SURT1000RMXLI-NC and SURT48RMXLPB Extended Warranty
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2804:56 AM. Last Modified: 2024-03-1803:57 AM
SURT1000RMXLI-NC and SURT48RMXLPB Extended Warranty
If we want to buy SURT1000RMXLI-NC + (1)SURT48RMXLBP with extended warranty for 1 year for both the UPS and extra battery bank, do we have to order 1 x WBEXTWAR1YR-SP-03 for both UPS and battery bank or 2 x WBEXTWAR1YR-SP-03, one for each item?