L / 3M - is it truly modular?

Hi,

 

The Easy UPS is not a modular system. It's also not scalable unless you were to add additional systems and place them in parallel. For a modular and scalable solution you would need to look at something like the Symmetra PX or Galaxy VL.  There are some other systems which are modular but not scalable. I hope this answers your question. 

Tags (1)
Haris1389
Cadet
0 Likes
0
295

Re: Schneider Easy UPS 3L / 3M - is it truly modular?

Thanks for the feedback!

Tags (1)