I have aSMX1500RM2UCNC and it has started to beep continuously with Alarm State: Connect Battery.
Existing battery still seems good, outputs 50V when tested with a multimeter. Still, we tried replacing the battery - same result. Factory reset, same result.
When plugged in to utility power, the UPS does not run without a battery, instead it powers on and off repeatedly every few seconds.
When the unit powers on after plugging battery in and with utility power plugged in, it stays up and running but immediately goes into Alarm State: Connect Battery.
We are not able to run tests or diagnostics using the panel.
The web UI shows, "The battery is not installed properly." We are quite certain that it is properly installed and fully seated.
Model: SMX1500RM2UCNC
Firmware: UPS 02.0 (ID1031)
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-08 07:52 AM
Was I not trying to help you in that previous thread?!? 🤔
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-08 01:31 PM
Yes, I think so, but that thread got locked somehow after I edited the subject line and I can't reply to it or even view the responses anymore. Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-10 12:03 PM
After resolving the power issue install the batteries let it charge to 100% and run a self test to see if the batteries are still good the batteries still shows 48 volts which is a good sign when fully charge typically this batteries can reach a voltage fo around 54 volts
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-02 12:48 PM
I finally got time to shut down our relay rack and do some further troubleshooting.
I have checked the sensitivity. It's set to normal, and I believe it always has been.
I have tried using a different outlet.
The UPS does not run on utility only. It powers on, then off repeatedly every 5 seconds or so.
When the UPS is running on battery only, it detects the battery, displays the load, battery capacity and estimated runtime. During my last test of this, the battery capacity actually increased from 36% to 37% to 38% while on battery only with no load.
I am unable to complete a proper calibration, logic reset or brain dead, because when the unit is plugged in, it does not detect a battery.
The UPS does not detect a battery when plugged in. Near as I can tell, it's borked.
Thanks,
-Dave
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-02 10:46 PM
Hi Dave,
Have you defaulted the unit to a factory state via LCD Menu?!? If not please do so and report back the results.
Given your hardware is out of warranty I’m hesitant to suggest the following. Which is to update the UPS firmware to the latest 15.5 release as you’re still running the initial 2.0 firmware.
You may review the release notes here:
APC Firmware upgrade FAQ:
https://www.apc.com/us/en/faqs/FA164737/
https://www.apc.com/us/en/faqs/FA279197/
NOTE: The UPS firmware process should be conducted live over the phone with APC Technical Support. All requirements must be in place and met prior to any upgrade.
All active faults / errors must be cleared before proceeding. As such the current battery disconnected message may cause the system to abort this process.
Questions Ask . . . 👍
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-04 08:31 AM
Try reducing the sensitivity to Low the Normal setting is the highest Sensitivity setting for this Unit. If the issue persist you may have a faulty sensor (too sensitive) or possibly a relay weld where the UPS continuously goes in to battery thus draining battery and it can not go to its normal or online mode.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of