SUVTP30KH+AP9619 ignores S, @000, KK and ZZ commands over serial

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUVTP30KH+AP9619 ignores S, @000, KK and ZZ commands over serial
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:20 AM . Last Modified: ‎2024-03-06 01:52 AM

0 Likes
10
1697
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:20 AM . Last Modified: ‎2024-03-06 01:52 AM

SUVTP30KH+AP9619 ignores S, @000, KK and ZZ commands over serial

I use dozens of APC SmartUPSs with serial cables and apcupsd. On power outage notification from the UPS, after running on battery for 10 minutes, the PC initiates shutdown. Just before halt, it sends the "S" command to the UPS, which tells the UPS to cut power to load and watch the utility line. When utility power returns, it pulls up the load and the PC boots. (apcupsd checks if the response to "S" is "OK" or "*" --- if not, it tries stronger measures @000, KK and ZZ.) No problem there.

I want exactly the same behavior from a 30kVA online SmartUPS SUVTP30KH. It has a serial port but also a AP9619 installed. I removed the AP9619. Then I connected the serial port with APC-approved cable to a PC. I used apctest to enter into serial communication with the UPS, and verified that the reply to "Y" is "SM" and "^A" return the UPS's model string. Now I cut utility power, and typed "S", but the response was "NA". Then I typed "@000" (with two seconds of pause between characters) and got "NANANA". For "KK" and "ZZ" the response was "NANA".

Another curious observation: if I reconnect the AP9619 and use a browser to log on to the Web server on the AP9619 and navigate to UPS -> Configuration -> Shutdown, the first line on that frame is "Shutdown Mode: Never". Also, if I navigate to Control, the last line in the frame is "Note: UPS is configured to never shutdown. No shutdown control commands will initiate."

I am ok with using either serial or the AP9619 (with PCnet or SNMP). But I am not able to get the specified behavior for our needs:
* Pretend we have only one PC powered by the UP.
* Do not wait for low battery. (We power down because our ACs stop, even if we have batteries in good shape.)
* After running on battery for 10 minutes, the PC must initiate shutdown (it does at present, with serial and SNMP).
* Shortly after the PC completes shutdown, the UPS must cut power to the PC. This is simply not happening at present. Not with PCnet, not with SNMP, not with serial!

APC's own documentation and support leave a lot to be desired. Any guidance, beginning with a factory-reset AP9619, or the serial port, will be strongly appreciated.

Message was edited by: 545ad3

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • ap9619
  • killpower
  • shutdown
  • suvtp30kh
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:20 AM . Last Modified: ‎2024-03-06 01:51 AM

0 Likes
0
1697
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:20 AM . Last Modified: ‎2024-03-06 01:51 AM

voidstar wrote:
it's a feature accessible through the front panel display to disallow shutdown via UPSLink. Looking at [the manual|http://www.apcmedia.com/salestools/AHIE-83NAUF_R0_EN.pdf], I would guess it's under setup->shutdown.
I left no stone unturned before asking for help. On the front panel of the UPS, that menu path takes you to precisely the same menu as through the Web interface to the NMC ("upshutdn.htm") --- in that menu, you get to choose Low Battery Duration, Shutdown Delay, Basic Signaling Shutdown, Sleep Time, End of Shutdown
Minimum Battery Capacity, and Return Delay. At the top of the (Web page) panel is the emphatic announcement: "Shutdown Mode: Never" without any option to change said shutdown mode.

The world has indeed come to the point where the manufacturer of such a gadget does not have the human resources to send back one email of the form: "We have checked that your UPS, serial number X123, firmware revision PQR dated YY/MM is hardwired to never shutdown. No flashing of firmware or configuration of software can achieve what you want. The UPS will not obey killpower commands. You can only switch the load off manually from the front panel or the Web interface." OR "Here is a link to a firmware. Please flash it and you will be able to change the shutdown mode to what you want." APC India has been playing phone and email tag for over a month now without any real action. I can understand why: they do not have a single person capable of even understanding the setup and the goal.

This is a very bad state of affairs. I have already informed our IS organization about the undesirability of APC hardware. We have several hundred small and large UPSs on our premises, so turning to another brand will be a significant change for us. But probably worthwhile.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-01 01:20 AM . Last Modified: ‎2024-03-06 01:52 AM

0 Likes
0
1697
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:20 AM . Last Modified: ‎2024-03-06 01:52 AM

You're right -- it's not in the local display. I asked again and the UPS engineer clarified it was only available on the local service port, which is a separate serial port on the UPS. It sounds like you haven't had a good experience with APC's tech support, but it might be worth calling them again and asking how to change the "secure shutdown mode" via the local service port.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:20 AM . Last Modified: ‎2024-03-06 01:52 AM

0 Likes
0
1697
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:20 AM . Last Modified: ‎2024-03-06 01:52 AM

voidstar wrote:
You're right -- it's not in the local display. I asked again and the UPS engineer clarified it was only available on the local service port, which is a separate serial port on the UPS. It sounds like you haven't had a good experience with APC's tech support, but it might be worth calling them again and asking how to change the "secure shutdown mode" via the local service port.
Yes, I have noticed that other "serial-looking" port on the front panel. My best bet remains to get the above information through this forum and try it out myself. A Web search was unfruitful. Can I run minicom or hyperterm on this port like on the smart serial port?

Is it impolite to ask for direct access to and instructions from the APC engineer you refer to here?

Message was edited by: 545ad3

Message was edited by: 545ad3

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-01 01:20 AM . Last Modified: ‎2024-03-06 01:51 AM

0 Likes
0
1697
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:20 AM . Last Modified: ‎2024-03-06 01:51 AM

Sent details via private message.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-01 01:20 AM . Last Modified: ‎2024-03-06 01:51 AM

0 Likes
0
1697
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:20 AM . Last Modified: ‎2024-03-06 01:51 AM

Changing the shutdown mode via the local service port solved the customer's problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:20 AM . Last Modified: ‎2024-03-06 01:51 AM

0 Likes
0
1697
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:20 AM . Last Modified: ‎2024-03-06 01:51 AM

hello. first off, just let me say I am not familiar with this UPS - I am familiar with the single phase smart UPS and the network management cards. what version of AOS and application (sumx) do you have on this AP9619?

what i'd recommend is that you reset the UPS to defaults via the NMC which should be under the Administration Tab->General->Reset/Reboot->Reset Only and choose UPS to defaults. If you need to reset the NMC to defaults, on that same screen, you can do reset to defaults and then specify if you want to reset TCP/IP settings too or exclude those if you don't want to reset them.

have you tried APC powerchute network shutdown (PCNS) at all? i am familiar with what apcupsd is but i can't say I have actually used and installed it.

it seems like you should be able to just use this and the network management card and tell PCNS to shutdown the PC after the UPS has been on battery after 10 minutes. then PCNS can be configured to turn the UPS off after it is done turning off.

this might help a bit to tell you how things are designed to happen with PCNS:

http://www.apcmedia.com/salestools/TDOY-5UQVBV_R3_EN.pdf

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:20 AM . Last Modified: ‎2024-03-06 01:51 AM

0 Likes
0
1697
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:20 AM . Last Modified: ‎2024-03-06 01:51 AM

I have a really simple question for APC, but it's proving unbelievably difficult to extricate a straight technical answer. All details about my UPS are known to them (including serial number), and it is under first year manufacturer's warranty. Does this UPS support powering down loads after PCNS shutdown? If yes, why+how is my configuration wrong? If no, is there a way to flash a different firmware to get killpower working? Why is it unreasonable to expect a prompt answer? Chances are, the designers of that that UPS are still alive, and they may even still be APC/Schnieder employees. But the representatives of APC in India is absolutely atrocious. They don't have the smallest clue. Seems APC has only sales people in India.


UPS manufacture date: 12/2010
UPS firmware 909.0501.I
PCNS version 3.0.1

NMC Model Number: AP9619
Hardware Revision: A10
Manufacture Date: 12/21/2010

Application Module
Name: sumx
Version: v3.7.2
Date: 02/02/2010
Time: 19:08:16

APC OS (AOS)
Name: aos
Version: v3.7.3
Date: 02/02/2010
Time: 17:05:14

Message was edited by: 545ad3

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-01 01:20 AM . Last Modified: ‎2024-03-06 01:51 AM

0 Likes
0
1697
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:20 AM . Last Modified: ‎2024-03-06 01:51 AM

>
I have a really simple question for APC, but it's proving unbelievably difficult to extricate a straight technical answer. All details about my UPS are known to them (including serial number), and it is under first year manufacturer's warranty. Does this UPS support powering down loads after PCNS shutdown?
>

Yes, all SmartUPS do (probably BackUPS with USB comms as well). If you want to test this, unplug the UPS and then command the NMC to reboot it. It should turn off, wait for AC, and then turn back on when you plug the power cord in.

>
If yes, why+how is my configuration wrong?
>

I'm not sure because I don't have enough familiarity with apcupsd -- the apcupsd-users list has more knowledgeable people in that area. That's why we're curious if you've tried PCNS because that should work. As for the UPSLink commands themselves, APC considers the link-language proprietary so I can't be much help there. I assume you've tested "apccontrol killpower" with the UPS unplugged?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:20 AM . Last Modified: ‎2024-03-06 01:51 AM

0 Likes
0
1697
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:20 AM . Last Modified: ‎2024-03-06 01:51 AM

"Yes, all SmartUPS do (probably BackUPS with USB comms as well). If you want to test this, unplug the UPS and then command the NMC to reboot it. It should turn off, wait for AC, and then turn back on when you plug the power cord in."

Wrong. It appears this particular SmartUPS explicitly denies any ability to shut down its load under PCNet or apcupsd control. The experiment you suggest above works, but is of no value. I want PCnet or apcupsd to successfully command the UPS to cut power, not the Web interface to the NMC.

"I'm not sure because I don't have enough familiarity with apcupsd -- the apcupsd-users list has more knowledgeable people in that area. That's why we're curious if you've tried PCNS because that should work."

I have tried both PCNS and apcupsd. They show the exact same behavior: the OS shuts down, but the UPS does not (can not) cut power to the load.

Please read carefully this thread and also the following ones. I am an experienced sysad and unlikely to have committed any silly mistakes.

[http://sourceforge.net/mailarchive/forum.php?thread_name=4FCA6497.5080305%40sagebrushnetworks.com&fo...] and
[http://sourceforge.net/mailarchive/forum.php?thread_name=4F83020F.6070906%40cse.iitb.ac.in&forum_nam...]

"I assume you've tested "apccontrol killpower" with the UPS unplugged?"

Yes. The UPS consistently and completely ignores the command.

At this point I almost know the answer: "Your specific UPS model does not support power down of load initiated from PCnet/PCNS or apcupsd." But it's a pity there is no one alive in APC to tell me that authoritatively.

Message was edited by: 545ad3

Message was edited by: 545ad3

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-01 01:20 AM . Last Modified: ‎2024-03-06 01:51 AM

0 Likes
0
1697
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:20 AM . Last Modified: ‎2024-03-06 01:51 AM

My apologies, I missed the part about "Shutdown Mode" and it's the first I've heard of that feature.

I asked one of the UPS engineers here, and it's a feature accessible through the front panel display to disallow shutdown via UPSLink. Looking at [the manual|http://www.apcmedia.com/salestools/AHIE-83NAUF_R0_EN.pdf], I would guess it's under setup->shutdown. I recommend the secure shutdown mode which accepts a double-byte UPSLink turn off command.

Hope that helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:20 AM . Last Modified: ‎2024-03-06 01:51 AM

0 Likes
0
1698
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:20 AM . Last Modified: ‎2024-03-06 01:51 AM

voidstar wrote:
it's a feature accessible through the front panel display to disallow shutdown via UPSLink. Looking at [the manual|http://www.apcmedia.com/salestools/AHIE-83NAUF_R0_EN.pdf], I would guess it's under setup->shutdown.
I left no stone unturned before asking for help. On the front panel of the UPS, that menu path takes you to precisely the same menu as through the Web interface to the NMC ("upshutdn.htm") --- in that menu, you get to choose Low Battery Duration, Shutdown Delay, Basic Signaling Shutdown, Sleep Time, End of Shutdown
Minimum Battery Capacity, and Return Delay. At the top of the (Web page) panel is the emphatic announcement: "Shutdown Mode: Never" without any option to change said shutdown mode.

The world has indeed come to the point where the manufacturer of such a gadget does not have the human resources to send back one email of the form: "We have checked that your UPS, serial number X123, firmware revision PQR dated YY/MM is hardwired to never shutdown. No flashing of firmware or configuration of software can achieve what you want. The UPS will not obey killpower commands. You can only switch the load off manually from the front panel or the Web interface." OR "Here is a link to a firmware. Please flash it and you will be able to change the shutdown mode to what you want." APC India has been playing phone and email tag for over a month now without any real action. I can understand why: they do not have a single person capable of even understanding the setup and the goal.

This is a very bad state of affairs. I have already informed our IS organization about the undesirability of APC hardware. We have several hundred small and large UPSs on our premises, so turning to another brand will be a significant change for us. But probably worthwhile.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore