SRT5KXLI built-in management card lightshow

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SRT5KXLI built-in management card lightshow
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Firemann
Firemann
Cadet

Posted: ‎2024-05-08 05:32 AM

0 Likes
3
398
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-08 05:32 AM

SRT5KXLI built-in management card lightshow

My SRT5KXLI Lan port is performing a lightshow, when lan cable is connected.
It starts with orange light left side on connector flashes apx. 5 times, then 1 flash on the right led, then the right led flashes orange and yellow quickly for 5 sec. then is repeats.
Seems like it reboots endless.

I have hold the reset for 25 sec, same result.

In the menu on front, I can't see the IP settings menu.

Any idea why?

Can I reach it by serial comm?
Can I buy an new Network Management card to the expantion slot?

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Teken
Janeway Teken
Janeway

Posted: ‎2024-05-08 07:42 AM . Last Modified: ‎2024-05-08 07:48 AM

0 Likes
2
384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-08 07:42 AM . Last Modified: ‎2024-05-08 07:48 AM

Without knowing anything related to your network here are some basic things to validate and try:

 

Disconnect the Ethernet cable from the NMC. Remove the NMC (It’s hot swappable) from the unit and wait ten seconds than reinstall.


Once the UPS sees the NMC the right LED will alternate from green / orange while the Ethernet cable is still disconnected.

 

Do you see this behaviour? If yes continue to connect the Ethernet cable to the NMC. Once a properly configured network is seen the NMC LEDS will be solid green on the right and blinking orange on the left to indicate network activity / traffic.

 

Does the NMC LED’s behave as outlined here?!?

 

An interim test is to isolate the NMC and connect it to portable router. If the NMC is set to DHCP a new IP Address should be provided and leased out.

 

If the NMC has been assigned a Static IP Address you can either format the NMC to bring it back to a OEM Default state.

 

Or connect to it with the supplied APC Serial cable over SSH / Telnet. You can than check the CLI and validate all network attributes are correct such as DHCP / Static, subnet, gateway, DNS, etc.


Let me know what you see and observe. 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Firemann
Firemann
Cadet

Posted: ‎2024-05-13 02:38 AM

In response to Teken
0 Likes
1
312
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-13 02:38 AM

Thanks for your suggestions, but the NMC is builtin on the mailboard on this model.

I'm considering buying a NMC for the slot, but I not sure that it will work with 2 NMC modules. (When one is faulty)

I have reset the NMC to default, and still same result.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Janeway Teken
Janeway

Posted: ‎2024-05-13 04:35 AM

In response to Firemann
0 Likes
0
305
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-13 04:35 AM

In case you did not complete the format procedure here it is.

 

Option 1 is referred to as "formatting" which wipes the AP9631 of all configurations, passwords, TCP/IP settings, etc.


press and hold the reset button for the 20 seconds and if successful, during the holding of the button, you'll see the pulsing green, then pulsing orange, and then you let go. The NMC will reboot and show alternating green and orange rapidly and 20 seconds later, it will have booted back up and reset completely as factory fresh.

 

Let me know what happens. 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of