SUA2200RMI2U and SUA3000RMI2U

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUA2200RMI2U and SUA3000RMI2U
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 02:21 AM . Last Modified: ‎2024-03-10 11:35 PM

0 Likes
3
1386
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:21 AM . Last Modified: ‎2024-03-10 11:35 PM

SUA2200RMI2U and SUA3000RMI2U

Hi, we have one of each of the above 2200 and 3000 size 2U APC UPS. The batteries on both are about ready to be replaced. Can we use a 3000 battery pack unit in the SUA2200 UPS unit, so we have two 3000 sized units to increase run time? Can we use (do they exist?) a larger than 3000 sized battery pack in ether or both of the 2U UPS'?
Thanks.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:22 AM . Last Modified: ‎2024-03-10 11:35 PM

0 Likes
0
1386
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:22 AM . Last Modified: ‎2024-03-10 11:35 PM

well, these units are not "XL" so they don't support any external battery packs. you'd need a Smart UPS XL or something beginning with SMX to be able to add extra battery packs to it.

i researched both of these SKUs as far as batteries go and the 2200 takes RBC43 and so does the the 3000. thus, they both take the same battery and the runtime differs on the load most likely.

there is going to be no other battery pack that we have tested or can suggest to achieve a higher runtime here plus then you need to worry about charging time, size, etc. if you need to get a unit with more runtime either now or for the future, see about getting a Smart UPS XL or unit that has a prefix with SMX.

hope that helps.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-30 02:22 AM . Last Modified: ‎2024-03-10 11:35 PM

0 Likes
0
1386
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:22 AM . Last Modified: ‎2024-03-10 11:35 PM

Hi,

Thanks, I probably should have looked into this / understood it a bit more. I was assuming the 2200 / 3000 numbers were relating somehow to the size of the battery, it seems that it is referring to how many watts the unit can handle. They do both have 8xHR5.8-12 cells, I will look into replacement.
If we end up using non APC batterys (money is tight) that are slightly higher or lower capacity, will the unit charge them correctly?

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:22 AM . Last Modified: ‎2024-03-10 11:35 PM

0 Likes
0
1387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:22 AM . Last Modified: ‎2024-03-10 11:35 PM

well, these units are not "XL" so they don't support any external battery packs. you'd need a Smart UPS XL or something beginning with SMX to be able to add extra battery packs to it.

i researched both of these SKUs as far as batteries go and the 2200 takes RBC43 and so does the the 3000. thus, they both take the same battery and the runtime differs on the load most likely.

there is going to be no other battery pack that we have tested or can suggest to achieve a higher runtime here plus then you need to worry about charging time, size, etc. if you need to get a unit with more runtime either now or for the future, see about getting a Smart UPS XL or unit that has a prefix with SMX.

hope that helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:22 AM . Last Modified: ‎2024-03-10 11:35 PM

0 Likes
0
1386
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:22 AM . Last Modified: ‎2024-03-10 11:35 PM

well, generally, yes, we'd recommend APC batteries. we cant be liable of what happens when you don't. but, you can do whatever you want. the charger is designed to charge whatever it comes with so at a minimum, just choose the same voltage of course, which i am sure you know to do. as far as the amp hour capacity, i think it will just affect the charging time and available runtime either way (more or less). it should not be an issue. also, just make sure wherever you get them from, that they have not been sitting around. you may want to look for date codes on the batteries as the APC ones usually have that.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore