Posted: ā2024-10-07 01:59 AM . Last Modified: ā2024-10-07 02:00 AM
I have a Smart-UPS SRT 2200 which is reporting that Internal pack needs replacement. It's a bit strange as this was replaced in November 2021, along with the two in the EBM (which report as OK)
This is the error reported:
Serial Number : xxxxx
Device Serial Number : xxxxx
Date : 10/04/2024
Time : 13:36:34
Code : 0x0119
Critical - UPS: Battery needs replacement. Order replacement battery, APCRBC141, for the internal pack, cartridge 1.
It's reporting that the health is OK and the replacement date is in 2026, yet the pack needs replacement.
I've removed the pack and tested the voltage, thinking it may be low. But it is 80V, which seems a little high for a 72V nominal voltage.
I've tried, will try the following, but has anyone got a suggestion?
Many thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ā2024-10-07 09:26 AM
After an online chat to APC, which asked me to go through the steps I had done. I did the following:
When I had removed the pack the other day and tested the voltage, I had simply scrolled the month up and down a few times, but that obviously doesn't reset the alarm.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ā2024-10-07 09:26 AM
After an online chat to APC, which asked me to go through the steps I had done. I did the following:
When I had removed the pack the other day and tested the voltage, I had simply scrolled the month up and down a few times, but that obviously doesn't reset the alarm.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ā2024-10-07 10:49 AM
Manually initiate a battery calibration with at least 30% attached load.
What are the results of completing the battery calibration procedure?!? š¤
Lastly, as you noted it makes sense to to validate each cell. In case there is a weak cell in the pack which can impact the entire battery cartridge.
Let me know the results. š
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ā2024-10-08 05:56 AM
@Teken Thanks. The UPS is used in conjunction with an SRT72BP, so there are 3 packs in total.
I had already run a calibration test (in the blind hope that might do something) and the runtime was less than expected - ~23 min from 100% to 27% at 42% load (917W) - but not mind-scratchingly bad. Which could be down to:
I'm going to run another one with a similar load.
I also tested each cell in the pack and they were all above 13V, so it doesn't appear there was a weak cell.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of