SUA3000R3XLN UPS and SUA48RMXLBP3V external battery pack all dead?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUA3000R3XLN UPS and SUA48RMXLBP3V external battery pack all dead?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
123
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:02 AM . Last Modified: ‎2024-03-13 01:52 AM

0 Likes
11
1736
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:02 AM . Last Modified: ‎2024-03-13 01:52 AM

SUA3000R3XLN UPS and SUA48RMXLBP3V external battery pack all dead?

I support a client who has 3000XL UPS and an external battery pack. There was an extended power outage (more than a week) some time ago and since then neither unit appears to be providing power. I have validated the wall outlet has approx 114V. When I check any of the 48V battery packs, they are all around 25V. There are no indicators whatsoever on the UPS. If I hold the test button and let go, I hear the fan start, the UPS beeps, and some load and battery charge leds flash ( 3 middle ones for load, 1,2,4 for battery charge) and then it goes dead again. I'm trying to figure out if this is normal and the battery packs need to be replaced or if this indicates a problem. The batteries are approx 2.5 years old. I'd appreciate any thoughts on any other tests I can do.

Thanks,
Rob

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 3000xl
  • battery
  • coach
  • outlet
  • pack
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:03 AM . Last Modified: ‎2024-03-13 01:51 AM

0 Likes
0
1735
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:03 AM . Last Modified: ‎2024-03-13 01:51 AM

You're welcome! Look into having the unit [Traded-Up|http://buy.apc.com/commerce/storefronts/tradeups/tradein.aspx?storefrontcode=apcetu&countrycode=US&t...] to a new one or have it repaired by [Coastal Business Machines|http://www.cbmi.com/service/], APC's authorized repair partner.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:02 AM . Last Modified: ‎2024-03-13 01:52 AM

0 Likes
0
1735
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:02 AM . Last Modified: ‎2024-03-13 01:52 AM

Thanks for all the help! I'll look at repair or replacement.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:02 AM . Last Modified: ‎2024-03-13 01:52 AM

0 Likes
0
1735
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:02 AM . Last Modified: ‎2024-03-13 01:52 AM

Good day,Are you measuring the voltage from the connector at the back of the SUA48RMXLBP3U (this should be the correct part# for the external battery pack)or from the terminals of the batteries inside it? I suggest that you run a selftest by pressing and holding down the test button for 2-3 seconds with the external battery pack connected and without them while the UPS is online, this will help you determine if it's the battery inside the UPS or those in the external battery pack that has failed.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:02 AM . Last Modified: ‎2024-03-13 01:52 AM

0 Likes
0
1735
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:02 AM . Last Modified: ‎2024-03-13 01:52 AM

Hello,

Thank-you for your response. I measured the voltage from the wire coming out of the battery packs. The battery packs have part #APCRBC105. There are a total of 3 of these battery packs, 1 in the UPS and 2 in the external battery pack enclosure. The most I see on any of them is 25V. I'm trying to figure out if I should be looking into buying new batteries or if I should be looking at a new UPS. Seems strange that everything died, but then again there was an extended outage.

Thanks,
Rob

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:02 AM . Last Modified: ‎2024-03-13 01:52 AM

0 Likes
0
1735
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:02 AM . Last Modified: ‎2024-03-13 01:52 AM

The nominal string voltage on an APCRBC105 is 48 Vdc, so those batteries may have already gone bad. But still, I'd suggest that you follow the steps in this kbase

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:03 AM . Last Modified: ‎2024-03-13 01:52 AM

0 Likes
0
1735
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:03 AM . Last Modified: ‎2024-03-13 01:52 AM

When I test with just the external battery pack the all lights on the UPS blink in a random fashion and it continually beeps until I disconnect the battery. If I hold the test button with no batteries attached and only connect to AC power it does nothing at all- is this normal?

Thanks,
Rob

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:03 AM . Last Modified: ‎2024-03-13 01:52 AM

0 Likes
0
1735
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:03 AM . Last Modified: ‎2024-03-13 01:52 AM

That has the same effect- all lights blink randomly and it beeps until you disconnect the battery. Should the UPS do anything with no battery connected while plugged in when you use the test button?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:03 AM . Last Modified: ‎2024-03-13 01:51 AM

0 Likes
0
1735
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:03 AM . Last Modified: ‎2024-03-13 01:51 AM

What I was recommending was to run the selftest with the external battery pack disconnected and the UPS still having it's internal battery installed and another selftest with the internal battery of the UPS installed and the external battery pack connected to the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:03 AM . Last Modified: ‎2024-03-13 01:51 AM

0 Likes
0
1734
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:03 AM . Last Modified: ‎2024-03-13 01:51 AM

Do all of the LEDs on the front panel blink randomly or only specific ones? During a selftest, the UPS switches to On-battery operation to check if the battery is still healthy, so if you do a selftest with no batteries connected (internal & external) the UPS will turn off. I suggest that you de-energize the UPS by turning the UPS off, disconnect the SUA48RMXLBP3U, unplug the UPS from where its plugged in and then press & hold down the "0" button for 5 seconds.
After that, plug the UPS to power source, turn it on then check if it does the same. If it does, the unit needs to be serviced or replaced.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:03 AM . Last Modified: ‎2024-03-13 01:51 AM

0 Likes
0
1734
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:03 AM . Last Modified: ‎2024-03-13 01:51 AM

Kulot,

Thanks for all the suggestions so far. I was able to do another test and this time the following LEDs were blinking: the 3 center ones for Load, and the 1st, 2nd and 4th from the top for Battery Charge.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:03 AM . Last Modified: ‎2024-03-13 01:51 AM

0 Likes
0
1734
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:03 AM . Last Modified: ‎2024-03-13 01:51 AM

Are those LEDs flashing on the UPS with the external battery pack disconnected? If they are, I'd say that the UPS is due for repair or replacement.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:03 AM . Last Modified: ‎2024-03-13 01:51 AM

0 Likes
0
1736
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:03 AM . Last Modified: ‎2024-03-13 01:51 AM

You're welcome! Look into having the unit [Traded-Up|http://buy.apc.com/commerce/storefronts/tradeups/tradein.aspx?storefrontcode=apcetu&countrycode=US&t...] to a new one or have it repaired by [Coastal Business Machines|http://www.cbmi.com/service/], APC's authorized repair partner.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of