SRT 2200 Switch OFF with delay by Modbus command problem
Send InviteCancel
Posted: 2021-06-2808:42 AM. Last Modified: 2024-03-1711:52 PM
I have to switch OFF SRT 2200 Smart UPS by Modbus RS-232 command with delay ab out 90sec.
If I write (0x06 command) to Modbus register 1540 (SimpleSignalingCommand_BF) value 0x1 -
APC switch OFF after correct delay time (about 90sec), but then immediately switch ON because the input Inlet power is present.
If I write to register 1540 value 0x2 -
APC switch OFF immediately without useful 90sec delay and do not switch on again.
If I write to register 1538 (0x602 OutletCommand_BF ) value 0x84 or 0x04 -
I reseive an error Modbus reply , seems to "Slave device or server Failure".
The sending sequence of bytes in (HEX):
01 06 06 02 00 04 29 41
and reply sequence is:
01 86 04 43 A3
So how to Switch OFF SRT 2200 Smart UPS by Modbus RS-232 command with 90sec delay and without switching ON it next moment if input Inlet power is present?