Smart-UPS 1500 and MC3 (AP9641) - "UPS: The battery is not installed properly."
  • Smart-UPS 1500 and MC3 (AP9641) - "UPS: The battery is not installed properly."
JCG-Rcarre
Crewman JCG-Rcarre
Crewman
Posted: ‎2023-10-30 09:05 AM
1112
3 days after reseting and setting up NMC3 , web UI displayed a Critical Alarm Present "The battery is not installed properly"
NMC is updated to latest firmware.
Does the battery need to be replaced ?
Could il be a failed NMC3 ?
Thanks for helping.
dpierce4776
Lt. Commander dpierce4776
Lt. Commander
Posted: ‎2023-11-01 07:45 AM
1083
Typically this means that you have a battery going bad. You will need to replace all the batteries in the unit as when one goes bad it drags the others down, and more than likley they were all installed at the same time as well. Meaning that they will all go bad shortly.
APC does not really do a a good job at reporting batter issues. Typically the one you describe, bad battery, or repeated battery disconnected alerts all mean a battery is failing. It is not a card issue.
JCG-Rcarre
Crewman JCG-Rcarre
Crewman
Posted: ‎2023-11-27 05:46 AM
In response to dpierce4776
I ordered a new battery and replace the failed one. => problem solved
battery were supposed to live 4 years, not 2 years.
Thanks for helping.
dpierce4776
Lt. Commander
1084
JCG-Rcarre
Crewman JCG-Rcarre
Crewman
Thanks for helping.