SY96K160H & Modbus/ dry relay contacts integration

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SY96K160H & Modbus/ dry relay contacts integration
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 03:42 AM . Last Modified: ‎2024-03-19 01:40 AM

0 Likes
4
1125
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:42 AM . Last Modified: ‎2024-03-19 01:40 AM

SY96K160H & Modbus/ dry relay contacts integration

Hello,

There are a few SY96K160Hs in LANs, but it is needed to monitor the system via dry relay contacts and RS-485 ( modbus protocol).

So I wonder,
1) if there is a card to provide some kind of signals and what signals we'll get - please send a table or a link?
2) If we use AP92200 ( ISXM) with modbaus integration (APPLICATION NOTE #70) , then what signals excactly we get?
3) If we install AP9619 in SY96K160H, then what signals we'll have from output contacts?
4) Is it possible to get RS-485 connection directly from SY96K160H

Any other ideas or hints are highly welcomed.
Thank you in advance.

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-26 03:42 AM . Last Modified: ‎2024-03-19 01:40 AM

0 Likes
0
1125
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:42 AM . Last Modified: ‎2024-03-19 01:40 AM

As an addendum to my last message, the UPS modbus map for all UPSes is in this appnote:

[UPS Modbus Map|http://www.apcmedia.com/salestools/JRUK-63SRXH_R2_EN.pdf]

Modular distribution, if purchased with the PX2, is also available via Modbus, however I don't see a Modbus map listed on the web. Feel free to message me if you need any help with modular distribution on Modbus.

The built-in dry contacts on the PX2 can be triggered by these UPS conditions:
* Any UPS Warning Alarm
* Any UPS Critical Alarm
* UPS On Battery
* On Battery & Low Battery
* Replace Battery
* System in Bypass
* Switchgear Alarm
* UPS is Overloaded
* UPS Output OFF
* UPS Load Alarm
* UPS Redundancy Alarm
* UPS Runtime Alarm

Additionally, if you have modular distribution, you can trigger on:
* Maximum/high/low/minimum module/subfeed/system current
* Module breaker position
* Maximum/high/low/minimum subfeed/system voltage
* Subfeed/system frequency

If the UPS has environmental monitoring (I'm not sure if this comes with it), then temperature and humidity probes can trigger the contacts as well.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-26 03:42 AM . Last Modified: ‎2024-03-19 01:40 AM

0 Likes
0
1125
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:42 AM . Last Modified: ‎2024-03-19 01:40 AM

Hi,

It doesn't look like the MegaWatt is capable of using smart slot cards.

However, if you can, there is a Modbus/JBus card:

http://www.apc.com/resource/include/techspec_index.cfm?base_sku=AP9622

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 03:42 AM . Last Modified: ‎2024-03-19 01:40 AM

0 Likes
0
1125
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:42 AM . Last Modified: ‎2024-03-19 01:40 AM

Thank you,
Why it doesn't look like the SYPX 2 is capable of using Smart slot cards?
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SY96K160H
The web site says that the UPS includes Web/SNMP Management Card

I wonder what data excactly the card ( AP9622) will send from the particular UPS ( PX-2)?
Why not to use ISXM or ISXC?

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-26 03:42 AM . Last Modified: ‎2024-03-19 01:40 AM

0 Likes
0
1125
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:42 AM . Last Modified: ‎2024-03-19 01:40 AM

PX2s have dry contacts that can trigger on a wide range of conditions, from various output voltage and current conditions on subfeeds, modular distribution breakers, as well as the UPS conditions. The Web/SNMP module firmware also enables ISX Manager to expose much of this information over Modbus.

I apologies for being vague on the exact capabilities... I'll know more on Tuesday when I go back to work.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-26 03:42 AM . Last Modified: ‎2024-03-19 01:40 AM

0 Likes
0
1126
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 03:42 AM . Last Modified: ‎2024-03-19 01:40 AM

As an addendum to my last message, the UPS modbus map for all UPSes is in this appnote:

[UPS Modbus Map|http://www.apcmedia.com/salestools/JRUK-63SRXH_R2_EN.pdf]

Modular distribution, if purchased with the PX2, is also available via Modbus, however I don't see a Modbus map listed on the web. Feel free to message me if you need any help with modular distribution on Modbus.

The built-in dry contacts on the PX2 can be triggered by these UPS conditions:
* Any UPS Warning Alarm
* Any UPS Critical Alarm
* UPS On Battery
* On Battery & Low Battery
* Replace Battery
* System in Bypass
* Switchgear Alarm
* UPS is Overloaded
* UPS Output OFF
* UPS Load Alarm
* UPS Redundancy Alarm
* UPS Runtime Alarm

Additionally, if you have modular distribution, you can trigger on:
* Maximum/high/low/minimum module/subfeed/system current
* Module breaker position
* Maximum/high/low/minimum subfeed/system voltage
* Subfeed/system frequency

If the UPS has environmental monitoring (I'm not sure if this comes with it), then temperature and humidity probes can trigger the contacts as well.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore