Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey
SMTL1500RM3UC storage when not in use
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2024-04-0310:26 AM. Last Modified: ‎2024-04-0310:30 AM
Yes, the battery cartridge should be removed if this unit will be held in long term storage. The reason for doing so is to prevent the scenario where the battery cartridge swells and becomes stuck inside of the housing. 🤦‍♂️
Once a month the cartridge should be reinstalled and the (UPS) unit turned on to recharge the cells for 24-72 hours. Failure to maintain the battery cartridge will result in damaged cells and extra long term business costs.
Take a sticky note and document each time the battery cartridge has been recharged. 👍
NOTE: Insure the unit is securely and safely stored in a conditioned space. Respect the storage temperatures called out by APC as it relates Lithium / LiFePO4 cells.