SURT5000XLI all load led are off

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SURT5000XLI all load led are off
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-07 10:55 PM . Last Modified: ‎2024-03-01 12:18 AM

0 Likes
7
2381
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:55 PM . Last Modified: ‎2024-03-01 12:18 AM

SURT5000XLI all load led are off

hi,

i notice that all load leds are off.

I did a test self in the ups and the result was replace battery.

i replaced the battery but all load leds still off.

What it is the problem?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:55 PM . Last Modified: ‎2024-03-01 12:17 AM

0 Likes
0
2380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:55 PM . Last Modified: ‎2024-03-01 12:17 AM

Hi Amelia,

I don't think this UPS offers USB... 

Your UPS should ship with an onboard network management card that you'll see installed in the SmartSlot in the rear of your UPS. Look for something that says AP9619 or AP9631 near an RJ-45 port. In order to set that up and configure it, refer to these instructions -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156064 

If you want to call your local technical support office, they may also be able to help walk you through it step by step live if you can be on the phone and near the UPS.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:55 PM . Last Modified: ‎2024-03-01 12:18 AM

0 Likes
0
2380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:55 PM . Last Modified: ‎2024-03-01 12:18 AM

Can you show me in this image what LEDs you're referring to to make sure we're on the same page? The load LEDs are the (5) stacked above each other on the far left. I want to make sure you're not referring to the battery charge LEDs on the far right as battery/load LEDs.

5tdgHHwuwnxdzPrxUCswuA%3D%3D.jpeg5tdgHHwuwnxdzPrxUCswuA%3D%3D.jpeg

Assuming the far left bar graph on the left is what you mean, how much load is on your UPS/what is plugged in? I think one LED comes on at about ~15-20% load..

Do you have a UPS management card installed/configured to review the log files and UPS status info?

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-07 10:55 PM . Last Modified: ‎2024-03-01 12:18 AM

0 Likes
0
2380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:55 PM . Last Modified: ‎2024-03-01 12:18 AM

hi,

you assume rigth. I´m refering to load led in the left side.

I have only 2 usb, 1 network card there are 2 left but i can´t see the card type.

None of the lights are on. All of them are off.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:55 PM . Last Modified: ‎2024-03-01 12:18 AM

0 Likes
0
2380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:55 PM . Last Modified: ‎2024-03-01 12:18 AM

What equipment is plugged into the UPS outlets or powered by the UPS? 

Do you have access to the network card to log in? 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-07 10:55 PM . Last Modified: ‎2024-03-01 12:17 AM

0 Likes
0
2380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:55 PM . Last Modified: ‎2024-03-01 12:17 AM

hi,

i have 

  • 4 switches: 2 Dlink, 1 HP and 1 Cisco Catalyst.
  • 1 thinkserver
  • 2 Lenovo Storage (1 Rack mount )
  • 1 Cisco Router 880
  • and 1 Planet PBX
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:55 PM . Last Modified: ‎2024-03-01 12:17 AM

0 Likes
0
2380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:55 PM . Last Modified: ‎2024-03-01 12:17 AM

Ok, so that is tough for me to tell if that would be close to 20%. Could you log in to the UPS management interface to see what actual % is reported. This would be the best thing to confirm what the UPS reports as its load percentage to see if it is a problem that the load LEDs are not lighting up versus the load just reporting as really low and not enough to illuminate any of the load LEDs.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-07 10:55 PM . Last Modified: ‎2024-03-01 12:17 AM

0 Likes
0
2380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:55 PM . Last Modified: ‎2024-03-01 12:17 AM

hi Angela,

can you help me connect to my UPS.

i only have 2 usb and 1 network port on my UPS «.

how can i connect in to my UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:55 PM . Last Modified: ‎2024-03-01 12:17 AM

0 Likes
0
2381
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:55 PM . Last Modified: ‎2024-03-01 12:17 AM

Hi Amelia,

I don't think this UPS offers USB... 

Your UPS should ship with an onboard network management card that you'll see installed in the SmartSlot in the rear of your UPS. Look for something that says AP9619 or AP9631 near an RJ-45 port. In order to set that up and configure it, refer to these instructions -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156064 

If you want to call your local technical support office, they may also be able to help walk you through it step by step live if you can be on the phone and near the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore