Dear support,
In continuation of topic SY96K160H & Modbus/ dry relay contacts integration, please tell me where the integrated relay and dry contacts are physically located in SY96K160H, the configuration and of which I can see through the web interface of the built-in monitoring and control card 0G-9354 (0G-9354A)?
Very thanks for the support.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-11-22 07:06 AM
Dear community,
Fortunately, I can answer my own question by testing it in practice. At the very bottom of the Power Frame SY96K160H are:
Below are photos of a real UPS with connected and configured dry contacts for monitoring the critical alarm status of UPS cooling air conditioners.

Very thanks for the support.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-11-22 07:06 AM
Dear community,
Fortunately, I can answer my own question by testing it in practice. At the very bottom of the Power Frame SY96K160H are:
Below are photos of a real UPS with connected and configured dry contacts for monitoring the critical alarm status of UPS cooling air conditioners.

Very thanks for the support.