SU VTP 30K - DC voltage
  • SU VTP 30K - DC voltage
5060
142
Posted: ‎2021-06-26 03:49 AM . Last Modified: ‎2024-03-19 01:37 AM
1024
Could anyone inform me what is the battery pack DC voltage for SU VTP 30K?
Aldar
  • Data Center & Facility 3 Phase UPS
Posted: ‎2021-06-26 03:49 AM . Last Modified: ‎2024-03-19 01:36 AM
Aldar
Replies 5
just a follow up..
it is a common neutral in the system, if you are using dual mains then you must supply 4W plus ground, same as mains input.
i'll have to double check monday but i saw it noted as "split battery referenced to neutral."
i'll follow up monday for you 😉
Thank you!
+/-192 VDC means there are 2 rows of 192VDC with one common point? Like:
+192 <----------> 0 <---------------> -192
I I I
I I I
I-----------------------I-----------------------I
What confuses me, this common point "0" is also used to wire neutral (N) of second mains (when dual mains are used). Is it right?
Thanks.
Message was edited by: Aldar - corrected "drawing"
Thank you very much!
Dual mains are not used. Indeed this DC wiring is correct, UPS is now running.
Just for information, the 3 phase input must be wired in some particular order, otherwise UPS gives "wiring fault". Like L2 shifted forward by 120deg comparing to L1.
Aldar
Aldar