SUVTP 30kVA - 2 Units in Parallel

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUVTP 30kVA - 2 Units in Parallel
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
114
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 04:51 AM . Last Modified: ‎2024-03-19 01:20 AM

0 Likes
5
1066
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:51 AM . Last Modified: ‎2024-03-19 01:20 AM

SUVTP 30kVA - 2 Units in Parallel

Dear Experts,

I'm currently proposing a parallel UPS system. I would like to verify a few questions:

In a parallel configuration, must the 2 SUVTP UPS tap from the same utility source ?
or is it possible for each UPS to tap from different utility source (different substations) ?

The reason for this is to prevent both UPS being effected from single source failures.


List of items:

2ea SUVTP30KH4B4S - APC Smart-UPS VT 30kVA 400V....
1ea SUVTOPT009S - APC Smart-UPS VT Parallel Communications Kit, including Installation
1ea SBPAR30K40H-WP - APC Maintenance Bypass Panel 30-40kVA, 400V Wallmount

I've gone throught the SBP electrical diagram. There are 3 UPS Output terminals (X002, X003, X004) but only 1 Mains Input terminal (X001) which suggest 1 source. Pls. advice.


Regards,
C.L.Chee

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-26 04:51 AM . Last Modified: ‎2024-03-19 01:20 AM

0 Likes
0
1064
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:51 AM . Last Modified: ‎2024-03-19 01:20 AM

yes, if one system drops off rectifier and powers directly from the dc bus. the output's will stay tied.

unless you get an a or p bus alarm loss, then should freewheel or switch to static bypass.

as each inverter tracks the bypass (rectifier) supply, and control each other by master/slave config - they should always stay in sync on output side irrelevant of the input.

hope that is correct and helps.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-26 04:51 AM . Last Modified: ‎2024-03-19 01:20 AM

0 Likes
0
1065
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:51 AM . Last Modified: ‎2024-03-19 01:20 AM

They must be feed by the same source. If the UPS were on different input sources you would never be able to put them into bypass.

However a better solution if you have 2 utility sources would be to buy two SUVT's and install them as single modules. Then take both UPS outputs and tie them into a STS to feed your load.

Utility 1-----Input------------------
Utility 2-----Bypass--------------UPSA---------------- STS>----------------- Load

Utility 2-----Input----------------- UPSB----------------
Utility 1-----Bypass-------------

The STS is a static transfer switch which accepts to Inputs and keeps the load powered by the primary source(UPS A) and will switch to secondary source(UPS B) if UPS a fails or is shut off. There is no interuption to the load during the transfer.

Also with this configuration you have an additional benefit. You can feed UPS A main 1 input with Utility 1 and they Bypass of UPS B with Utility 1 and vise versa with Utility 2. By doing this if Utility 1 is lost UPS A still has its bypass feed to power the load and and UPS B still has its main input to keep the UPS running in Online mode.

You would be able to gain the benefits of two utility sources and still accomplish the same thing as two SUVT's in parallel assuming that you were doing that for redundancy and not capacity.

Here is APC's 200A STS.

http://www.apcc.com/resource/include/techspec_index.cfm?base_sku=STE200

Message was edited by: upsguy

Message was edited by: upsguy

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 04:51 AM . Last Modified: ‎2024-03-19 01:20 AM

0 Likes
0
1065
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:51 AM . Last Modified: ‎2024-03-19 01:20 AM

Hi UPSGuy,

Thanks for you feedback.

By attaching a STS it would have limited the purpose of SUVTP's parallel capability. There's a need for both UPS in parallel to share loads.

Let's assume Parallel for Capacity is required and any other switching equipment on the output side is a definate NO.
Maybe if you don't mind just help me understand the Parallel operation abit

If both UPS (parallel configuration) has only 1 utility input and same source, what would happend if the following were to occur:

1. UPS-A somehow does not accept input and switch to battery mode. Does UPS-B operate in normal mode or being forced to batt. mode ?
2. UPS-A internal fault causing it to switch to static bypass mode. Does UPS-B operate in normal mode or being forced to bypass mode ?

From past experiences with UPS that doest not have parallel feature, strict rules apply when it comes to getting both output synchronized (VIA STS) whereby both UPS must tap from the same source and operate in the same mode in order to have zero transfer time.

Please advise.

C.L.Chee

Reply

Link copied. Please paste this link to share this article on your social media post.

upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-26 04:51 AM . Last Modified: ‎2024-03-19 01:20 AM

0 Likes
0
1065
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:51 AM . Last Modified: ‎2024-03-19 01:20 AM

If // for capacity is required and you are not planing on adding any output switching then you would have to have the same input to each SUVT because..

When both UPS are online each UPS output is synconized to each other as well as the bypass input which would also be the mains 1 input if single feed.

You wouldnt be able to get the two units to // with each other if they were being fed different phased sources.

Also if you were somehow able to get the units // and online when you went to transfer them to static bypass which is just utility flowing through the units, if they were fed by different utility sources then you would be // two seperatly derived sources of power together on the output bus which I'm sure you know is a bad thing.

Sync could be an issue with an ATS but I've seen it implemented various times without phase sync circuits installed. However it would be just easier to install two SUVT's in // to accomplish your redundancy because I can't ever think of a reason to buy two SUVT 30ks for capacity. There are to many good UPS which can handle 60+kva and be expandable that won't come with the disadvantages of having to // two units together to reach the desired KVA size.

parallel = //

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 04:51 AM . Last Modified: ‎2024-03-19 01:20 AM

0 Likes
0
1065
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:51 AM . Last Modified: ‎2024-03-19 01:20 AM

Even if there's only 1 input source would it still be possible for these // UPS to sync output if one is online and the other is on bypass or battery mode ?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 04:51 AM . Last Modified: ‎2024-03-19 01:20 AM

0 Likes
0
1065
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:51 AM . Last Modified: ‎2024-03-19 01:20 AM

yes, if one system drops off rectifier and powers directly from the dc bus. the output's will stay tied.

unless you get an a or p bus alarm loss, then should freewheel or switch to static bypass.

as each inverter tracks the bypass (rectifier) supply, and control each other by master/slave config - they should always stay in sync on output side irrelevant of the input.

hope that is correct and helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of