Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
SNMP monitoring UPS attached to server
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2902:36 AM. Last Modified: 2024-03-1303:26 AM
SNMP monitoring UPS attached to server
I'm trying to monitor UPSes attached to servers using either ISX Central or a generic SNMP Network Management solution. The server is running PowerChute and the UPS is attached and recognized by PowerChute. The server MIB however shows OID unsupported for the PowerNet OIDs. Anyone attempted to do this?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2902:36 AM. Last Modified: 2024-03-1303:26 AM
SNMP isnt supported by powerchute software. APC products that you want to monitor via SNMP need to have a network interface - for UPSs, they must have an APC Network Management Card like AP9630 or AP9631. Other devices support it without that such as Netbotz or KVMs.
once you install the network management card in the UPS and assign a network address, you can then GET, SET, and WALK via SNMP to get data from the UPS as well as the NMC itself.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2902:36 AM. Last Modified: 2024-03-1303:26 AM
SNMP isnt supported by powerchute software. APC products that you want to monitor via SNMP need to have a network interface - for UPSs, they must have an APC Network Management Card like AP9630 or AP9631. Other devices support it without that such as Netbotz or KVMs.
once you install the network management card in the UPS and assign a network address, you can then GET, SET, and WALK via SNMP to get data from the UPS as well as the NMC itself.
hope that helps.