SMX2000RMLV2U, new batteries, low runtime, what gives?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMX2000RMLV2U, new batteries, low runtime, what gives?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:29 AM . Last Modified: ‎2024-03-17 11:16 PM

0 Likes
5
740
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:29 AM . Last Modified: ‎2024-03-17 11:16 PM

SMX2000RMLV2U, new batteries, low runtime, what gives?

I recently installed 10 new 12V 5AH batteries in my UPS (SMX2000RMLV2U), at first it appears to work great. However when I let the UPS to do a runtime calibration, the estimate dropped to ~20min @~400W, which is about 1/3 of the spec. I then did a manual calibration (a heat gun drawing ~780W), it lasted 8min46s before battery run dry. I also measured the open end voltage of the battery pack with my multimeter, it was ~136V and ~126V before and after discharge. Though to my surprise the UPS reported ~43% charge after I plug back in the drained battery pack.

Searching on the Internet, some suggested to use a APC calibration key or APCfix.exe to resolve runtime issue. But my understanding is that they would let UPS get a better estimate, but actual runtime is not affected. Given that the runtime in my test is not far off, I suspect the problem lies somewhere else, no?

I would like to know your thoughts. Thank you

PS: I should mention that I got the UPS used so it's probably out of warranty

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:30 AM . Last Modified: ‎2024-03-17 11:15 PM

0 Likes
0
740
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:30 AM . Last Modified: ‎2024-03-17 11:15 PM

I got some 100Ohm resistors today and tested the internal resistance of the batteries. It appears that each battery have a internal resistance of ~0.7Ohms when fully charged. A good battery should be only ~1/30 of that

It's most likely bad batteries, I am working on return/replace them

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 09:29 AM . Last Modified: ‎2024-03-17 11:16 PM

0 Likes
0
740
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:29 AM . Last Modified: ‎2024-03-17 11:16 PM

Yi-xiao,

The APC calibration key is only for older UPSes. Newer UPSes do not need it; the manual calibration you performed should be all that is necessary.

You are correct that this won't affect the actual runtime of the UPS. The UPS runs until the battery is drained or it is commanded to turn off. After discharge you measured 12.6V/battery which seems a bit high for a fully discharged battery so I'd be suspicious of a bad battery cell. If you bought the batteries from APC, then I'd recommend calling tech support and asking about the runtime.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:30 AM . Last Modified: ‎2024-03-17 11:16 PM

0 Likes
0
740
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:30 AM . Last Modified: ‎2024-03-17 11:16 PM

On 1/3/2019 1:41 PM, voidstar said:

Yi-xiao,

The APC calibration key is only for older UPSes. Newer UPSes do not need it; the manual calibration you performed should be all that is necessary.

You are correct that this won't affect the actual runtime of the UPS. The UPS runs until the battery is drained or it is commanded to turn off. After discharge you measured 12.6V/battery which seems a bit high for a fully discharged battery so I'd be suspicious of a bad battery cell. If you bought the batteries from APC, then I'd recommend calling tech support and asking about the runtime.

Thank you voidstar

You are right 12.6V for a discharged battery seems to be a bit high. OTOH the the battery pack was 110V (reported by the UPS) shortly before the load was dropped. I heard that drained lead acid battery may back-shoot the voltage once the load is dropped, but not sure if it's normal for it to be as high as 1.6V/battery. 

I am in touch with the battery vendor, but am also wondering if there is any other troubleshoot I can do to isolate the problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 09:30 AM . Last Modified: ‎2024-03-17 11:15 PM

0 Likes
0
740
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:30 AM . Last Modified: ‎2024-03-17 11:15 PM

Make sure voltage reported by the UPS is similar to voltage reported by your voltmeter. You might try testing individual batteries rather than all 10 *edit: only makes sense for testing battery cartridges rather than individual batteries within the cartridge*. You could test batteries in a UPS system you trust for comparative purposes. You might also try looking for a manufacturing date code on the battery -- SLA batteries last roughly six months without being charged.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:30 AM . Last Modified: ‎2024-03-17 11:15 PM

0 Likes
0
740
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:30 AM . Last Modified: ‎2024-03-17 11:15 PM

The UPS reading on battery pack voltage, both before and after runtime calibration, seems to agree with my multimeter reading. I was not able to use my multimeter when the UPS was on battery though. And another UPS take the same RBC was not available.

Assuming the 110V and 126V reading before and after UPS drops the load are both accurate, that sounds like a internal resistance of 1-2 ohms right (to my limited electrical training). I believe good SLA batteries (even 10 in series) should only be a fraction of it?

Thanks for all your suggestions, I will find some time this weekend to open the cartridge.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:30 AM . Last Modified: ‎2024-03-17 11:15 PM

0 Likes
0
741
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:30 AM . Last Modified: ‎2024-03-17 11:15 PM

I got some 100Ohm resistors today and tested the internal resistance of the batteries. It appears that each battery have a internal resistance of ~0.7Ohms when fully charged. A good battery should be only ~1/30 of that

It's most likely bad batteries, I am working on return/replace them

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of