SRT 2200 Switch OFF with delay by Modbus command problem
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2808:42 AM. Last Modified: 2024-03-1711:52 PM
SRT 2200 Switch OFF with delay by Modbus command problem
I have to switch OFF SRT 2200 Smart UPS by Modbus RS-232 command with delay ab out 90sec.
If I write (0x06 command) to Modbus register 1540 (SimpleSignalingCommand_BF) value 0x1 -
APC switch OFF after correct delay time (about 90sec), but then immediately switch ON because the input Inlet power is present.
If I write to register 1540 value 0x2 -
APC switch OFF immediately without useful 90sec delay and do not switch on again.
If I write to register 1538 (0x602 OutletCommand_BF ) value 0x84 or 0x04 -
I reseive an error Modbus reply , seems to "Slave device or server Failure".
The sending sequence of bytes in (HEX):
01 06 06 02 00 04 29 41
and reply sequence is:
01 86 04 43 A3
So how to Switch OFF SRT 2200 Smart UPS by Modbus RS-232 command with 90sec delay and without switching ON it next moment if input Inlet power is present?