SUA1000I battery connector. Where I can buy this part?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUA1000I battery connector. Where I can buy this part?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
118
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-07-07 10:11 PM . Last Modified: β€Ž2024-03-04 10:59 PM

0 Likes
7
2936
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-07 10:11 PM . Last Modified: β€Ž2024-03-04 10:59 PM

SUA1000I battery connector. Where I can buy this part?

Hello!

I need this thing:

xiqsVXHEc1liuX93MKeM2g%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpegxiqsVXHEc1liuX93MKeM2g%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg

This thing called like "battery connector". Right? Is that possible to buy it from APC? Esp. in Russia.

Thank you!

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • battery-connector
  • connector
  • sua1000i
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-07-07 10:11 PM . Last Modified: β€Ž2024-03-04 10:55 PM

0 Likes
0
2937
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-07 10:11 PM . Last Modified: β€Ž2024-03-04 10:55 PM

indeed, soldering all kind of plugs are always the best solution!!

i have a yacht at sea, its mandatory to solder all joints of plugs and wires because it oxidate within a year if not soldered...similar thing is in cars with millions of plugs....most of plugs goes burnt because of weak joint or oxidation of joint......i have repair tons of air conditioning fan connectors with 3-4 speeds selector especially coz of that problem....after i crimp+solder the new ones, it never got back on service for that reason anymore πŸ™‚

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Anonymous user
Not applicable

Posted: β€Ž2021-07-07 10:11 PM . Last Modified: β€Ž2024-03-04 10:59 PM

0 Likes
0
2937
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-07 10:11 PM . Last Modified: β€Ž2024-03-04 10:59 PM

this is 60 Ampere fuse (see the top of fuse for number)....you can buy it in any store with electronics, so as "fast on" connecting plugs 4 pcs and 2 pcs of wire 4mm^2 you need.....so you can assemble it by yourself in less then 5 minutes...

i have few dozens of original fuses like that, i can sell you few for few bucks, but i am afraid how shipping price will be expensive if you are out of EU 😞

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: β€Ž2021-07-07 10:11 PM . Last Modified: β€Ž2024-03-04 10:56 PM

0 Likes
0
2937
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-07 10:11 PM . Last Modified: β€Ž2024-03-04 10:56 PM

I see from your picture that one of the F2 terminals (the white part in the top right of the picture) appears to have some heat damage (yellowing). That generally indicates a poor connection (high current + poor connection = high heat).

The fuse itself is just the blue piece. I don't know of any place that sells the complete assembly - when I need them, I make the cables myself.

I believe this is a connector from a battery pack. If you purchase a genuine APC RBC, it should come with the fuse and other components already installed.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-07-07 10:11 PM . Last Modified: β€Ž2024-03-04 10:55 PM

0 Likes
0
2937
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-07 10:11 PM . Last Modified: β€Ž2024-03-04 10:55 PM

Thanks for the reply.

I need this part brand new, because I want to sell this UPS. And this connector is damaged more than it seems on the first photo:

GvlqPQMdH72lpvr6gTcCTQ%3D%3D.jpegGvlqPQMdH72lpvr6gTcCTQ%3D%3D.jpeg

This connector was damaged because of batteries - swelled, so I had to disassemble UPS to remove them:

XtirSZLPTXmjMwN2LUg5xQ%3D%3D.jpegXtirSZLPTXmjMwN2LUg5xQ%3D%3D.jpeg

It is not uncommon for this model, I'll tell you 😞

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: β€Ž2021-07-07 10:11 PM . Last Modified: β€Ž2024-03-04 10:55 PM

0 Likes
0
2937
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-07 10:11 PM . Last Modified: β€Ž2024-03-04 10:55 PM

The metal part of the connector is AMP / Tyco 790319-3. One vendor of this part is Newark / Element14 - Link

The white plastic cover is AMP / Tyco 154719-1. Newark / Element14 - Link

Note that the connectors are crimped onto the wire with specialized (expensive) tooling. Also, please remember that is not supported or recommended by APC.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-07-07 10:11 PM . Last Modified: β€Ž2024-03-04 10:55 PM

0 Likes
0
2937
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-07 10:11 PM . Last Modified: β€Ž2024-03-04 10:55 PM

hey, lets not make a "rocket science" about simple "fuse bridge" :))

to make it simple; it just needs to cut the old and damaged "fast on" plugs and plastic covers, buy a new one in any electronics or electric equipment&material shop for 10-15 cents per piece, crimp it with simple small pliers, put the plastic covers on and AMEN,....thats it....simplest, fastest and cheapest solution, but still professional .....and fact that "fuse bridge" will be 10mm shorter doesnt chage the originality of that bridge...nor it changes performance of battery or UPS.....the matter fact, that fuse bridge should be as short as possible, because it is increasing "internal resistance" of battery if we speak in manner of "rocket science" about performance...

the best solution for stacking batteries in serial connection would be if we could connect plus of one battery with minus of other battery directly with a bridge not longer then 10mm and solder it to make a solid joint that cant oxidate by time and increase internal resistance off battery pack....but soldering isnt practical for several reasons, but thats for another topic πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: β€Ž2021-07-07 10:11 PM . Last Modified: β€Ž2024-03-04 10:55 PM

0 Likes
0
2937
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-07 10:11 PM . Last Modified: β€Ž2024-03-04 10:55 PM

The original poster asked what the part was and where he could buy it, and I told him. tongue-out

The days of going to a nearby electronics store and buying a part like that are long gone, at least here in the US. If the original poster is in the US, send me a friend request so you can PM me, and I'll throw a couple in an envelope and send them out.

The only thing I disagree with in your reply is the "crimp it with simple small pliers" bit - it is very hard to get a good crimp connection with pliers, especially if the connection will be carrying a lot of current. If the correct crimper is not available, I would strongly suggest making as good a connection as possible with pliers and then soldering the wire into the connector.

Of course, an APC RBC will come pre-wired with the fuse. But I can understand the desire to save money.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-07-07 10:11 PM . Last Modified: β€Ž2024-03-04 10:55 PM

0 Likes
0
2938
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-07 10:11 PM . Last Modified: β€Ž2024-03-04 10:55 PM

indeed, soldering all kind of plugs are always the best solution!!

i have a yacht at sea, its mandatory to solder all joints of plugs and wires because it oxidate within a year if not soldered...similar thing is in cars with millions of plugs....most of plugs goes burnt because of weak joint or oxidation of joint......i have repair tons of air conditioning fan connectors with 3-4 speeds selector especially coz of that problem....after i crimp+solder the new ones, it never got back on service for that reason anymore πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of