SU RT 8000 XL - how to configure behaviour when power is lost ?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SU RT 8000 XL - how to configure behaviour when power is lost ?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
bernd_apc
Ensign bernd_apc
Ensign

Posted: ‎2021-06-28 04:56 AM . Last Modified: ‎2024-03-18 03:58 AM

0 Likes
3
1110
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:56 AM . Last Modified: ‎2024-03-18 03:58 AM

SU RT 8000 XL - how to configure behaviour when power is lost ?

Hi,

we have a SU RT 8000 XL and NMC AP9617 with firmware 3.7.2 (which seems to be the most recent).

Some weeks ago we had a power interruption in our building. Here are the according entries in the log:

10.08.2016 14:40:50 UPS: The output power is turned off.
10.08.2016 14:38:53 UPS: Started a reboot process.
10.08.2016 14:20:23 UPS: A graceful shutdown process is being used to shut down the load equipment before the UPS turns off. Initiated by PowerChute ns from 146.107.93.90.
10.08.2016 14:20:21 UPS: No longer on battery power.
10.08.2016 14:10:21 UPS: On battery power in response to an input power problem.

At 14:20:21 power was available again. But although power was available again, the clients (SLES 10 and SLES 11) started a shutdown just some seconds after power was restored. Why ? I expect that the clients don't shutdown when power is restored because it's not necessary any longer. Am i wrong ?
Here is my configuration of the shutdown:

Start of Shutdown
Low Battery Duration:  minutes
Shutdown Delay:  seconds
Maximum Required Delay: 15 minutes
Basic Signaling Shutdown: Enable
Duration of Shutdown
Sleep Time: hours [0 to 359.9]
End of Shutdown
Minimum Battery Capacity:  %
Return Delay:  seconds

I have to admit that i'm not completely familiar with this configuration.
What does "Low Battery Duration" mean ? The time that UPS can run on battery ? Or the time upon the UPS is shut down ? How can i find out that duration ?
"Shutdown Delay": help says: "Defines how long the UPS waits before it shuts down in response to a turn-off command." Where does the turn-off command come from ? Is the power loss the turn-off command ? Is it initiated by the UPS itself ? Or one of the clients ? What is shut down ? The UPS, the clients, or both ?
"Maximum Required Delay: " help says: "This delay is calculated whenever the management interface of the UPS turns on or is reset, or when "Force Negotiation" is selected as Maximum Required Delay. "Force Negotiation" polls each client for information on the time it needs for a graceful shutdown." I find "Force Neotiation" in "Power Chtue ==> configuration". Calculation needs just 1 - 2 sec. Is that right ? Help says it can take up to 10 minutes.
Where can i configure "x min after power loss shut down the clients" ? Is that the "Shutdown Delay" ? Or is it configured in the web interface of the clients ?

Thanks.

Bernd

 

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 8000
  • configuration
  • lost
  • power
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
bernd_apc
Ensign bernd_apc
Ensign

Posted: ‎2021-06-28 04:56 AM . Last Modified: ‎2024-03-18 03:58 AM

0 Likes
0
1110
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:56 AM . Last Modified: ‎2024-03-18 03:58 AM

Hi,

i think it's a bit different. After reading the help from the PCNS and the UPS it seems for me like this:

I have configured 600 sec. for the "UPS on battery event" in the PCNS.
(Shut down the system only when the event lasts this long (seconds) in the PCNS)
That means the client OS will start shutdown when the UPS is on battery for 10 minutes or more.
Starting with the shutdown of the client OS the UPS also gets a "turn off" from PCNS on the client(s).
UPS will keep running the "Low Battery Duration" time (configured in the NMC, i have 15 min.)
UPS will further on keep running a hard coded 2 minutes and the "shutdown delay" (configured in the NMC, i have 2 min.).

So, after getting the "turn off" from the client, my UPS should keep running for 19 min. Right ?

This is the log from my power failure:

10.08.2016 14:40:50 UPS: The output power is turned off.
10.08.2016 14:38:53 UPS: Started a reboot process.
10.08.2016 14:20:23 UPS: A graceful shutdown process is being used to shut down the load equipment before the UPS turns off. Initiated by PowerChute ns from 146.107.93.90.
10.08.2016 14:20:21 UPS: No longer on battery power.
10.08.2016 14:10:21 UPS: On battery power in response to an input power problem.

It's close to the above explained procedure, but not exactly. What means "UPS: started a reboot process" and where does it come from ?

There is a helpful image in the help from the PCNS:

What is that "sleep command" ?

Thanks. 

Bernd

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:56 AM . Last Modified: ‎2024-03-18 03:58 AM

0 Likes
0
1110
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:56 AM . Last Modified: ‎2024-03-18 03:58 AM

Hi Bernd, 

What I believe happened in your situation was that PCNS sent a shutdown command to your clients just before, or at the time power was restored, and once a command is sent, even when power restores immediately after, the clients will continue to shutdown. 

What we can do is change your settings to hopefully avoid this in the future. Please see my answers to your questions below:

The "Low Battery Duration" is the time at which the UPS will start a shut down depending on the amount of runtime you have left. So in your situation, the UPS will send a shutdown command when there is 15 mins left of runtime on battery. 

The turn-off command comes from the low battery duration. So once you reach 15 mins left of runtime, the command is sent. This is a global command, so it will be sent to all PowerChute clients, and once those clients are shut down, the UPS itself will turn off. Right now your shutdown delay is set to 120 seconds. So once you reach 15 mins of runtime, the UPS will send a shutdown command to the PCNS clients, wait 120 seconds for them to shut off, then shut itself down. 

For the Force Negotiation, the time it takes to calculate the Maximum Required Delay depends on how many PowerChute clients you have. It has to poll each of them individually which is why it may take up to 10 mins max if you have a lot of clients. Since you only have 2 clients, the calculation should not take very long. 

As for configuring "x min after power loss shut down the clients", that can be done in the PCNS interface for the clients. 

Let me know if you have any further questions. 

Nicole 

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 04:56 AM . Last Modified: ‎2024-03-18 03:58 AM

0 Likes
0
1110
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:56 AM . Last Modified: ‎2024-03-18 03:58 AM

The big picture is: the UPS turns computers back on by cycling power to them. So once a single computer has chosen to shut down, even if power comes back, the UPS still needs to shut down so it can turn the computer back on.

Reply

Link copied. Please paste this link to share this article on your social media post.

bernd_apc
Ensign bernd_apc
Ensign

Posted: ‎2021-06-28 04:56 AM . Last Modified: ‎2024-03-18 03:58 AM

0 Likes
0
1111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:56 AM . Last Modified: ‎2024-03-18 03:58 AM

Hi,

i think it's a bit different. After reading the help from the PCNS and the UPS it seems for me like this:

I have configured 600 sec. for the "UPS on battery event" in the PCNS.
(Shut down the system only when the event lasts this long (seconds) in the PCNS)
That means the client OS will start shutdown when the UPS is on battery for 10 minutes or more.
Starting with the shutdown of the client OS the UPS also gets a "turn off" from PCNS on the client(s).
UPS will keep running the "Low Battery Duration" time (configured in the NMC, i have 15 min.)
UPS will further on keep running a hard coded 2 minutes and the "shutdown delay" (configured in the NMC, i have 2 min.).

So, after getting the "turn off" from the client, my UPS should keep running for 19 min. Right ?

This is the log from my power failure:

10.08.2016 14:40:50 UPS: The output power is turned off.
10.08.2016 14:38:53 UPS: Started a reboot process.
10.08.2016 14:20:23 UPS: A graceful shutdown process is being used to shut down the load equipment before the UPS turns off. Initiated by PowerChute ns from 146.107.93.90.
10.08.2016 14:20:21 UPS: No longer on battery power.
10.08.2016 14:10:21 UPS: On battery power in response to an input power problem.

It's close to the above explained procedure, but not exactly. What means "UPS: started a reboot process" and where does it come from ?

There is a helpful image in the help from the PCNS:

What is that "sleep command" ?

Thanks. 

Bernd

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of