SUA1000UXI Smart-UPS Battery runtime

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUA1000UXI Smart-UPS Battery runtime
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:26 AM . Last Modified: ‎2024-03-12 03:04 AM

0 Likes
9
1607
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:26 AM . Last Modified: ‎2024-03-12 03:04 AM

SUA1000UXI Smart-UPS Battery runtime

I have a SUA1000UXI Smart Ups with 2 external 12V Amaron Quanta 65 AH batteries i.e. one 24V  65AH Quanta battery. The runtime remaining shown in Powerchute Business edition is 83 minutes with 25% load. Theoretically it should be 6.63 Hrs. Since it uses only external batteries there is option to change no. of battery banks ( which is 0 for me). What is the default battery value used by UPS to calculate runtime? What runtime should I expect with my batteries.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:26 AM . Last Modified: ‎2024-03-12 03:04 AM

0 Likes
0
1606
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:26 AM . Last Modified: ‎2024-03-12 03:04 AM

Hello,

UPS models that support XL capability support changing the amount of battery packs as you've found. Some UPS models also support adding a value for external battery cabinent "AH" but I am only familiar with doing that in the Network Management Card. I assume you have not found that in any of the PCBE screens after looking?

2395_AH cabinet.jpg

I know the APC battery pack for this UPS has 12vDC 17AH batteries in it, qty 4 in it. They are wired to be a 24V pack. I think that the battery pack is intended to give you about 34-36AH so you could at a minimum adjust the external battery pack accordingly to account for your external pack if there is no field to specify AH.

I don't have a runtime chart for this older model unfortunately. If it is required, I will have to dig further.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:26 AM . Last Modified: ‎2024-03-12 03:04 AM

0 Likes
0
1607
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:26 AM . Last Modified: ‎2024-03-12 03:04 AM

Hello,

UPS models that support XL capability support changing the amount of battery packs as you've found. Some UPS models also support adding a value for external battery cabinent "AH" but I am only familiar with doing that in the Network Management Card. I assume you have not found that in any of the PCBE screens after looking?

2395_AH cabinet.jpg

I know the APC battery pack for this UPS has 12vDC 17AH batteries in it, qty 4 in it. They are wired to be a 24V pack. I think that the battery pack is intended to give you about 34-36AH so you could at a minimum adjust the external battery pack accordingly to account for your external pack if there is no field to specify AH.

I don't have a runtime chart for this older model unfortunately. If it is required, I will have to dig further.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:26 AM . Last Modified: ‎2024-03-12 03:04 AM

0 Likes
0
1606
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:26 AM . Last Modified: ‎2024-03-12 03:04 AM

With the latest version of PCBE I dont get the above screen. I can still set the no.of battery banks. If I do change the no. is there are effect on the charge/voltage supplied to the batteries or is it just used to calculate runtime. There is a firmware upgrade shown for my model but I'm not sure how I apply it to my ups. Thanks for the help

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:26 AM . Last Modified: ‎2024-03-12 03:04 AM

0 Likes
0
1606
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:26 AM . Last Modified: ‎2024-03-12 03:04 AM

Yes, that screen is from a UPS Network Management Card so I didn't know if PCBE offered the same thing.

The only thing that setting (AH or external battery pack qty) would change is the reported runtime estimate you receive. So no change to charge/voltage.

Where are you seeing a firmware upgrade for your model? There is none so that is why I am curious. SUA model UPSs are not field upgradable. Perhaps it is a PowerChute update? Can you provide a screenshot of where you see this and I can guide you?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:26 AM . Last Modified: ‎2024-03-12 03:04 AM

0 Likes
0
1606
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:26 AM . Last Modified: ‎2024-03-12 03:04 AM

Ok, that is misleading and wouldn't apply to you. It is really an SNMP MIB available for your UPS if you use a UPS Network Management Card with your UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:26 AM . Last Modified: ‎2024-03-12 03:04 AM

0 Likes
0
1607
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:26 AM . Last Modified: ‎2024-03-12 03:04 AM

2392_APC Upgrade.png

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:26 AM . Last Modified: ‎2024-03-12 03:04 AM

0 Likes
0
1607
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:26 AM . Last Modified: ‎2024-03-12 03:04 AM

Hi

The UPS can be calibrated using RS232 Port. for proper battery PACK and runtime.

Make sure you have the following:

1) PC with RS232 Port

2) APC RS232 Communication cable supplied with UPS

3) Hyperterminal software running in the PC

3) Teamviewer ver 9 loaded on to the PC with RS232 (for remote access)

4) UPS to be connected thru RS232 with the PC

5) No Load should be connected to the UPS

6) the UPS should be kept on.

Let set ups a time and we can perform the calibration thru Teamviewer

Thanks

- Muthu

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:26 AM . Last Modified: ‎2024-03-12 03:03 AM

0 Likes
0
1607
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:26 AM . Last Modified: ‎2024-03-12 03:03 AM

The only port I can use is USB. I wish there was a simpler way to calibrate this Smart-Ups. Every time there is power failure the battery drops to around 87%. With power restored and soon failed the battery level dropped from 87% to 67%. There was a load of <10%. It did take a long time to recharge again to 100%. Is it because the ups is not properly calibrated this is happening. The batteries are brand new.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:26 AM . Last Modified: ‎2024-03-12 03:03 AM

0 Likes
0
1605
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:26 AM . Last Modified: ‎2024-03-12 03:03 AM

Did you update the battery pack quantity? The percentage of battery capacity is based on the capacity thinks it has. If it cannot "see" or update based on the amount of batteries connected, this percentage could be misleading.

You can issue a runtime calibration though PowerChute Business Edition or just try a manual one here, assuming you updated the external battery pack count in PowerChute at least. Instructions on a manual runtime calibration (option 3) is here -> Why are the battery charge LEDs flashing on a Smart-UPS? | FAQs | Schneider Electric US

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:26 AM . Last Modified: ‎2024-03-12 03:03 AM

0 Likes
0
1605
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:26 AM . Last Modified: ‎2024-03-12 03:03 AM

I did set the battery count to 2 and it shows around 700+ minutes with 10% load.I hope the PCBE software has the AH option in future updates.  But when power fails the battery level drops very fast. The battery LEDs also go off one by one with time. I have heard about problems with calibration constant, so maybe I should just call support and tell them to update it for me. This document came with my UPS which considers battery bank of 80AH http://www.apcmedia.com/salestools/ASTE-6Z8LB7/ASTE-6Z8LB7_R0_EN.pdf

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of