SURT2000XLI problem diagonistic

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SURT2000XLI problem diagonistic
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-07 10:14 PM . Last Modified: ‎2024-03-04 10:53 PM

0 Likes
4
1205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:14 PM . Last Modified: ‎2024-03-04 10:53 PM

SURT2000XLI problem diagonistic

Hi there,

I have had a Smart-UPS attached to some devices and the devices have been reading that there are "voltage distruptions". The problem happens rarely (2 times a month at most and only at night so can't see if the battery is discharged). I have had the equipment the UPS supplies checked for faults and there didn't seem to be any, so I was wondering if it was the UPS which could be failing? The load on the UPS is only around 1000W below its limits. How could I go about diagnoising the fault (if there is one) what should I check? The UPS is only 1 and a half years old and none of the error LEDs are illuminated.

Many Thanks,

Hottest Fudge

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
wayne_i_apc
Lieutenant wayne_i_apc
Lieutenant

Posted: ‎2021-07-07 10:14 PM . Last Modified: ‎2024-03-04 10:52 PM

0 Likes
0
1205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:14 PM . Last Modified: ‎2024-03-04 10:52 PM

Hi Mr Fudge (?!),

In your first post you speak of "voltage distruptions", while in later posts the discussion is about "voltage distortion". Notice in the specifications that Angela provided the "output voltage regulation" is listed as +/- 1% and "output voltage distortion" can be almost 8% in specific cases. While these are good numbers for AC power to a computer system (probably even better than utility (mains) power), if the output voltage regulation was 8% it would be disappointing for a UPS output of this class. On the other hand, a step-approximation output UPS doesn't even list output voltage distortion as a specification because it would horrify anyone who didn't understand the meaning of "distortion" while the UPS output is still acceptable for most computer systems.

Returning to you original post, can you be more specific about what your "attached devices" are, and how are they "attached"? Are they powered by the UPS in question, and are they connected to it's communication system (communication port or network management card)? How are they "reading" these "voltage disruptions", are they actually monitoring the UPS output directly, as in a powerline monitor system? And what does "voltage disruptions" mean?

When you say it happens "2 times a month", I would be suspicious of a scheduled self-test (I believe 14 days is the default self-test schedule), with a switchover to utility when testing the bypass feature possibly causing a glitch in the UPS output. Otherwise, as Angela already said, there is NO transfer time-- this type of UPS operates contiunously on it's inverter, so ANY problem (voltage, frequency, distortion, noise) with utility power will have absolutely NO effect on it's output! It's like utility power only supplies the input to a very large "battery charger", while the UPS runs continuously from the "batteries".

Wayne

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:14 PM . Last Modified: ‎2024-03-04 10:53 PM

0 Likes
0
1205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:14 PM . Last Modified: ‎2024-03-04 10:53 PM

What do these devices consider "voltage disruptions?" Meaning, does the voltage need to fluctuate more than 4V, for example? It'd be helpful to understand what your devices are looking at specifically.

It is normal for the UPS's output voltage to fluctuate slightly within a defined range that they can operate in so it is tough to say what it is if we don't know what your devices are looking at.

It'd also be good if you had a Network Management Card or PowerChute Business Edition and could check the event/data log at the times your devices report a problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-07 10:14 PM . Last Modified: ‎2024-03-04 10:52 PM

0 Likes
0
1205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:14 PM . Last Modified: ‎2024-03-04 10:52 PM

Thank you very much for your prompt reply! And sorry for my delayed one...

I will check with the manufacture as to what is the minimum amount of voltage distortion that gives the error. As for the UPS I have read that the output voltage distortion is < 3% (so 230 +/- 6.9V or +/- 3.45V), which is correct?

The UPS is currently in a rather secluded place and with no access to the network. Although there is a closed network PC (not connected to internet) do you think it would be prudent to set up the powerchute software on that, also how helpful would the software be?

Could my problem perhaps be that, if or when there is a power cut, the UPS isn't quick enough to change from mains power to battery power?

Many Thanks,

Hottest Fudge

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:14 PM . Last Modified: ‎2024-03-04 10:52 PM

0 Likes
0
1205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:14 PM . Last Modified: ‎2024-03-04 10:52 PM

Hi again.

What I see for this UPS in regards to output voltage distortion (and other items) is:

Output voltage selections 220, 230(default), 240V
Output voltage regulation range  +/-1% (typical)
Output frequency range 50/60Hz +/- 3Hz (default); 50/60Hz +/- 0.1Hz (user selectable)
Output voltage distortion <3% linear, <8% non-linear
Number of output phases 1 phase
Nominal output current (Amps) 8.7

It is hard to guess what the issue is without knowing what the equipment looks at. This is an online UPS so it has 0ms transfer time to battery power so I doubt that is related.

If we have no idea what the equipment is looking at, you could set up PowerChute but I think understanding what the tolerance of your equipment is first will be helpful and a good start. PowerChute may not catch something that only lasts for 1 second depending on what it is and maybe depending on the answer to the tolerance of the equipment will explain normal operation of the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

wayne_i_apc
Lieutenant wayne_i_apc
Lieutenant

Posted: ‎2021-07-07 10:14 PM . Last Modified: ‎2024-03-04 10:52 PM

0 Likes
0
1206
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:14 PM . Last Modified: ‎2024-03-04 10:52 PM

Hi Mr Fudge (?!),

In your first post you speak of "voltage distruptions", while in later posts the discussion is about "voltage distortion". Notice in the specifications that Angela provided the "output voltage regulation" is listed as +/- 1% and "output voltage distortion" can be almost 8% in specific cases. While these are good numbers for AC power to a computer system (probably even better than utility (mains) power), if the output voltage regulation was 8% it would be disappointing for a UPS output of this class. On the other hand, a step-approximation output UPS doesn't even list output voltage distortion as a specification because it would horrify anyone who didn't understand the meaning of "distortion" while the UPS output is still acceptable for most computer systems.

Returning to you original post, can you be more specific about what your "attached devices" are, and how are they "attached"? Are they powered by the UPS in question, and are they connected to it's communication system (communication port or network management card)? How are they "reading" these "voltage disruptions", are they actually monitoring the UPS output directly, as in a powerline monitor system? And what does "voltage disruptions" mean?

When you say it happens "2 times a month", I would be suspicious of a scheduled self-test (I believe 14 days is the default self-test schedule), with a switchover to utility when testing the bypass feature possibly causing a glitch in the UPS output. Otherwise, as Angela already said, there is NO transfer time-- this type of UPS operates contiunously on it's inverter, so ANY problem (voltage, frequency, distortion, noise) with utility power will have absolutely NO effect on it's output! It's like utility power only supplies the input to a very large "battery charger", while the UPS runs continuously from the "batteries".

Wayne

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of