SYMIM5 RIM Fault with Data Dumps

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SYMIM5 RIM Fault with Data Dumps
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:35 AM . Last Modified: ‎2024-03-12 03:38 AM

0 Likes
4
1159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:35 AM . Last Modified: ‎2024-03-12 03:38 AM

SYMIM5 RIM Fault with Data Dumps

Hi All,

First, thanks for the great forum for us to post questions.  I have a Symmetra LX and have two questions after we have had an error on the system.

Question 1

In our Main IM slot (lower slot) SYMIM5 is is operational but is labled a SYMIM5Q, I can find no documentation on what the different is between a normal SYMIM5 and the 5Q version?

Question 2

Our system recorded a fault in the RIM (It is labeled SYMIM5) and received the following data :

FW REV: 513,Slv : 602

H/W Rev:

SN: Qd1023360096

Mfg Date:  06/03/10

RIM Status Dump :

R 05 0000 0000 0000

0000 0000 E0Eb 806B

29F7E0EB  1E07D2AD

We have two other spares RIMS that we tried to replace that have exact same firmware and get a similar error as follows:

spare unit 1

FW REV: 513,Slv : 602

RIM Status Dump :

R 05 0000 0000 0000

0000 0000 E0EB 806B

29F7E4EB  1E07D2AD

The underlined 4 and 7 are only differance in the DUMP's.

All three RIM units (including the original that has been working for years) have same repeatable failure when plugged into the system.

When any of the RIM units are installed they work for approximately 90 seconds then fail.  Here is the error message :

v1

Name     : APC1

Location : Server Room

Contact  : David

http://APC1.compro.net

http://10.10.10.222

Serial # : ZA0653003989

Device Ser #: QQ1020260075

Date: 02/19/2014

Time: 11:05:37

Code: 0x0205

Critical - UPS: Redundant Intelligence Module failure.

I am starting to suspect it is actually the IM and not the RIM, any help ????

Thanks



Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:35 AM . Last Modified: ‎2024-03-12 03:38 AM

0 Likes
0
1157
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:35 AM . Last Modified: ‎2024-03-12 03:38 AM

HI All,

Problem solved and we are back to normal working status.  The error we received consistently claimed the RIM was at fault.  We used our spare RIM parts and the error were the same on each RIM.  We took the system into Maintenance Mode via the switch and moved the MIM into the RIM and put our original failed RIM back into the lower slot, making it the master.  Interestingly, now the fault moved to the RIM.  At this point we have either a bad RIM slot or a bad MIM (original) that has lost communications but will operated as a MIM without a RIM installed.  We removed the suspect SIMIM5 and placed our two spares SYMim5's into the slots and all errors are cleared.

The confusion was that in our original setup the fault report (and red light led's)  were always in the RIM when in fact is appears the MIM lost communications resulting in the same error.  Just FYI on how we resolved the unique failure.

Thanks to all for you help in supporting our question.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:35 AM . Last Modified: ‎2024-03-12 03:38 AM

0 Likes
0
1157
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:35 AM . Last Modified: ‎2024-03-12 03:38 AM

Hi there, the "Q" at the end of your part number , together with the "QQ" in the serial number , denote that this is a "refurbished" item from APC stock....here on the west coast we sometimes get such items out of the Los Angeles distribution center. If you open a tech support case with APC they can look at the hex code in the status dump and help determine what the failures relate to. Good luck !

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:35 AM . Last Modified: ‎2024-03-12 03:38 AM

0 Likes
0
1157
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:35 AM . Last Modified: ‎2024-03-12 03:38 AM

I agree tech support can go over this in more detail via phone or maybe email but I'll provide what I know.

1.) As Battman indicated, a Q at the end of a SKU (and you'll also see a Q in the second character of its serial number - like what you pasted from the email alert) indicates a part is refurbished. We typically send these out for warranty replacements after the initial 30 days of warranty. Did you have IM replaced under warranty at some point for something else in 2010ish?

2.) On the second issue, after R 05 in the raw status - there are the five groups of '0000' and this is where faults would be displayed. So, what you posted indicates at the precise time you extracted the raw status, the module was not likely in a fault state.

What I would do is:

  • Provide us event.txt from the Network Management Card -> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA... - this will be helpful to give us a little more background.
  • If you're able to, you can see if you can catch the raw status dump while the IM is faulting if it's coming and going. We could see what it is reporting for a specific fault.
  • Another option to verify which module is showing fault, which I have no reason based on what you've provided so far, is not the RIM (versus MIM), is to swap the slots they are in to verify then the fault lies with the MIM in the bottom slot once you move it. To do this, please review this article first -> Proper Procedure for Replacing the Intelligence Modules in any Single-phase Symmetra UPS | FAQs | Sc...

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:35 AM . Last Modified: ‎2024-03-12 03:38 AM

0 Likes
0
1157
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:35 AM . Last Modified: ‎2024-03-12 03:38 AM

Thank you for your reply.  I now understand the difference, as I just did not see a difference in the parts, but make perfect sense to identify  new or refurbished units.  I see in our activity log indeed we did send a unit into APC for repair and this is the unit we received back a few years ago.   

Thanks  for the help....

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:35 AM . Last Modified: ‎2024-03-12 03:38 AM

0 Likes
0
1158
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:35 AM . Last Modified: ‎2024-03-12 03:38 AM

HI All,

Problem solved and we are back to normal working status.  The error we received consistently claimed the RIM was at fault.  We used our spare RIM parts and the error were the same on each RIM.  We took the system into Maintenance Mode via the switch and moved the MIM into the RIM and put our original failed RIM back into the lower slot, making it the master.  Interestingly, now the fault moved to the RIM.  At this point we have either a bad RIM slot or a bad MIM (original) that has lost communications but will operated as a MIM without a RIM installed.  We removed the suspect SIMIM5 and placed our two spares SYMim5's into the slots and all errors are cleared.

The confusion was that in our original setup the fault report (and red light led's)  were always in the RIM when in fact is appears the MIM lost communications resulting in the same error.  Just FYI on how we resolved the unique failure.

Thanks to all for you help in supporting our question.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of