I was recently given an SU2200NET. It charges fine, but when I connect a serial cable to my PC, the UPS shuts off. Is there a special cable I need?? I downloaded the software from the APCC download pages.
Knovats
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:40 AM . Last Modified: 2024-03-08 02:08 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:40 AM . Last Modified: 2024-03-08 02:08 AM
I was recently given an SU2200NET. It charges fine, but when I connect a serial cable to my PC, the UPS shuts off. Is there a special cable I need?? I downloaded the software from the APCC download pages.
Knovats
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:40 AM . Last Modified: 2024-03-08 02:08 AM
Keith,
The cable is purchaseable here:
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=940%2D0024
The software, PowerChute Business Edition, is available for free download here:
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SFPCBE705
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:40 AM . Last Modified: 2024-03-08 02:08 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:40 AM . Last Modified: 2024-03-08 02:08 AM
Thank You very much.
Keith
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:40 AM . Last Modified: 2024-03-08 02:08 AM
Hi,
You need to use the cable 940-0024 that is shipped with the UPS.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:40 AM . Last Modified: 2024-03-08 02:08 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:40 AM . Last Modified: 2024-03-08 02:08 AM
I was recently given an SU2200NET. It charges fine, but when I connect a serial cable to my PC, the UPS shuts off. Is there a special cable I need?? I downloaded the software from the APCC download pages.
Knovats
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.