Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

SNMP, C-language Code

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SNMP, C-language Code
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:38 AM . Last Modified: ‎2024-03-06 01:30 AM

0 Likes
4
1384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:38 AM . Last Modified: ‎2024-03-06 01:30 AM

SNMP, C-language Code

I have a need to embed UPS control and monitoring inside a body of C-language code, a large test application. I have about a dozen SmartUPS units scattered around a large test site. There will be a GUI, one of many GUI panels dealing with the test, which displays UPS status and numeric values. (I have at least one other kind of device on the etwork that will require SNMP control and monitoring, an NTI IPDU, so I need to learn how to do this.)

Having never done anything before using SNMP, I'd like some advice on the least painful way to approach this. I have thought about including Net_SNMP libraries in the application, and developing control and monitor function calls in that manner. From this forum I ran across the Solarwind website, with the very nice MIB tree and MIB list for the APC products, so that aspect looks very straight-forward.

So advice, and if anyone has any code examples, I'd greatly appreciate it. I hate reinventing the wheel.

(20 years ago I thought C looked like a typewritter had barfed. Then I came across MIB files.)

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:38 AM . Last Modified: ‎2024-03-06 01:30 AM

0 Likes
0
1384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:38 AM . Last Modified: ‎2024-03-06 01:30 AM

Thank you voidstar. I walked the whole UPS branch and there are something like 250 returns. I'll find that one. The course current returns 0, while powereing my HP desktop and monitor. I figure the measurement must round down rather than up. Getting the current in 10ths will help a lot.

I started working with Net-SNMP and have pretty much run into a brick wall. Net-SNMP is incredibly complicated, I imagine because it is trying to be the SNMP swiss army knife -- all things to all OS's and all IDE's. Unfortunately, that means to tailor the many, MANY header files, to something simple like XP and C99, isn't even remotely straight-forward. And when I compile, there are things missing. Still slogging through it.

And still looking for other solutions and/or C example code.

I found SNMP Source, which looks fairly simple, but the code examples are C# and VB. Not very helpful.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-01 01:38 AM . Last Modified: ‎2024-03-06 01:30 AM

0 Likes
0
1384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:38 AM . Last Modified: ‎2024-03-06 01:30 AM

>
(20 years ago I thought C looked like a typewritter had barfed. Then I came across MIB files.)
>

:-)

>
Having never done anything before using SNMP, I'd like some advice on the least painful way to approach this.
>

I think it helps to be able to play around with an SNMP GUI to figure out what you want the code to do. Grab [GetIF here|http://www.wtcs.org/snmp4tpc/getif.htm] and the latest [PowerNet MIB here|http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SFPMIB405&tab=software] (scroll down or search the page). Then walk the device you intend to monitor and see what OIDs are supported.

All of my SNMP code is all in python. The net-snmp C API [looks fairly straightforward|http://www.net-snmp.org/wiki/index.php/TUT:Simple_Application].

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:38 AM . Last Modified: ‎2024-03-06 01:30 AM

0 Likes
0
1384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:38 AM . Last Modified: ‎2024-03-06 01:30 AM

I installed Getif as suggested. Very cool little app. I browsed the various commands for the SmartUPS1000 that I have connected to my network. Almost everytihng works and makes sense. I'm surprised that measurements are returned as integers only, such as output current, which returns a 0 or 1 only, when the actual current is like 1.4 Amps according to the UPS front panel.
.iso.org.dod.internet.private.enterprises.apc.products.hardware.ups.upsOutput.upsAdvOutput.upsAdvOutputCurrent

I'm still looking for someone out there who has some example code.

Over the next few days I'll investigate incorporating Net-SNMP and learning how to send queries from C function calls.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-01 01:38 AM . Last Modified: ‎2024-03-06 01:30 AM

0 Likes
0
1384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:38 AM . Last Modified: ‎2024-03-06 01:30 AM

>
I'm surprised that measurements are returned as integers only, such as output current, which returns a 0 or 1 only, when the actual current is like 1.4 Amps according to the UPS front panel.
.iso.org.dod.internet.private.enterprises.apc.products.hardware.ups.upsOutput.upsAdvOutput.upsAdvOutputCurrent
>

SNMP's number formats are all various forms of integers. So what we do is leave upsAdvOutputCurrent as-is for code that relies on it, and also include higher precision OIDs that report in tenths:

.iso.org.dod.internet.private.enterprises.apc.products.hardware.ups.upsOutput.upsHighPrecOutput.upsHighPrecOutputCurrent

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:38 AM . Last Modified: ‎2024-03-06 01:30 AM

0 Likes
0
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:38 AM . Last Modified: ‎2024-03-06 01:30 AM

Thank you voidstar. I walked the whole UPS branch and there are something like 250 returns. I'll find that one. The course current returns 0, while powereing my HP desktop and monitor. I figure the measurement must round down rather than up. Getting the current in 10ths will help a lot.

I started working with Net-SNMP and have pretty much run into a brick wall. Net-SNMP is incredibly complicated, I imagine because it is trying to be the SNMP swiss army knife -- all things to all OS's and all IDE's. Unfortunately, that means to tailor the many, MANY header files, to something simple like XP and C99, isn't even remotely straight-forward. And when I compile, there are things missing. Still slogging through it.

And still looking for other solutions and/or C example code.

I found SNMP Source, which looks fairly simple, but the code examples are C# and VB. Not very helpful.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of