SRC2000XLI-CC (Harsh Environment) battery issue

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SRC2000XLI-CC (Harsh Environment) battery issue
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
avinandan012
avinandan012
Cadet

Posted: ‎2024-10-06 02:44 AM

0 Likes
4
802
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-06 02:44 AM

SRC2000XLI-CC (Harsh Environment) battery issue

I have a SRC2000XLI-CC (Harsh Environment) with AP9630. Purchased in 2015.

My old battery was EOL, so on 4-OCT-2024 I changed the internal battery with new batteries(same make and model).  Last battery replacement was AUG-2023( I had bad power last year, usually batteries last about 2+ years).

Now the battery indicator is blinking constantly. Now it's 40+ hours passed yet the battery does not reach 100% charge and runtime showing as 0 min. The old battery used to reach full charge around 4 hours or so after full discharge.

AP9630 shows battery voltage 108.5VDC

Measuring from multimeter battery voltage shows 105.1VDC.

My guess is battery is not charging somehow.
How to reset this model? Or what might be the issue?

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
Teken
Kirk Teken
Kirk

Posted: ‎2024-10-07 09:59 AM

0 Likes
2
779
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-07 09:59 AM

When the new battery was installed did you update the battery installation date? Did you manually initiate a Self Test?!? Was this followed up by completing a manual battery calibration?!?

Reply

Link copied. Please paste this link to share this article on your social media post.

avinandan012
avinandan012
Cadet

Posted: ‎2024-10-07 08:51 PM

0 Likes
0
749
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-07 08:51 PM

Q. When the new battery was installed did you update the battery installation date?
A. On 4-OCT-2024. Yes.

Q. Did you manually initiate a Self Test?!?
A. Yes. Seft test succeeds.

Q. Was this followed up by completing a manual battery calibration?!?
A. Unable to perform as the unit thinks batteries are not charged.

 

UPS_MNGCard.PNG

 

UPS_Issue3.PNG

 

UPS_Issue2.PNG

 

UPS_Issue1.PNG

 

Reply

Link copied. Please paste this link to share this article on your social media post.

avinandan012
avinandan012
Cadet

Posted: ‎2024-10-07 09:04 PM

In response to Teken
0 Likes
1
749
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-07 09:04 PM

I have ordered a 120Volt DC bench power supply to manually charge the batteries and 4 x 200 Watts incandescent bulbs for manual battery calibration should be delivered by next two days. Will update after I try manual calibration.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-10-08 07:30 AM . Last Modified: ‎2024-10-08 08:03 AM

In response to avinandan012
0 Likes
0
726
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-08 07:30 AM . Last Modified: ‎2024-10-08 08:03 AM

You may consider doing the following if recharging the individual cells do not resolve this issue.

 

Brain Dead: This procedure will reset the system and clear possible issues in the MCU. It will not resolve any possible hardware faults in the system though.

 

https://www.apc.com/us/en/faqs/FA156611/

 

NMC: Your system is running on older 6.X.X firmware. The latest 7.X.X firmware branch adds new features and resolves some bugs seen on the NMC.

 

Please only download the Smart-UPS firmware. NOT the (Sy) Symmetra or any other version.

 

https://www.apc.com/us/en/product/AP9631/ups-network-management-card-2-with-environmental-monitoring...

 

UPS Firmware: I don’t recommend updating the UPS system firmware but you should review the (Read Me) file for the latest release. As it indicates a few charging and voltage changes for your system.

 

You can not update the UPS firmware until all active faults / error codes are cleared! Given you have a battery problem this specific update can’t be taken anyways.

 

Regardless, I wanted to call this out as this specific update does address quite a few bugs and provides system improvements to the charging parameters.

 

https://www.apc.com/ca/en/faqs/FAQ000239180/

 

Let me know how everything turns out. 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore