Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

SUA1500I shutdown and six led blinking when low voltage compensation occur

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUA1500I shutdown and six led blinking when low voltage compensation occur
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:30 AM . Last Modified: ‎2024-03-14 12:45 AM

0 Likes
3
1499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:30 AM . Last Modified: ‎2024-03-14 12:45 AM

SUA1500I shutdown and six led blinking when low voltage compensation occur

Hi everyone,
I'm owner of a SUA1500I smart-ups.
My problems started today, when the unit started to shutdown without any particular reason. Actually it doesn't shutdown completely, by meaning that when the unit usually shutdown, the led are all switched off, instead in my case six led start blinking 'till I press the OFF button.
What I've realized is that the problem occurs when the low-voltage compensation system runs. Aftter just half second than the LOW-VOLTAGE led switch on, this problem occurs.
In my apartment I usually have a low voltage, 213-215 V, so out from the 220-230V range, indeed the unit sometime use the Low-voltage compensation, but nothing of similar happened before today. It happens with any type of load, also with 2 or 3 switch and 1 router, so I can exclude an overload as well as a battery problem, the latter because I've changed it on last October, and becouse if I plug-out the line cord from the wall plug, the problem doesn't occur (nothing to compensate!!!!).

The following is the LOG string generated when the problem occurs

*14.06.2010 03:02:57 UPS: An automatic voltage regulator (AVR) relay fault exists.*

Do someone had a similar problem with such kind of APC Units?
Thank you in advancel.

Sebastiano

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • low
  • sua1500i
  • voltage
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:30 AM . Last Modified: ‎2024-03-14 12:44 AM

0 Likes
0
1499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:30 AM . Last Modified: ‎2024-03-14 12:44 AM

Hi everyone,
I'm owner of a SUA1500I smart-ups.
My problems started today, when the unit started to shutdown without any particular reason. Actually it doesn't shutdown completely, by meaning that when the unit usually shutdown, the led are all switched off, instead in my case six led start blinking 'till I press the OFF button.
What I've realized is that the problem occurs when the low-voltage compensation system runs. Aftter just half second than the LOW-VOLTAGE led switch on, this problem occurs.
In my apartment I usually have a low voltage, 213-215 V, so out from the 220-230V range, indeed the unit sometime use the Low-voltage compensation, but nothing of similar happened before today. It happens with any type of load, also with 2 or 3 switch and 1 router, so I can exclude an overload as well as a battery problem, the latter because I've changed it on last October, and becouse if I plug-out the line cord from the wall plug, the problem doesn't occur (nothing to compensate!!!!).

The following is the LOG string generated when the problem occurs

*14.06.2010 03:02:57 UPS: An automatic voltage regulator (AVR) relay fault exists.*

Do someone had a similar problem with such kind of APC Units?
Thank you in advancel.

Sebastiano

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:30 AM . Last Modified: ‎2024-03-14 12:45 AM

0 Likes
0
1499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:30 AM . Last Modified: ‎2024-03-14 12:45 AM

Hi JonPro,
you focused exactly the issue. I can turn on the ups again but it shuts down again as soon as the AVR Trim starts to "compensate" the voltage being fed to it by the line. I have tried to "bypass" the problem by lowering the lowVoltage threshold from 208V to 204V or lower, and so the unit stays on as the AVR doesn't start, but it would be more dangerous for all the HW units connected to the UPS, as this procedure is like to exclude the AVR Trim. Indeed, the unit is essential for me especially in summer like now, as many people widely use air conditioning systems, and I often have a low voltage in my apartment (210V low pe instead of regular 220W, or lower values in the instant the air cond. units rise-up), and unfortunately the italian energy company allows a 10% of oscillation around the 220Volts value, so by contract they are OK.
Unfortunately the warranty already expired, I bought his unit on July 2007. What I dislike of this situation is that I bought a new battery pack just 7 months ago!!!!!.
Anyhow...at this point I would like to join the trade-ups program for replace this unit with an identical model. Otherwise I will try to open it and to replace the faulty components.

Thank you.

Sebastiano

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:30 AM . Last Modified: ‎2024-03-14 12:45 AM

0 Likes
0
1499
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:30 AM . Last Modified: ‎2024-03-14 12:45 AM

That would really happen everytime that UPS would try to boos/ trim the input voltage, it's like to relay fails to return to normal state. I would suggest that you contact the APC Support Group for your region.

JonPro

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:30 AM . Last Modified: ‎2024-03-14 12:44 AM

0 Likes
0
1500
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:30 AM . Last Modified: ‎2024-03-14 12:44 AM

Hi everyone,
I'm owner of a SUA1500I smart-ups.
My problems started today, when the unit started to shutdown without any particular reason. Actually it doesn't shutdown completely, by meaning that when the unit usually shutdown, the led are all switched off, instead in my case six led start blinking 'till I press the OFF button.
What I've realized is that the problem occurs when the low-voltage compensation system runs. Aftter just half second than the LOW-VOLTAGE led switch on, this problem occurs.
In my apartment I usually have a low voltage, 213-215 V, so out from the 220-230V range, indeed the unit sometime use the Low-voltage compensation, but nothing of similar happened before today. It happens with any type of load, also with 2 or 3 switch and 1 router, so I can exclude an overload as well as a battery problem, the latter because I've changed it on last October, and becouse if I plug-out the line cord from the wall plug, the problem doesn't occur (nothing to compensate!!!!).

The following is the LOG string generated when the problem occurs

*14.06.2010 03:02:57 UPS: An automatic voltage regulator (AVR) relay fault exists.*

Do someone had a similar problem with such kind of APC Units?
Thank you in advancel.

Sebastiano

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore