SURT100XLI Fault and LED 3 and 4 illuminated

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SURT100XLI Fault and LED 3 and 4 illuminated
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 10:36 PM . Last Modified: ‎2024-03-06 10:50 PM

0 Likes
1
1661
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:36 PM . Last Modified: ‎2024-03-06 10:50 PM

SURT100XLI Fault and LED 3 and 4 illuminated

Hi,

I have a SURT1000XLi which has gone into a fault state, dropping output power.  The UPS will not power on, but when connected to mains power, the rear fan turns on, and after about 4 seconds it illuminates the Fault LED, as well as the 3rd and 4th (from the top down) battery LEDs.  All these LED stay on solid - they do not flash.

Can anyone advise what fault condition this combination of LEDs indicates?

Some additional details:

UPS age: 4yr 6mths

Battery age: 11months

UPS load at failure: 12%

The UPS is remotely monitored via StruxureWare DCE, and I am not aware of any external event which may have caused this fault condition to occur.

 

Thanks in advance for any assistance.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • fault
  • led
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 10:36 PM . Last Modified: ‎2024-03-06 10:50 PM

0 Likes
0
1661
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:36 PM . Last Modified: ‎2024-03-06 10:50 PM

Found the answer.

The light pattern indicates a DC/DC converter fault.

Full list of codes below which may be of interest to others.

 

Fault Codes Explanation:

SURT firmware stores the failure code any time the unit goes into the failure bypass or ups failure states. It also stores the overload failure in the bypass state if applicable. The failure code is stored in the EEPROM and is therefore preserved until overwritten with a new value or until the EEPROM is cleared. The code can be retrieved with UPS-Link "Ctrl-U" when in programming mode only.

 The fault status can be decoded by relating the battery charge capacity bar graph and moreover the Ctrl-U result to the appropiate codes list.

 These are the codes for the different UPS models.

 

1) 230Vac models of SUOL/SURT 1000 & 2000 (Lynx 1):

 

     Fault                                        Display                                     Ctrl-U

Overload (includes short circuit)       Overload LED                                       40

Inverter fault                                    First / lowest capacity LED                    02

Transfer relay weld                          Second capacity LED                            01

PFC failure                                      Third capacity LED                                04

DC bus overvoltage                        Fourth capacity LED                              10

Overtemperature                              Fifth / highest capacity LED                   20

Output overvoltage                          First and second capacity LEDs            08

DC/DC converter fault                     Second and third capacity LEDs            80

Unknown fault (just in case)                   All capacity LEDs                                  00

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Anonymous user
Not applicable

Posted: ‎2021-06-30 10:36 PM . Last Modified: ‎2024-03-06 10:50 PM

0 Likes
0
1662
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:36 PM . Last Modified: ‎2024-03-06 10:50 PM

Found the answer.

The light pattern indicates a DC/DC converter fault.

Full list of codes below which may be of interest to others.

 

Fault Codes Explanation:

SURT firmware stores the failure code any time the unit goes into the failure bypass or ups failure states. It also stores the overload failure in the bypass state if applicable. The failure code is stored in the EEPROM and is therefore preserved until overwritten with a new value or until the EEPROM is cleared. The code can be retrieved with UPS-Link "Ctrl-U" when in programming mode only.

 The fault status can be decoded by relating the battery charge capacity bar graph and moreover the Ctrl-U result to the appropiate codes list.

 These are the codes for the different UPS models.

 

1) 230Vac models of SUOL/SURT 1000 & 2000 (Lynx 1):

 

     Fault                                        Display                                     Ctrl-U

Overload (includes short circuit)       Overload LED                                       40

Inverter fault                                    First / lowest capacity LED                    02

Transfer relay weld                          Second capacity LED                            01

PFC failure                                      Third capacity LED                                04

DC bus overvoltage                        Fourth capacity LED                              10

Overtemperature                              Fifth / highest capacity LED                   20

Output overvoltage                          First and second capacity LEDs            08

DC/DC converter fault                     Second and third capacity LEDs            80

Unknown fault (just in case)                   All capacity LEDs                                  00

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore