SMX1500 Battery Box

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMX1500 Battery Box
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
mburns
Crewman mburns
Crewman

Posted: ‎2025-04-24 09:57 AM

0 Likes
3
509
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-24 09:57 AM

SMX1500 Battery Box

The older model of APC products had large battery boxes you could hook up to the rackmount gear.  I remember some had adapter cables, so you could use the older big battery boxes with the newer gear.  Does anything like this exist with the SMX1500 XL models? I want to use the plug in the back to hookup the older larger battery boxes? Does anyone know of anyone who has done this? Or is there a product I am not seeing?

 

I am tempted to just order a cord, cut the one end off, and put two O-rings on it for battery terminals, and just do it manually.   I see the newer cords have two female, and two male pins in between the two pins for the power. It appears to hookup to a little circuit board that detects if power is supplied by the looks of it.  I am afraid if I do something like this, it won't work anyway, due to the circuit board not being hooked up.  Can anyone confirm this? My luck, I will cut the end off a $100 cable, and it wont work.  

 

Thanks

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Teken
Kirk Teken
Kirk

Posted: ‎2025-04-25 05:44 AM

0 Likes
2
487
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-25 05:44 AM

This is the official extended battery pack for the SMX Series UPS:

 

https://www.apc.com/us/en/product/SMX48RMBP2U/apc-smartups-xseries-external-battery-pack-rack-tower-...

 

The system incorporates a simple resistor network to determine if a battery pack is present and the quantity. 

In older SMX UPS firmware the number of extended battery packs were manually entered into the system as whole packs ( NOT) as individual battery cartridges.

 

If you search this forum you’ll see a really old thread about building one. 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

mburns
Crewman mburns
Crewman

Posted: ‎2025-11-19 08:03 AM

In response to Teken
0 Likes
1
142
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-19 08:03 AM

Can you post the link to thread? I tried the search, and that's why I posted! If youre not going to be helpful, just don't reply.   Like I got days on end to spend browsing page after page of useless results.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2025-11-20 04:30 AM

In response to mburns
0 Likes
0
139
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-20 04:30 AM

I provided you with at least three pieces of important information that you didn’t know more than 7 months ago! 🤦‍♂️

 

Yet you accuse me of not being helpful?!? 🤢

 

So after seven months later you come back to insult me?!? Based on your reply I surely won’t go out of my way help spoon feed you the information because I’m not inclined to do so! 🫵

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore