SU1400 fans running continuously

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SU1400 fans running continuously
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
114
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:23 PM . Last Modified: ‎2024-03-14 04:34 AM

0 Likes
7
1487
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:23 PM . Last Modified: ‎2024-03-14 04:34 AM

SU1400 fans running continuously

We have quite a few SU1400's around. Most are on their third (or more) battery. A few found their way into office environments as we switched to newer APC RM UPS's and larger APC UPS's in server rooms and network closets where HVAC and equipment fans drown out any fan noise the UPS's make. A while ago I noticed the fans on some of the SU1400 fans were always running but not on all our SU1400's.

That seemed weird so I did searches on the Internet and on this forum. I saw other people reporting the same problem, but the only precise explanation I saw was the possibility the problem was a bad temperature sensor.

I put a new replacement battery (an genuine APC brand RBC7) in a SU1400 last week and noticed it's fan was running as well. So that's three I've noticed doing the same thing (now that I'm aware of this I'll have to check other SU's in other areas) and that's what made me curious. Is it possible these three all have bad temperature sensors?

Because these tend to power things like switches there is no where to run the PowerChute software, but I tried the serial port on one with the factory 940-1524C Smart Signal cable) and it returned a status of 33AC (is it true that 8C means "normal"?). What does 33AC mean? This particular battery was purchased and installed in 2/2007 so it's not real old and it has led an easy life (only a couple significant outages, a light load: 2 LEDs) and either machine room or office temperatures and humidity. If I recall correctly, that battery was installed when the old one failed the SU self-test. I think this battery was a genuine APC replacement. And I think the fan has been running since that battery was replaced. All three UPS's seem to work fine other than the fan issue. All three pass a manually initiated self-test.

Any suggestions/explanations? Thanks in advance.

Message was edited by: El_Kabong: Fixed a type and added the word "precise" to the second paragraph.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 10:23 PM . Last Modified: ‎2024-03-14 04:33 AM

0 Likes
0
1485
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:23 PM . Last Modified: ‎2024-03-14 04:33 AM

As far as I know, APC Smart UPS 1400 Battery floating voltage is 27.4 Vdc(Approximately). Thus, the voltage 27.9 Vdc is no harm to the batteries. However, if the unit tries to charge the bad battery, the battery will become warm and possibly vent or swell. Did you replace the batteries with genuine APC Replacement Battery Cartridge(RBC)? Batteries can also be damaged if the environment they are used in is too warm.

Click on the below link to know the Smart UPS Battery Charger Technology:
http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=1516

You may review the Material Safety Data Sheet for the batteries which APC use. You can download the MSDS through the below document.
http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=564

My advise to you is that replace the UPSs with new Smart UPSs if they are pretty old instead of replacing the batteries.

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 10:23 PM . Last Modified: ‎2024-03-14 04:34 AM

0 Likes
0
1485
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:23 PM . Last Modified: ‎2024-03-14 04:34 AM

The fans on an SU unit will run for the following reasons:

1. The UPS is on battery.
2. The UPS is charging the battery.
3. The UPS has a load greater than 75%.
4. The internal temperature of the UPS has reached greater than 140 degrees F (60 degrees C).

El_Kabong wrote:
I tried the serial port on one with the factory 940-1524C Smart Signal cable) and it returned a status of 33AC (is >it true that 8C means "normal"?). What does 33AC mean?
What did you input to the UPS to get this response? The unit does not report anything via hyperterminal without an input.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:23 PM . Last Modified: ‎2024-03-14 04:34 AM

0 Likes
0
1485
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:23 PM . Last Modified: ‎2024-03-14 04:34 AM

Thanks (I saw that info earlier in search results). As I mentioned above the SU1400 I'm currently looking at is in an office environment, lightly loaded and passes the manual battery test so the only thing on that list I can't confirm is whether the battery is charging.

8C is supposedly the normal response for shift y zero which appears to be the SU's battery capacity estimate perhaps?

Message was edited by: El_Kabong: s/light/lightly/

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 10:23 PM . Last Modified: ‎2024-03-14 04:34 AM

0 Likes
0
1485
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:23 PM . Last Modified: ‎2024-03-14 04:34 AM

The Power Chute Business Edition software can allow you to view the UPS's internal temperature. This will help us to determine if the temperature is the root cause of the fan operation. It also allows you to view the UPS battery capacity and runtime. Please verify if the UPS runtime which is shown on the software is correct.

Please do not input any commands at terminal screen if you do not know why the Shift...command is used for. Entering a wrong value may damage the UPS.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:23 PM . Last Modified: ‎2024-03-14 04:34 AM

0 Likes
0
1485
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:23 PM . Last Modified: ‎2024-03-14 04:34 AM

I have 2 SU1400s that exhibit the same behavior. Unit #1 wound up destroying its battery by overcharging (battery ruptured). I set that unit aside and haven't used it since last fall. Now unit #2 is beginning to show the same behavior.

Unit #2's battery is exactly 15 months old today so it's not new but it's not excessively old. According to the logs, there have been 11 power transfers since this battery was installed (most were 2-3 second blips; one was 21 minutes which I'd estimate brought the battery down to 60% charge). Add to this the automatic self tests that occur every 14 days. So all-told, this battery hasn't seen a lot of use.

I'm running APCUPSD as the power daemon. It reports currently:

BCHARGE : 100.0 Percent
ITEMP : 27.9 C Internal
BATTV : 27.9 Volts

So the temperature and battery charge and voltage appear to be okay? Yet the UPS' charging circuit appears to be wedged "on". The battery is very warm.

This is the same behavior that I saw with the other SU1400. Its battery got so hot that it was audibly sizzling when I disconnected it from the UPS.

Any ideas?

edit: I should have mentioned that current load is 19.2%

Message was edited by: jrmayfield

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 10:23 PM . Last Modified: ‎2024-03-14 04:33 AM

0 Likes
0
1486
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:23 PM . Last Modified: ‎2024-03-14 04:33 AM

hmm...If you have another working Identical UPS, swap the batteries between the working unit and the unit in question. Then, check if the UPS in question runs the fan always with the other good known batteries installed.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:23 PM . Last Modified: ‎2024-03-14 04:33 AM

0 Likes
0
1486
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:23 PM . Last Modified: ‎2024-03-14 04:33 AM

Thanks, Techie. I borrowed a battery pack from an SU1500 to test. With the borrowed pack, the fan turns off after a few seconds just like it should. Turns out the old 15-month-old batteries were swollen to the point of leaking around the top (thank goodness for baking soda). I hadn't noticed this when I posted last night. So I guess it was a dead battery.

I'm curious though about what happened. The firmware was reporting battery voltage of 27.9V and 100% charge yet the charger was apparently still active. This suggests that either the firmware uses some other criteria for controlling the charger or the charger became "stuck" and killed the battery. Hopefully the former. Can you shed any light on this?

(Seems like the UPS should have some sort of failsafe that prevents the charger from overcharging a dead battery to the point of bursting. Perhaps by monitoring battery temperature...last night's battery was quite warm even though the it hadn't reached the point of audibly sizzling/hissing like the Unit #1's battery last fall).

Also, I'm curious about the reported battery voltage. The firmware was showing 27.9V for the bad battery. Is 27.9V too high? A scan through this forum turns up a message from August 2008 that says anything above 27.7V means the charging circuit is broken. Is this true? I'd hate to buy a replacement battery pack only to find out that the charging circuit has a fault.

Jimmie

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 10:23 PM . Last Modified: ‎2024-03-14 04:33 AM

0 Likes
0
1486
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:23 PM . Last Modified: ‎2024-03-14 04:33 AM

As far as I know, APC Smart UPS 1400 Battery floating voltage is 27.4 Vdc(Approximately). Thus, the voltage 27.9 Vdc is no harm to the batteries. However, if the unit tries to charge the bad battery, the battery will become warm and possibly vent or swell. Did you replace the batteries with genuine APC Replacement Battery Cartridge(RBC)? Batteries can also be damaged if the environment they are used in is too warm.

Click on the below link to know the Smart UPS Battery Charger Technology:
http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=1516

You may review the Material Safety Data Sheet for the batteries which APC use. You can download the MSDS through the below document.
http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=564

My advise to you is that replace the UPSs with new Smart UPSs if they are pretty old instead of replacing the batteries.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of