During the installation of additional battery packs a 'Scheduled Runtime Calibration' was selected 'Yes' via the LCD. How do we cancel the scheduled runtime calibration? Would this runtime calibration turn off the outlets; cut power to the equipment?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:37 AM . Last Modified: 2024-03-07 10:55 PM
Hi,
A calibration test will not cut power to the load. The test switches the UPS to battery and runs until the battery is low. It will then switch back to AC. To stop the test go to test and diags - calibration.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:37 AM . Last Modified: 2024-03-07 10:55 PM
Hi,
A calibration test will not cut power to the load. The test switches the UPS to battery and runs until the battery is low. It will then switch back to AC. To stop the test go to test and diags - calibration.