A few minutes ago the APC SU2200 momentarily switched to battery and then back again. I wasn't expecting a self test for another 9 days or so. I accessed the web interface and did not find any event logged for the momentary transfer to battery I noticed a short while ago.
All events, including Informational, Warning and Critical, are configured to be logged to the event log. I wonder what happend to the event that I physically witnessed earlier?
Thanks in advance for any insight you may have.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:18 AM . Last Modified: 2024-03-12 11:45 PM
How long was the transfer? Very short transfers of 1-3 seconds may not be recorded. A self test should always log self test started/passed (or failed) and would not show as "on battery."
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:18 AM . Last Modified: 2024-03-12 11:45 PM
How long was the transfer? Very short transfers of 1-3 seconds may not be recorded. A self test should always log self test started/passed (or failed) and would not show as "on battery."
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:18 AM . Last Modified: 2024-03-12 11:45 PM
Two to three seconds. Thank you for the quick response and you have answered my question.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:18 AM . Last Modified: 2024-03-12 11:45 PM
I think it may depend on UPS and what causes the transfer too because I do see one second events recorded in some logs once in a while.