SRT2200 Erroneous 0x0119 Battery needs replacement

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SRT2200 Erroneous 0x0119 Battery needs replacement
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
john.bayly
Crewman john.bayly
Crewman

Posted: ‎2024-10-07 01:59 AM . Last Modified: ‎2024-10-07 02:00 AM

0 Likes
3
2152
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-07 01:59 AM . Last Modified: ‎2024-10-07 02:00 AM

SRT2200 Erroneous 0x0119 Battery needs replacement

I have a Smart-UPS SRT 2200 which is reporting that Internal pack needs replacement. It's a bit strange as this was replaced in November 2021, along with the two in the EBM (which report as OK)

This is the error reported:

 

 

Serial Number : xxxxx
Device Serial Number : xxxxx
Date : 10/04/2024
Time : 13:36:34
Code : 0x0119

Critical - UPS: Battery needs replacement. Order replacement battery, APCRBC141, for the internal pack, cartridge 1.

 

 

It's reporting that the health is OK and the replacement date is in 2026, yet the pack needs replacement.

johnbayly_0-1728291176868.png

I've removed the pack and tested the voltage, thinking it may be low. But it is 80V, which seems a little high for a 72V nominal voltage.

 

I've tried, will try the following, but has anyone got a suggestion?

  • Put UPS into bypass and removed pack (in order to test voltage), and reinstalled
  • Restarted the Network Management Card
  • UPS Self-Test - Passed
  • TODO: Check individual cell voltages for any outliers

Many thanks.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
john.bayly
Crewman john.bayly
Crewman

Posted: ‎2024-10-07 09:26 AM

0 Likes
0
2107
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-07 09:26 AM

After an online chat to APC, which asked me to go through the steps I had done. I did the following:

  1. I swapped out a pack from a good UPS
  2. Update the month to now
  3. Everything was good
  4. Swapped out the "bad" pack and entered the original month (Nov 2021)
  5. Everything is still good

When I had removed the pack the other day and tested the voltage, I had simply scrolled the month up and down a few times, but that obviously doesn't reset the alarm.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
john.bayly
Crewman john.bayly
Crewman

Posted: ‎2024-10-07 09:26 AM

0 Likes
0
2108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-07 09:26 AM

After an online chat to APC, which asked me to go through the steps I had done. I did the following:

  1. I swapped out a pack from a good UPS
  2. Update the month to now
  3. Everything was good
  4. Swapped out the "bad" pack and entered the original month (Nov 2021)
  5. Everything is still good

When I had removed the pack the other day and tested the voltage, I had simply scrolled the month up and down a few times, but that obviously doesn't reset the alarm.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-10-07 10:49 AM

0 Likes
0
2124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-07 10:49 AM

Manually initiate a battery calibration with at least 30% attached load.

 

What are the results of completing the battery calibration procedure?!? 🤔

 

Lastly, as you noted it makes sense to to validate each cell. In case there is a weak cell in the pack which can impact the entire battery cartridge.

 

Let me know the results. 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

john.bayly
Crewman john.bayly
Crewman

Posted: ‎2024-10-08 05:56 AM

0 Likes
0
2099
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-08 05:56 AM

@Teken Thanks. The UPS is used in conjunction with an SRT72BP, so there are 3 packs in total.

 

I had already run a calibration test (in the blind hope that might do something) and the runtime was less than expected - ~23 min from 100% to 27% at 42% load (917W) - but not mind-scratchingly bad. Which could be down to:

  • Batteries being 3 years old
  • The UPS not utilising the internal pack (I suspect this is the case) as the expected run time with 3 new packs is 49min (49 * 2 / 3 = 33)
  • The test stopped at 27%

johnbayly_1-1728392133532.png

I'm going to run another one with a similar load.


I also tested each cell in the pack and they were all above 13V, so it doesn't appear there was a weak cell.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore