SMX1500RM2U will not complete firmware update over USB (v09.1 to v15.0)

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMX1500RM2U will not complete firmware update over USB (v09.1 to v15.0)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
user97
user97
Cadet

Posted: ‎2023-10-26 10:12 AM

0 Likes
2
997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-10-26 10:12 AM

SMX1500RM2U will not complete firmware update over USB (v09.1 to v15.0)

Problem:

- Firmware v15.0 update via USB initiates but fails to complete. UPS remains at v09.1; functions normally after power cycling.

 

Setup:

- Windows 10 LTSC (1809 17763) with USB 2.0 and USB 3.0 ports (I tried both)

- "APC Firmware Upgrade Wizard v4.3.6" via USB connection

- Firmware file "SMTSMX20UPS_15-0.enc" (only file the software will allow me to choose)

- SMX1500RM2U (built in 2015); no Network Management Card, local access only; current firmware:

     UPS: v09.1 (ID:20-5)
     MCU: v09.1
     UBL: v06.9
     MBL: v06.0

- “APC PowerChute Serial Shutdown v1.0” software communicates with unit via USB without a problem

 

Steps to reproduce:

1. UPS plugged in with battery installed, connected via USB to PC; start with UPS ON or OFF (same result)

2. Run “APC Firmware Upgrade Wizard v4.3.6,” software detects UPS and authorizes a firmware update. Requires that I select firmware file, only allows me to choose “ SMTSMX20UPS_15-0.enc” file.

3. I initial firmware update process, if unit is ON, it now automatically powers OFF. Moments later UPS screen wakes with message:

     “Firmware Update in Progress...”

      [Front panel LEDs: Green (OFF), Orange (ON steady), Red (ON flashing), Red (ON Steady)]

4. At same moment, PC software shows:

      “Initiating the transfer”

5. About 1 minute later: at the UPS a click is heard and the screen powers OFF.

6. 15 seconds later: PC software status changes to:

     “Sending device firmware file 1 of 1...0%”

7. About 4 minutes later: with no change in condition/status at UPS or software a new message appears on the PC:

     “Re-sending device firmware part 1 of file 1...0%”

8. The software repeats a “re-send” attempt about every 4 minutes then finally presents an “update failed” message. When I power ON the UPS, it functions normally but firmware is still v09.1.

 

Anyone have an idea why this is failing? Is there an alternate path to update firmware without an NMC? This is a new-to-me unit and I have no idea if previous firmware updates were successfully applied over USB. I don't have a dongle for the RJ45 port.

 

-Thanks for reading!

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
LarryK
Lt. Commander LarryK
Lt. Commander

Posted: ‎2023-11-15 12:31 PM

0 Likes
1
948
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-11-15 12:31 PM

According to https://www.apc.com/us/en/faqs/FA279197/

 

IMPORTANT: IT IS NOT RECOMMENDED TO USE LOCAL CONNECTION VIA USB CABLE WITH THE CURRENT VERSION OF THE FIRMWARE UPGRADE WIZARD. It is recommended to use local connection via Serial cable. The serial cable supplied with the UPS must be used. USB support will be re-added to a future version of the Firmware Upgrade Wizard.

 

So using the USB connection is - apparently - not the way to do this.  As I type this I am waiting for APC Support to call back and confirm that the 940-0625A serial cable can be used with a USB adapter to update all of my clients' 1015 and 1027 UPS devices.

Reply

Link copied. Please paste this link to share this article on your social media post.

user97
user97
Cadet

Posted: ‎2023-11-23 02:11 PM

In response to LarryK
0 Likes
0
922
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-11-23 02:11 PM

Thanks for the reply. Somehow I missed this note. This is probably the solution to my problem. I wonder where I put my APC serial cable...

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore