SU1400 overheating with swollen batteries

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SU1400 overheating with swollen batteries
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:42 AM . Last Modified: ‎2024-03-15 04:53 AM

0 Likes
3
1164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:42 AM . Last Modified: ‎2024-03-15 04:53 AM

SU1400 overheating with swollen batteries

My SU1400 was cooking with no alarms - unless you count the sound of the fan running at top speed.

I only noticed because I went down to the basement. It took a couple of hours for the unit to cool down enough for me to work loose the badly swollen batteries. They measured 12.8V.

My supplier tells me that this indicates a failure of the charging circuitry on the UPS. Is there a way for me to test this without batteries?

I have the AP9605 network interface card installed so I should be able to connect to it.

Thank you for your help.
Keith

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:42 AM . Last Modified: ‎2024-03-15 04:53 AM

0 Likes
0
1164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:42 AM . Last Modified: ‎2024-03-15 04:53 AM

Yes, older units like SU1400 need to have batteries installed, more precisely, they need batteries that measure at least 22-23VDC. Since yours probably has shorted cells, it is possible that voltage has dropped well below that, but it is worth a shot. Also you may try without batteries, but if my memory serves right, it will not do anything even with mains power connected. 

I consider inspecting my UPS unit personally every few weeks or months a good practice, there are times like this when you may notice abnormalities well before the UPS could. Proper monitoring over serial or network is a very recommended thing to do if the UPS is to remain out of sight for extended periods of time. Batteries do not deform that badly in short term, it means they could have been bad for more weeks or months even, which places unnecessary stress on the electronics as well. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:42 AM . Last Modified: ‎2024-03-15 04:53 AM

0 Likes
0
1164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:42 AM . Last Modified: ‎2024-03-15 04:53 AM

If your batteries are more than 3 years old and your setup is a set-it and forget-it type (located in basement) it is possible that the batteries are simply worn out. Regular self test on the UPS ensures that it detects faulty battery, provided that self test is enabled on the unit. Sounds like your batteries have internally their cells shorted. This type of failure can be detected by the ups with briefly transferring the load to battery, if there is no battery capacity, it will indicate battery failure. Without this self test enabled, the UPS assumes the shorted cells to be depleted batteries, thus force charging current in them, without them ever reaching full charge. The charger has obviously not failed since it tries to charge the batteries as we can tell. What is possible though is that the charging voltage is out of range. Too high voltage shortens battery life. Acceptable charge voltage for SU1400 is between 27.1-27.7 VDC, best to be around 27.2-27.3 VDC. 

 

Unofficially speaking (not being an APC employee).  Try the following only at your own risk, and be wary to not to short circuit the electronics, including battery terminals. Dangerous voltages may be present. Attempt only if you are qualified and have the proper tools and accessories. Do not touch anything inside the unit with bare hands, including battery terminals. The following procedure can be undertaken by service center personnel, take it to an authorized service center if you are unsure. 

Charge voltage can be checked by connecting your faulty batteries just so that you can start the unit. After connecting the batteries, plug in the unit to the mains so that charging may start.  Then disconnect UPS negative battery lead from battery terminal, and use a multimeter to measure DC voltage between UPS battery leads positive and the disconnected negative.

 

Anyway, a good indication for the need of battery replacement (if it is not indicated by the ups yet)  is by paying attention to UPS internal temperature, which is reported by the UPS when queried. It is usually above by several degrees of room temperature, and should stay consistent apart from battery operation and after it, battery charging, which generates more heat than usual standby float charging mode. If charger forces excessive current for extended periods of time, standby temperature of the UPS increases which is a good way to help determine that it requires attention. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:42 AM . Last Modified: ‎2024-03-15 04:53 AM

0 Likes
0
1164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:42 AM . Last Modified: ‎2024-03-15 04:53 AM

Thank you Wolf for the detailed reply. I really appreciate you taking the time to help.

My UPS does perform the self test weekly but since it is in the basement, I seldom notice. It is not being monitored by Powerchute though, only by my two QNAP NAS units. I will see if I can write or find a tool to interrogate the temperature and other values so that I can monitor them more closely.

It has been a long time since I have connected to it directly but when it was overheating, there was no indication on the front panel.

The batteries were 28 months old but were not APC batteries. Unfortunately, I left the failed batteries with the company. I will ask if I can get them back for testing.

You wrote:

After connecting the batteries, plug in the unit to the mains so that charging may start

Does this mean I cannot start the unit without batteries? (I haven't tried yet.) I have another smaller Smart-UPS that I can temporarily cannibalize for testing if necessary.

Thank you again,
Keith

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:42 AM . Last Modified: ‎2024-03-15 04:53 AM

0 Likes
0
1165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:42 AM . Last Modified: ‎2024-03-15 04:53 AM

Yes, older units like SU1400 need to have batteries installed, more precisely, they need batteries that measure at least 22-23VDC. Since yours probably has shorted cells, it is possible that voltage has dropped well below that, but it is worth a shot. Also you may try without batteries, but if my memory serves right, it will not do anything even with mains power connected. 

I consider inspecting my UPS unit personally every few weeks or months a good practice, there are times like this when you may notice abnormalities well before the UPS could. Proper monitoring over serial or network is a very recommended thing to do if the UPS is to remain out of sight for extended periods of time. Batteries do not deform that badly in short term, it means they could have been bad for more weeks or months even, which places unnecessary stress on the electronics as well. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore