SRT10KRMXLT - Bypass not in range, high voltage and low voltage messages?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SRT10KRMXLT - Bypass not in range, high voltage and low voltage messages?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:08 AM . Last Modified: ‎2024-03-18 12:05 AM

0 Likes
11
3203
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:08 AM . Last Modified: ‎2024-03-18 12:05 AM

SRT10KRMXLT - Bypass not in range, high voltage and low voltage messages?

Hello,

We have a new SRT10KRMXLT with 5 external battery packs. This unit is set to replace our aging Smart-UPS RT 10000 RM XL. Both units are next to each other being feed from main utility.

We are testing the new unit by cutting power and switching to backup generator, the messages we see are:

  • UPS: On battery power in response to low input voltage.
  • UPS: Bypass not in range ; low voltage.
  • UPS: No longer on battery power.
  • UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.

I am curious about the two highlighted messages, are they normal to receive during a "switch from main to generator test"?

What I would expect is the "On Battery power" and "No longer on battery power" messages; but not sure what to make of the other two notifications the UPS generates?

We also ran into an issue where we got a unexpected "Bypass not in range, high voltage" message from the new UPS but our old UPS did not do anything. So I am thinking, is the new UPS set too sensitive?

Here are the power settings and data log of the new UPS:

MmLBew56%2F11RLL%2B3Y6nDJA%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngMmLBew56%2F11RLL%2B3Y6nDJA%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

Here is the data log for the high voltage notification...

%2BzQ2fRpVVqMIA21L2e7P7g%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png%2BzQ2fRpVVqMIA21L2e7P7g%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

Here are the power settings from our old UPS that did not generate the "high voltage" message.

rJi1kN3Zc2bL3W4toLg51A%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngrJi1kN3Zc2bL3W4toLg51A%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

So what I am wondering, do I need to copy the settings from the old UPS to the new UPS for the power settings of Bypass Upper/Lower Voltage to avoid the "high voltage" message? I have attached the data log.

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:08 AM . Last Modified: ‎2024-03-18 12:05 AM

0 Likes
0
3199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:08 AM . Last Modified: ‎2024-03-18 12:05 AM

HI, 

we Facing the exactly same issue of that, any thing can do to solve that issue?

bob

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:08 AM . Last Modified: ‎2024-03-18 12:04 AM

0 Likes
0
3199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:08 AM . Last Modified: ‎2024-03-18 12:04 AM

I would like to add that this is still an on-going issue for us, been using the UPS for a few months now.

The UPS occasionally throws:

  • UPS: Bypass not in range ; high voltage.
  • UPS: An input voltage or frequency problem no longer prevents switching to b...

The issue clears on itself fairly quickly but this was never observed on our older UPS likely because it was not as sensetive.

We have mains power > diesel generator > UPS.

We've had a electrician on-site a few times to verify everything and they confirmed power coming in is clean and stable.

I tried to adjust the logging in the APC network management card to try and log the event data point to see what the input values are, but have not been able to see anything in the logs that would cause this.

I also worked with APC Support but did not get anywhere.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

jaszadrian_apc
Crewman jaszadrian_apc
Crewman

Posted: ‎2021-06-28 08:09 AM . Last Modified: ‎2024-03-18 12:04 AM

0 Likes
0
3199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:09 AM . Last Modified: ‎2024-03-18 12:04 AM

Hi,

We have a Smart-UPS SRT 10000

About UPS
 
Model: Smart-UPS SRT 10000
SKU: SRT10KXLI

I have the same problem and there is no answer to the problem by the distributors

Date Time Event
  12-Oct-19 02:52:14 UPS: No longer on battery power.
  12-Oct-19 02:52:13 UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.
  12-Oct-19 02:51:49 UPS: Bypass not in range ; low voltage.
  12-Oct-19 02:51:48 UPS: On battery power in response to frequency and phase difference.
  12-Oct-19 02:48:33 UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.

 

 


Smart-UPS SRT 10000
Integrated EMU
Date  Time  Vmin  Vmax  Vout  Iout  %Wout  %out  FrqOut  %Cap  Vbat  Tups  T1ambC  %Hum1  T2ambC  %Hum2 
  Smart-UPS SRT 10000 Integrated EMU
Date  Time  Vmin  Vmax  Vout  Iout  %Wout  %out  FrqOut  %Cap  Vbat  Tups  T1ambC  %Hum1  T2ambC  %Hum2 
 12-Oct-19    03:55:04   0.00   0.00   217.73   8.56   16.50   19.07   51.90   99.00   0.00   19.00   20.0             
 12-Oct-19    03:45:04   0.00   0.00   217.59   8.34   15.99   18.34   51.56   99.00   0.00   19.00   20.0             
 12-Oct-19    03:35:04   0.00   0.00   217.67   8.50   16.38   18.65   51.89   99.00   0.00   19.00   20.0             
 12-Oct-19    03:25:04   0.00   0.00   217.13   8.41   16.22   18.43   51.40   99.00   0.00   19.00   21.0             
 12-Oct-19    03:15:04   0.00   0.00   217.14   8.44   16.32   18.57   51.09   99.00   0.00   20.00   21.0             
 12-Oct-19    03:05:04   0.00   0.00   217.69   8.53   16.52   18.80   51.70   99.00   0.00   21.00   22.0             
 12-Oct-19    02:55:04   0.00   0.00   218.14   8.81   17.16   19.43   51.70   99.00   0.00   20.00   23.0             
 12-Oct-19    02:45:03   0.00   0.00   226.67   8.19   16.38   18.67   50.00   99.00   0.00   19.00   20.0             
 12-Oct-19    02:35:03   0.00   0.00   223.52   8.31   16.46   18.70   50.00   99.00   0.00   19.00   21.0             
 12-Oct-19    02:25:03   0.00   0.00   226.20   8.25   16.56   18.66   50.00   99.00   0.00   19.00   21.0             
 12-Oct-19    02:15:03   0.00   0.00   225.42   8.31   16.63   18.79   50.00   99.00   0.00   20.00   21.0             
 12-Oct-19    02:05:03   0.00   0.00   220.28   8.59   16.79   19.06   50.09   99.00   0.00   20.00   23.0 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:08 AM . Last Modified: ‎2024-03-18 12:05 AM

0 Likes
0
3200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:08 AM . Last Modified: ‎2024-03-18 12:05 AM

HI, 

we Facing the exactly same issue of that, any thing can do to solve that issue?

bob

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:08 AM . Last Modified: ‎2024-03-18 12:05 AM

0 Likes
0
3199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:08 AM . Last Modified: ‎2024-03-18 12:05 AM

Hello - 

Your new UPS is already set at the widest possible settings for bypass and should therefor be less sensitive than the older unit. Do the "Bypass our of Range" messages clear once the unit stabilizes on generator power or are they consistent? Will the UPS function online with the generator input?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:08 AM . Last Modified: ‎2024-03-18 12:05 AM

0 Likes
0
3199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:08 AM . Last Modified: ‎2024-03-18 12:05 AM

HI Laim,

Any instruction of that? please.

Bob

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:08 AM . Last Modified: ‎2024-03-18 12:04 AM

0 Likes
0
3199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:08 AM . Last Modified: ‎2024-03-18 12:04 AM

Basically just checking the unit to see if the alerts clear after the power stabilizes on generator. It might be best to gather the event and data logs from the network management card from the time frame of a generator test. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:08 AM . Last Modified: ‎2024-03-18 12:04 AM

0 Likes
0
3200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:08 AM . Last Modified: ‎2024-03-18 12:04 AM

I would like to add that this is still an on-going issue for us, been using the UPS for a few months now.

The UPS occasionally throws:

  • UPS: Bypass not in range ; high voltage.
  • UPS: An input voltage or frequency problem no longer prevents switching to b...

The issue clears on itself fairly quickly but this was never observed on our older UPS likely because it was not as sensetive.

We have mains power > diesel generator > UPS.

We've had a electrician on-site a few times to verify everything and they confirmed power coming in is clean and stable.

I tried to adjust the logging in the APC network management card to try and log the event data point to see what the input values are, but have not been able to see anything in the logs that would cause this.

I also worked with APC Support but did not get anywhere.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:08 AM . Last Modified: ‎2024-03-18 12:04 AM

0 Likes
0
3199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:08 AM . Last Modified: ‎2024-03-18 12:04 AM

Hi Mirza - 

Was the electrician able to look at the line with a scope while the UPS was giving the Bypass not in range messages?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:08 AM . Last Modified: ‎2024-03-18 12:04 AM

0 Likes
0
3199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:08 AM . Last Modified: ‎2024-03-18 12:04 AM

No, because this would happen randomly.. like once a week... hard to time an electrician on-site if this is totally random.

I was hoping I could catch something using the APC Management Card but the data log interval range starts at 1 minute, we would need much more granular log interval (down to a second).

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:09 AM . Last Modified: ‎2024-03-18 12:04 AM

0 Likes
0
3199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:09 AM . Last Modified: ‎2024-03-18 12:04 AM

I think your only option would be a recording scope that could be left on the line for an extended period of time. The network card in the UPS just doesn't offer the same level of detail that a true scope would. From there you could hopefully back track and narrow down the cause of the disturbance. In the meantime, your UPS will function just fine and it will not allow your unit to switch to bypass should there be a potentially dangerous power issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

jaszadrian_apc
Crewman jaszadrian_apc
Crewman

Posted: ‎2021-06-28 08:09 AM . Last Modified: ‎2024-03-18 12:04 AM

0 Likes
0
3200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:09 AM . Last Modified: ‎2024-03-18 12:04 AM

Hi,

We have a Smart-UPS SRT 10000

About UPS
 
Model: Smart-UPS SRT 10000
SKU: SRT10KXLI

I have the same problem and there is no answer to the problem by the distributors

Date Time Event
  12-Oct-19 02:52:14 UPS: No longer on battery power.
  12-Oct-19 02:52:13 UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.
  12-Oct-19 02:51:49 UPS: Bypass not in range ; low voltage.
  12-Oct-19 02:51:48 UPS: On battery power in response to frequency and phase difference.
  12-Oct-19 02:48:33 UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.

 

 


Smart-UPS SRT 10000
Integrated EMU
Date  Time  Vmin  Vmax  Vout  Iout  %Wout  %out  FrqOut  %Cap  Vbat  Tups  T1ambC  %Hum1  T2ambC  %Hum2 
  Smart-UPS SRT 10000 Integrated EMU
Date  Time  Vmin  Vmax  Vout  Iout  %Wout  %out  FrqOut  %Cap  Vbat  Tups  T1ambC  %Hum1  T2ambC  %Hum2 
 12-Oct-19    03:55:04   0.00   0.00   217.73   8.56   16.50   19.07   51.90   99.00   0.00   19.00   20.0             
 12-Oct-19    03:45:04   0.00   0.00   217.59   8.34   15.99   18.34   51.56   99.00   0.00   19.00   20.0             
 12-Oct-19    03:35:04   0.00   0.00   217.67   8.50   16.38   18.65   51.89   99.00   0.00   19.00   20.0             
 12-Oct-19    03:25:04   0.00   0.00   217.13   8.41   16.22   18.43   51.40   99.00   0.00   19.00   21.0             
 12-Oct-19    03:15:04   0.00   0.00   217.14   8.44   16.32   18.57   51.09   99.00   0.00   20.00   21.0             
 12-Oct-19    03:05:04   0.00   0.00   217.69   8.53   16.52   18.80   51.70   99.00   0.00   21.00   22.0             
 12-Oct-19    02:55:04   0.00   0.00   218.14   8.81   17.16   19.43   51.70   99.00   0.00   20.00   23.0             
 12-Oct-19    02:45:03   0.00   0.00   226.67   8.19   16.38   18.67   50.00   99.00   0.00   19.00   20.0             
 12-Oct-19    02:35:03   0.00   0.00   223.52   8.31   16.46   18.70   50.00   99.00   0.00   19.00   21.0             
 12-Oct-19    02:25:03   0.00   0.00   226.20   8.25   16.56   18.66   50.00   99.00   0.00   19.00   21.0             
 12-Oct-19    02:15:03   0.00   0.00   225.42   8.31   16.63   18.79   50.00   99.00   0.00   20.00   21.0             
 12-Oct-19    02:05:03   0.00   0.00   220.28   8.59   16.79   19.06   50.09   99.00   0.00   20.00   23.0 
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:09 AM . Last Modified: ‎2024-03-18 12:04 AM

0 Likes
0
3199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:09 AM . Last Modified: ‎2024-03-18 12:04 AM

I continue to have this problem, few times a month I get alerts from the UPS related to input frequency issues and also battery pack disconnects but everything seems to work fine (we do regular testing of switching from main to generator and for a few seconds the UPS kicks in).

I spent days working with APC support when we installed the UPS and eventually just gave up, I had an electrician verify everything and do input/output readings using probes, no issues whatsoever. The management card shows the event errors and that they are resolved, the power detail logs show no abnormalities. 

APC support just kept sending me in a loop and that it is an issue with the power coming in. Next time I go and replace the UPS, I will definitely be looking at evaluating other UPS manufacturers.

Reply

Link copied. Please paste this link to share this article on your social media post.

CaliDuck
Crewman CaliDuck
Crewman

Posted: ‎2024-08-26 04:07 PM

0 Likes
0
952
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-26 04:07 PM

We had an APC Support Tech tell us this was due to the latest firmware version having an issue and they provided us this link. They told us to wait for a newer firmware...wow! So hope/pray?
https://www.apc.com/us/en/faqs/FAQ000266396/

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of