APC SMART UPS C1500 has L.02 warning but no amber lights. Replace battery?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC SMART UPS C1500 has L.02 warning but no amber lights. Replace battery?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
143
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
FrozenTundra
FrozenTundra
Cadet

Posted: ‎2023-04-06 11:16 AM

1 Like
8
40334
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-06 11:16 AM

APC SMART UPS C1500 has L.02 warning but no amber lights. Replace battery?

Hi There! I am hoping to get some good advice because I am at a loss at the moment. 

 

One of my APC SMART UPS C1500 Batteries has been displaying the L.02 warning on the screen for the past week or so. The manual says the L.02 warning indicates "LIFETIME EXCEEDED"  I was initially working with our IT company to get this diagnosed and fixed. They said I should replace the battery. Unfortunately the battery is sold out on the APC website at the moment. The It company we are contracted with were unable to help me find it anywhere else and said I needed to reach out to a local IT company for additional help . We never had to do that in the past - so now I am scrambling to find a local IT company to partner with that will take weeks- a month to set up. 

 

The biggest issue is I will be leaving to be out of town for two weeks. Where I am going will require 12 hours of travel time to reach the destination, so I could not hop on a plane and get back to the office very quickly/easily. I am very concerned about leaving when this is still an issue.

 

So I have a few questions...

 

1. The light is still solid green, indicating it is online. That has not changed since the L.02 warning popped up.

2. The battery light (top right corner - across from the green light) has not turned green or amber. 

3. The lights have not blinked/turned amber/no warning sounds are coming from the device

 

Considering all of the above, will this device be healthy enough to last until I return 4/28? When that warning displays do you typically have 30 days to replace or should it be done immediately? I am going to order the battery while I am gone so it is there waiting when I land so I can go straight to the office to replace the battery. I am hoping due to the fact that it is online and there are no amber lights that is a good sign. 

 

I know this is lengthy I just tried to include as much info as possible. If you have made it this far- THANK YOU. I truly appreciate all of your time and expertise. 

 

 

Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
lanman
lanman
Cadet

Posted: ‎2023-04-12 10:39 AM

0 Likes
0
40250
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-12 10:39 AM

Same issue here but don't know the solution.

Reply

Link copied. Please paste this link to share this article on your social media post.

Wilspin
Wilspin
Cadet

Posted: ‎2023-06-07 11:59 AM

0 Likes
0
39335
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-06-07 11:59 AM

I also have one. From what I understand that is hardware error code. APC does not publish or make the list of codes available. you need new unit if brain dead reset wont work see;

https://community.spiceworks.com/topic/2166304-apc-smart-ups-error-codes

Reply

Link copied. Please paste this link to share this article on your social media post.

DSJones15
DSJones15
Cadet

Posted: ‎2023-10-05 09:10 AM

0 Likes
0
36178
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-10-05 09:10 AM

Were you getting an L.01 code before the L.02 code came up?

There are APC batteries available on Amazon (surprise, surprise), but I buy mine locally.

There probably won't be any other errors showing for the batteries as long as the system has AC power, as the batteries are hot swappable, assuming (gasp) that this error only refers to the battery and not the entire unit.

I am NOT an expert on these and my experience is limited.

I am still trying to determine if this error (L.01) and yours (L.02) are referring to the batteries or the entire unit.

I will find that out today when I replace the batteries on mine.

Reply

Link copied. Please paste this link to share this article on your social media post.

Pavigo
Crewman Pavigo
Crewman

Posted: ‎2023-12-17 09:56 PM . Last Modified: ‎2023-12-19 08:46 PM

2 Likes
1
33898
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-12-17 09:56 PM . Last Modified: ‎2023-12-19 08:46 PM

I was able to reset code by saying that battery was replaced.

 

To enter to configuration mode hold the MUTE and MENU buttons together for 2 seconds until the system emits a short beep and the display will flash to indicate the UPS has entered Configuration Mode.

When in Configuration Mode, the MENU button cycles the display through the available options.

The MUTE button toggles the configuration settings for that option.

 

rb.0 - Did not replace battery (default)

rb.1 - Battery has been replaced Select rb.1 to indicate that the battery has been replaced, this will reset the constants for the battery runtime calibration to the default for a new battery.

 

So, press 'menu'  several times until you see    rb0, then press 'sound' button  to change it to rb1, then 'menu' to save changes

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Pavigo
Crewman Pavigo
Crewman

Posted: ‎2023-12-19 08:53 PM

1 Like
0
33823
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-12-19 08:53 PM

replaced batteries with 

SLA12-7F2 Duracell Ultra 12V 7AH AGM SLA Battery with F2 Terminals

Reply

Link copied. Please paste this link to share this article on your social media post.

Wilspin
Wilspin
Cadet

Posted: ‎2023-12-21 09:11 AM

In response to Pavigo
0 Likes
0
33725
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-12-21 09:11 AM

Nope did not work for me. I get an error when trying to set the replace battery.  

Reply

Link copied. Please paste this link to share this article on your social media post.

DenisAllard
Crewman DenisAllard
Crewman

Posted: ‎2024-02-09 01:09 PM

2 Likes
0
32001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-09 01:09 PM

Pavigo you are the king.  My C1500 was displaying the L.01 error code ever since I got two new USANDBATTERY replacements more than a week ago and the LCD would stay on at all times with this alarm showing.  Tried everything under the sun but would not chance playing with the menu options are they are not documented anywhere that I could find.  But came across this post, cycled to rb.0 to rb.1 in the menu as per your post and I heard a CLICK! All is fixed now.  Thank you so much.  Denis

Reply

Link copied. Please paste this link to share this article on your social media post.

gic
gic
Cadet

Posted: ‎2024-09-18 03:00 AM

0 Likes
0
23297
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-18 03:00 AM

I have an APC C1000 UPS. After hot swapping the battery, I had to fully power down the unit and remove the battery again to clear the original battery error. After this when I started the unit it displayed the error L.02. Using the guide from the above post by Pavigo, I cleared the error. Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore