Dear Community Members, We are currently experiencing a technical issue that is affecting the ability to create new posts. Our team is actively investigating the root cause and working to resolve it as quickly as possible. We apologize for the inconvenience and appreciate your patience. SE Community Team!
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:22 AM . Last Modified: 2024-03-07 11:08 PM
So the other day when blackout happened the ups throw me this error :
UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
And it wont sustain the load, which is strange cause the load isn't even 10% on the readings
So i replace the battery with apc official battery, i tested all of them with before installing to make sure it's brand new.
but the same error happens again after i run the calibration (after the battery is 100%)
Any ideas?
NMC is AP9631
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:22 AM . Last Modified: 2024-03-07 11:08 PM
Update : Finally solved this issue ! I followed this guide
https://www.stevenjordan.net/2016/05/fix-early-ups-shutdowns.html?m=1
After setting the constant to FF, the runtime says 8hrs 26 min, should've done this right after i bought it.
But how often do i need to do this though?
Another question for apc team, is the hard calibration absolutely necessary or not after resetting constant?
Since constant reset doesnt work with nmc installed, i need to remove nmc before running it,
But I read from various forum posts that the NMC card is hot-swappable, so that means when i need to calibrate i could just unplug the nmc and reset the battery constant.
So if hard callibration is not neccesary it's much simpler if it's not and i dont mind doing it once-twice a year.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:22 AM . Last Modified: 2024-03-07 11:08 PM
Update : Finally solved this issue ! I followed this guide
https://www.stevenjordan.net/2016/05/fix-early-ups-shutdowns.html?m=1
After setting the constant to FF, the runtime says 8hrs 26 min, should've done this right after i bought it.
But how often do i need to do this though?
Another question for apc team, is the hard calibration absolutely necessary or not after resetting constant?
Since constant reset doesnt work with nmc installed, i need to remove nmc before running it,
But I read from various forum posts that the NMC card is hot-swappable, so that means when i need to calibrate i could just unplug the nmc and reset the battery constant.
So if hard callibration is not neccesary it's much simpler if it's not and i dont mind doing it once-twice a year.
Link copied. Please paste this link to share this article on your social media post.