SNMP OIDs for Symmetra 16K

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SNMP OIDs for Symmetra 16K
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:32 AM . Last Modified: ‎2024-03-07 11:59 PM

0 Likes
4
2666
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:32 AM . Last Modified: ‎2024-03-07 11:59 PM

SNMP OIDs for Symmetra 16K

How can I use SNMP to determine when there is a power module failure with a Symmetra 16K?

The Diagnostics web page shows:

- UPS Status is On Line, Alarms Present, Power Module failure

- Power Modules: Modules 1-4 are "On & OK", Module 5 is "IIC Lost Comm"

Is there a SNMP OID that indicates these failures?

Many thanks!

Rich Brown
Hanover, NH

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • mib
  • oid
  • snmp
  • symmetra
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:32 AM . Last Modified: ‎2024-03-07 11:59 PM

0 Likes
0
2666
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:32 AM . Last Modified: ‎2024-03-07 11:59 PM

How can I use SNMP to determine when there is a power module failure with a Symmetra 16K?

The Diagnostics web page shows:

- UPS Status is On Line, Alarms Present, Power Module failure

- Power Modules: Modules 1-4 are "On & OK", Module 5 is "IIC Lost Comm"

Is there a SNMP OID that indicates these failures?

Many thanks!

Rich Brown
Hanover, NH

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:32 AM . Last Modified: ‎2024-03-07 11:59 PM

0 Likes
0
2668
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:32 AM . Last Modified: ‎2024-03-07 11:59 PM

Hi Kevin,

Thanks for the speedy response, and the link to the MIB. This version does contain the variable upsAdvStateAbnormalConditions (1.3.6.1.4.1.318.1.1.1.11.2.1.0) which is defined like this:

-----
upsAdvStateAbnormalConditions OBJECT-TYPE
SYNTAX DisplayString
ACCESS read-only
STATUS mandatory
DESCRIPTION
"An ASCII string containing the 32 flags representing the current active UPS faults. If the Network Card is unable to determine the values of the flags, thisvariable is set to 'UNKNOWN'. If this variable is notsupported by the connected UPS, this variable is set to 'NOT SUPPORTED'.
-----

which has flags for both the "Power Module Failure" and "IIC Inter-Module Communication Failure". I suspect this may do exactly what I want. Best regards,

Rich Brown
Hanover, NH

PS I searched the APC site pretty carefully, but was unable to come up with a link to the current MIB. Is there some place that I should have been looking? Thanks again.

Message was edited by: richb-hanover

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:32 AM . Last Modified: ‎2024-03-07 11:59 PM

0 Likes
0
2668
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:32 AM . Last Modified: ‎2024-03-07 11:59 PM

Hello,

This is the link for download most current mib in APC website:
http://www.apcc.com/tools/download/software_comp.cfm?sw_sku=SFPMIB389&id=55&family=&part_num=&swfam=...

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:32 AM . Last Modified: ‎2024-03-07 11:59 PM

0 Likes
0
2668
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:32 AM . Last Modified: ‎2024-03-07 11:59 PM

I had the same issue of not being alerted when a power module would go offline in my Symmetra RM 6000's. I finally called APC and they helped me setup a custom OID alert for power module status.

Using InfraStruXure 6.0.2
- Go to Device - SNMP Device Communication Settings - Supplemental OIDs
- Add a new Supplemental OID
- Sensor Type = Generic
- OID = .1.3.6.1.4.1.318.1.1.1.13.2.2.1.2.1 for Bay 1 Power Module (top left)
- OID = .1.3.6.1.4.1.318.1.1.1.13.2.2.1.2.2 for Bay 2 Power Module (second from the top left)
- OID = .1.3.6.1.4.1.318.1.1.1.13.2.2.1.2.3 for Bay 3 Power Module (third from the top left)
- OID = .1.3.6.1.4.1.318.1.1.1.13.2.2.1.2.4 for Bay 4 Power Module (bottom left)
- Now right click on any Symmertra UPS and select Create Thresholds - Other Numeric - Minimum Value - Select the newly created Sensors (Power Module Bay 1 - 4) and set the Minimum value to 4. This will alert you if a power module is not On/Ok. The OID will respond with a value of 2 if no power module is present and will respond with a value of 4 if a power module is On/Ok.

This has really helped me keep an eye on the power modules so I am alerted before I have an overload on the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:32 AM . Last Modified: ‎2024-03-07 11:59 PM

0 Likes
0
2667
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:32 AM . Last Modified: ‎2024-03-07 11:59 PM

How can I use SNMP to determine when there is a power module failure with a Symmetra 16K?

The Diagnostics web page shows:

- UPS Status is On Line, Alarms Present, Power Module failure

- Power Modules: Modules 1-4 are "On & OK", Module 5 is "IIC Lost Comm"

Is there a SNMP OID that indicates these failures?

Many thanks!

Rich Brown
Hanover, NH

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore