SUA 1500i AVR Boost on permanently

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SUA 1500i AVR Boost on permanently
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Wnug
Wnug
Cadet

Posted: ‎2024-09-15 09:57 AM . Last Modified: ‎2024-09-15 09:59 AM

0 Likes
3
428
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-15 09:57 AM . Last Modified: ‎2024-09-15 09:59 AM

SUA 1500i AVR Boost on permanently

Hi. Can anyone offer any advice please? I have an APC SUA1500i. Recently the AVR Boost orange LED came on and the transformer is buzzing. It remains permanently on all the time now with or without load. I have checked the input voltage and it is a solid 240v (UK) but the UPS is reporting 194v through Powerchute. I have tested it on another outlet with the same result. I have set the sensitivity to Low and have dropped to the lowest voltage range in the input voltage parameters in Powerchute. There are no warnings or errors in Powerchute. Should I swap out the 5 AVR relays on the main board or will it be something else? Thanks! Winston.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Teken
Janeway Teken
Janeway

Posted: ‎2024-09-16 04:49 AM

0 Likes
2
387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-16 04:49 AM

Hi Winston,

 

Please complete the brain dead reset process and report back what you see and observe once completed:

 

https://www.apc.com/us/en/faqs/FA156611/

 

Please call out the serial number of the system as well. 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Wnug
Wnug
Cadet

Posted: ‎2024-09-16 07:19 AM

In response to Teken
0 Likes
1
366
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-16 07:19 AM

Hi! Thanks for your reply. I previously completed a brain dead reset on it and it performed a self test and came back up normally, albeit AVR Boost kicking in as soon as you connect it to an outlet. I then took it apart 😊. Is there anything in particular I need to look out for if I were to do try another BD reset? Serial number is AS0201110136.

 

Thanks! 👍🏽

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Janeway Teken
Janeway

Posted: ‎2024-09-18 03:55 AM

In response to Wnug
0 Likes
0
360
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-18 03:55 AM

Your system is very old more specifically it’s from 2002! 🫨

 

If possible move the unit to another home / building. Measure the input voltage to determine its 240 VAC. If so apply AC Mains to the system and report back if the system remains in AVR Mode.

 

As you stated earlier about changing the power quality and transfer voltages. Change both to the default settings and transfer voltage back to the default settings.

 

Complete the brain dead procedure again. Once complete power up the system without the battery cartridge attached what happens?!?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of