SURT10000XLI - Alternation between bypass and online mode

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SURT10000XLI - Alternation between bypass and online mode
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
POsorio_apc
Crewman POsorio_apc
Crewman

Posted: ‎2021-06-26 05:28 AM . Last Modified: ‎2024-03-19 12:48 AM

0 Likes
10
3326
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:28 AM . Last Modified: ‎2024-03-19 12:48 AM

SURT10000XLI - Alternation between bypass and online mode

Hello,

Last saturday I installed two Smart UPS 10kVA (SURT10000XLI - Three phases) with two bypass each.
Today, one of this UPS are switching between Online and Bypass mode. The only way to turn the UPS to "normal" mode is:
- Cut the power and Turn off the UPS
- Press the O button for a while
- Power ON the UPS again
After this procedure the UPS are OK (online led is green and battery led's also) but only for a while (~30min).

We use one breaker with 30Amp, one for each UPS.

The question is if do you think that we should us breakers with 60Amp or this has nothing to do with breakers?

The strange think is that the other UPS works perfect (with the same breakers potency - Amp).

Thank you for your time.
BR,
Luis Osorio

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:28 AM . Last Modified: ‎2024-03-19 12:48 AM

0 Likes
0
3326
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:28 AM . Last Modified: ‎2024-03-19 12:48 AM

dear ,

      the issue is not ciritical simple first reset the NMC card and then check .if issue is not resolved then replaced the NMC

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:28 AM . Last Modified: ‎2024-03-19 12:48 AM

0 Likes
0
3326
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:28 AM . Last Modified: ‎2024-03-19 12:48 AM

is it possible to log in to the pre-installed network management card and configure it to retrieve the event and data logs that the unit can provide? this would most likely be helpful in diagnosing the issue.

instructions are here -> http://nam-en.apc.com/app/answers/detail/a_id/9321

i forgot to add - if instructions are needed to set up the NMC, check this out -> http://nam-en.apc.com/app/answers/detail/a_id/3061

Reply

Link copied. Please paste this link to share this article on your social media post.

POsorio_apc
Crewman POsorio_apc
Crewman

Posted: ‎2021-06-26 05:28 AM . Last Modified: ‎2024-03-19 12:48 AM

0 Likes
0
3328
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:28 AM . Last Modified: ‎2024-03-19 12:48 AM

Ok. I will try tomorow.
By the way, I can see some generi alarms when I connect to the UPS through web access. Is something like:
- (...) hardware fault;
And an error with the information that bypass condition probably caused by an external acessories...
but I will confirm it tomorow.

Excluding some possible causes, do you think that a breaker with 30A to a load of ~5Amp could be the cause for this issue?

Thank u.
BR,
Luis Osorio

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:28 AM . Last Modified: ‎2024-03-19 12:48 AM

0 Likes
0
3328
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:28 AM . Last Modified: ‎2024-03-19 12:48 AM

no i dont think so at this point to be honest. that is probably not up to code but i don't think it should case this type of problem based on what you said so far.

Reply

Link copied. Please paste this link to share this article on your social media post.

POsorio_apc
Crewman POsorio_apc
Crewman

Posted: ‎2021-06-26 05:28 AM . Last Modified: ‎2024-03-19 12:48 AM

0 Likes
0
3328
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:28 AM . Last Modified: ‎2024-03-19 12:48 AM

Hello again,

I attached the requested files.
I switch the UPS to Bypass mode manually (switch button from the back of UPS).

Thank you again.
Pedro

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:28 AM . Last Modified: ‎2024-03-19 12:48 AM

0 Likes
0
3328
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:28 AM . Last Modified: ‎2024-03-19 12:48 AM

ok i took a look at the logs. definitely seems to be an issue with the UPS inverter that is causing the UPS to go in and out of bypass because of the hardware fault. then i also see some funny stuff going on with battery capacity which is most likely causing your runtime to drop and cause the battery discharged messages.

the first thing i might do is braindead the UPS and see if it still does the same thing. if so, then you probably want to contact your local APC support and see what they can do for a warranty replacement.

to braindead, you need to remove any load attached which there doesnt appear to be any now. once thats done, you need to turn the UPS off by pushing the off (o) button. remove AC power - by cutting the breaker to the UPS or flipping the input breaker maybe. then, go back to the front of the unit and hold down the off (o) button again for 5-10 seconds until you hear a click and see some front panel LEDs flash. if you don't get that, leave the UPS in this state for 10-15 minutes and it will automatically braindead if you also disconnect the batteries from it temporarily - including internal or any attached battery packs.

once this is complete, then try to reconnect everything, return breakers to their normal state and then power up the unit again and check the management card to see if you are still seeing the same faults or if you can tell by the front if it is still switching to bypass. i imagine this WONT fix the problem but it is worth a try before we have to pursue replacing it.

Reply

Link copied. Please paste this link to share this article on your social media post.

POsorio_apc
Crewman POsorio_apc
Crewman

Posted: ‎2021-06-26 05:28 AM . Last Modified: ‎2024-03-19 12:48 AM

0 Likes
0
3328
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:28 AM . Last Modified: ‎2024-03-19 12:48 AM

I did the procedure that you suggested and I don't want to "launch the rockets" 🙂 but has already more than 1 hour without going to bypass alternately...
We also observed that all connections were tight.
I will give feedback to you tomorow.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:28 AM . Last Modified: ‎2024-03-19 12:48 AM

0 Likes
0
3328
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:28 AM . Last Modified: ‎2024-03-19 12:48 AM

sure thing. i'll wait to see what you find.

Reply

Link copied. Please paste this link to share this article on your social media post.

POsorio_apc
Crewman POsorio_apc
Crewman

Posted: ‎2021-06-26 05:28 AM . Last Modified: ‎2024-03-19 12:48 AM

0 Likes
0
3328
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:28 AM . Last Modified: ‎2024-03-19 12:48 AM

Hello,

Bad news...
The UPS was off this morning...
I turned on the UPS and I have the same problem on the front of the UPS (switching between bypass and online)...

Log:
Date Time Event
10/20/2011 00:35:22 System: Network service started. System IP is 10.227.2.201 from DHCP server 10.227.2.1 with 86330 second lease.
10/20/2011 00:35:16 UPS: The output power is turned off.
10/20/2011 00:35:16 UPS: Restored the local network management interface-to-UPS communication.
10/20/2011 00:35:05 System: Network service started. IPv6 address FE80::2C0:B7FF:FEC4:4F10 assigned by link-local autoconfiguration.
10/20/2011 00:34:55 System: Warmstart.
10/20/2011 00:34:43 System: Restarting.
10/19/2011 23:41:37 UPS: The output power is turned off.
10/19/2011 23:41:37 UPS: Restored the local network management interface-to-UPS communication.
10/19/2011 23:41:36 System: Network service started. System IP is 10.227.2.201 from DHCP server 10.227.2.1 with 86330 second lease.
10/19/2011 23:41:26 System: Network service started. IPv6 address FE80::2C0:B7FF:FEC4:4F10 assigned by link-local autoconfiguration.
10/19/2011 23:41:16 System: Warmstart.
10/19/2011 22:12:20 UPS: The output power is turned off.


Why Warmstart and UPS off this morning?

Thank you.
Luis

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:28 AM . Last Modified: ‎2024-03-19 12:48 AM

0 Likes
0
3328
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:28 AM . Last Modified: ‎2024-03-19 12:48 AM

that UPS doesnt power the network switch does it?

here are the reasons why an NMC might "warmstart" and what it means. if the UPS is turning off output that is powered by something on the UPS, the NMC will try to reboot to fix its network connection and cannot ping its default gateway.

http://nam-en.apc.com/app/answers/detail/a_id/2572

there definitely appears to be a problem with the UPS here - i don't know why its acting a little differently today but i'd recommend contacting your local support to pursue a replacement because i don't think you can trust the UPS. you could move your network management card to your new UPS so if you do get a warranty replacement, check to see if it comes with an NMC or not.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:28 AM . Last Modified: ‎2024-03-19 12:48 AM

0 Likes
0
3327
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:28 AM . Last Modified: ‎2024-03-19 12:48 AM

dear ,

      the issue is not ciritical simple first reset the NMC card and then check .if issue is not resolved then replaced the NMC

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore