SMX1500RM2UCNC Alarm state: Replace Battery

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMX1500RM2UCNC Alarm state: Replace Battery
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
daaave
Crewman daaave
Crewman

Posted: ‎2024-11-07 11:16 AM

0 Likes
6
382
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-07 11:16 AM

SMX1500RM2UCNC Alarm state: Replace Battery

Re-posting this question, because in the previous thread, someone pointed out that I had posted the wrong model number in the subject, so I edited the subject and somehow that seems to have locked the thread, as I can no longer reply or see the other replies.  To confirm the model number, etc., here is the full info:
 
Model: SMART-UPS X1500
SKU: SMX1500RM2UCNC
Serial Number: AS2152160954
Firmware Revision: UPS 02.0 (ID1031)
Manufacture Date: 12/28/2021
Apparent Power Rating: 1440 VA
Real Power Rating: 1350 W
Internal Battery SKU: APCRBC115
External Battery SKU: SMX48RMBP2U
 
=======
 
Hello,

 

I have aSMX1500RM2UCNC and it has started to beep continuously with Alarm State: Connect Battery.

 

Existing battery still seems good, outputs 50V when tested with a multimeter.  Still, we tried replacing the battery - same result.  Factory reset, same result.

 

When plugged in to utility power, the UPS does not run without a battery, instead it powers on and off repeatedly every few seconds.

 

When the unit powers on after plugging battery in and with utility power plugged in, it stays up and running but immediately goes into Alarm State: Connect Battery.

 

We are not able to run tests or diagnostics using the panel.

 

The web UI shows, "The battery is not installed properly."  We are quite certain that it is properly installed and fully seated.

 

Model: SMX1500RM2UCNC

Firmware: UPS 02.0 (ID1031)

 

Thanks!

 
=======
 
Since posting the above, I had also performed the "brain dead" logic reset, or whatever it's called, I can't access the old thread anymore.  This made no difference to the behaviour of the unit.
 
=======
 
Additionally, we had a scheduled power outage last weekend, and to my surprise, the unit perofmed all of it's correct functions: emailed status change reports, switched the load to battery, sent low battery notifications, and supported load until it was out of battery.  So it seems to work fine except for two things:
1. It constantly beeps.
2. It constantly reports: UPS: The battery is not installed properly.
 
Attaching most recent event.txt and data.txt logs .
 
Thanks!
Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
Teken
Janeway Teken
Janeway

Posted: ‎2024-11-08 07:52 AM

0 Likes
1
361
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-08 07:52 AM

Was I not trying to help you in that previous thread?!? 🤔

Reply

Link copied. Please paste this link to share this article on your social media post.

daaave
Crewman daaave
Crewman

Posted: ‎2024-11-08 01:31 PM

In response to Teken
0 Likes
0
298
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-08 01:31 PM

Yes, I think so, but that thread got locked somehow after I edited the subject line and I can't reply to it or even view the responses anymore.  Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

RyanG32
Ensign RyanG32 Ensign
Ensign

Posted: ‎2024-11-10 12:03 PM

0 Likes
3
314
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-10 12:03 PM

Based on the errors that you have you may have distorted power that is causing the UPS to go into battery 
 
This UPS should be able to un without batteries if the power is okay
 
You may want to consider reducing the sensitivity of the UPS so that it does not react as fast and allows for a bit of distortion if your load can handle it I suggest you do this
the UPS typically is set to high sensitivity by default 
 
If the issue persists try to plug the unit to a different outlet preferably to a different circuit or isolate if the issue by connecting another UPS and to the same outlet and see if it behaves the same. I could also be caused by a loose connection.
I suggest that you try to make sure that the UPS can run on utilility only so that you do not discharge the battery any further. since on your data logs it is now only 29 % charged depending on your load and low battery threshold the UPS will turn off its outlet
 
11/02/2024 09:11:10 Device UPS: A low battery condition no longer exists. 0x0110
11/02/2024 09:11:10 Device UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately. 0x0107
11/02/2024 09:11:09 Device UPS: The output power is turned off. 0x0114
11/02/2024 09:11:09 Device UPS: The graceful shutdown period has ended. 0x014F
11/02/2024 09:11:09 Device UPS: No longer on battery power. 0x010A
11/02/2024 09:11:09 Device UPS: Switched outlet group 3, Outlet Group 3, has been commanded to shutdown with on delay. 0x0174
11/02/2024 09:11:09 Device UPS: The power for switched outlet group 3, Outlet Group 3, is now turned off. 0x0135
11/02/2024 09:11:09 Device UPS: Switched outlet group 2, Outlet Group 2, has been commanded to shutdown with on delay. 0x0174
11/02/2024 09:11:09 Device UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off. 0x0135
11/02/2024 09:11:09 Device UPS: Switched outlet group 1, Outlet Group 1, has been commanded to shutdown with on delay. 0x0174
11/02/2024 09:11:09 Device UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off. 0x0135
11/02/2024 09:05:21 Device UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon. 0x010F
11/02/2024 08:51:19 Device UPS: On battery power in response to distorted input. 0x0109
11/02/2024 08:51:18 Device UPS: The battery is now installed. 0x0130
 
RyanG32_0-1731268837513.png

 

After resolving the power issue install the batteries let it charge to 100% and run a self test to see if the batteries are still good the batteries still shows 48 volts which is a good sign when fully charge typically this batteries can reach a voltage fo around 54 volts
Reply

Link copied. Please paste this link to share this article on your social media post.

daaave
Crewman daaave
Crewman

Posted: ‎2025-03-02 12:48 PM

In response to RyanG32
0 Likes
2
149
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-02 12:48 PM

I finally got time to shut down our relay rack and do some further troubleshooting.

 

I have checked the sensitivity.  It's set to normal, and I believe it always has been.

 

I have tried using a different outlet.

 

The UPS does not run on utility only.  It powers on, then off repeatedly every 5 seconds or so.

 

When the UPS is running on battery only, it detects the battery, displays the load, battery capacity and estimated runtime.  During my last test of this, the battery capacity actually increased from 36% to 37% to 38% while on battery only with no load.

 

I am unable to complete a proper calibration, logic reset or brain dead, because when the unit is plugged in, it does not detect a battery.

 

The UPS does not detect a battery when plugged in.  Near as I can tell, it's borked.

 

Thanks,

 

-Dave

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Janeway Teken
Janeway

Posted: ‎2025-03-02 10:46 PM

In response to daaave
0 Likes
0
145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-02 10:46 PM

Hi Dave,

 

Have you defaulted the unit to a factory state via LCD Menu?!? If not please do so and report back the results.

 

Given your hardware is out of warranty I’m hesitant to suggest the following. Which is to update the UPS firmware to the latest 15.5 release as you’re still running the initial 2.0 firmware.

 

You may review the release notes here:

 

https://download.schneider-electric.com/files?p_Doc_Ref=Smart-UPS_FW_Release_Notes&p_File_Name=SMTSM...

 

APC Firmware upgrade FAQ:

 

https://www.apc.com/us/en/faqs/FA164737/

 

https://www.apc.com/us/en/faqs/FA279197/

NOTE: The UPS firmware process should be conducted live over the phone with APC Technical Support. All requirements must be in place and met prior to any upgrade.

 

All active faults / errors must be cleared before proceeding. As such the current battery disconnected message may cause the system to abort this process.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

forum_forum
forum_forum
Cadet

Posted: ‎2025-03-04 08:31 AM

In response to daaave
0 Likes
0
116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-04 08:31 AM

Try reducing the sensitivity to Low the Normal setting is the highest Sensitivity setting for this Unit. If the issue persist you may have a faulty sensor (too sensitive) or possibly a relay weld where the UPS continuously goes in to battery thus draining battery and it can not go to its normal or online mode.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login