SMT750i very limited connectivity to Synology Diskstation.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMT750i very limited connectivity to Synology Diskstation.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 02:09 AM . Last Modified: ‎2024-03-05 11:52 PM

0 Likes
4
1768
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:09 AM . Last Modified: ‎2024-03-05 11:52 PM

SMT750i very limited connectivity to Synology Diskstation.

It seems that the SMT750i cannot communicate more than very basic information in conjuction with a Synology Diskstation.
We need to be able to remote monitor UPS parameters so this is a very unfortunate situation for us.

Installing Powerchute on the main Debian server may be a possible fallback but it still needs to signal the Diskstation and
other servers to shutdown. I'd rather keep the DiskStation the controller for this.

Is there a schedule when this issue will be resolved?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:09 AM . Last Modified: ‎2024-03-05 11:52 PM

0 Likes
0
1769
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:09 AM . Last Modified: ‎2024-03-05 11:52 PM

i believe this is a result of the UPS being micro-link based. if I understand you correctly, you are looking for more data points beyond what you listed in your post above? but the SAN can still do a shutdown based on whats provided by NUT in your current set up?

Please don't shoot the messenger - we don't officially support NUT (or the apcupsd alternative). However if all that is required is shutdown, and if the host can connect to the UPS via USB, NUT should work for that function. For the additional information you want from the UPS, I believe you'd need an AP9620 Legacy Communications Card because I believe you are looking for items that are either APC proprietary USB usages or just additional information we used to provide on older UPS models or via our own software but do not anymore via this type of UPS and NUT.

there is some information on AP9620 here -> http://www.apc.com/site/support/index.cfm/faq/ -> search for FA156172

please let me know if I have misunderstood. i also can understand you may not want to have to buy the added accessory either..

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-07-01 02:09 AM . Last Modified: ‎2024-03-05 11:52 PM

0 Likes
0
1768
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:09 AM . Last Modified: ‎2024-03-05 11:52 PM

I've since received an AP9620 LCC which makes this work as expected:

DiskStation> upsc ups

battery.charge: 100

battery.charge.low: 10

battery.charge.warning: 50

battery.mfr.date: 2012/09/28

battery.runtime: 2640

battery.runtime.low: 120

battery.temperature: 26.9

battery.type: PbAc

battery.voltage: 27.3

battery.voltage.nominal: 24.0

device.mfr: American Power Conversion

device.model: Smart-UPS 750

device.serial: AS??????????

device.type: ups

driver.name: usbhid-ups

driver.parameter.pollfreq: 30

driver.parameter.pollinterval: 5

driver.parameter.port: auto

driver.parameter.productid: 0002

driver.version: SDS4-1-2012Q3branch-2664-121205

driver.version.data: APC HID 0.95

driver.version.internal: 0.37

input.sensitivity: high

input.transfer.high: 253

input.transfer.low: 208

input.voltage: 233.1

output.current: 0.75

output.frequency: 50.0

output.voltage: 233.1

output.voltage.nominal: 230.0

ups.beeper.status: enabled

ups.delay.shutdown: 20

ups.delay.start: 30

ups.firmware: UPS 08.3 USB_FW:LCC 02.2

ups.load: 23.3

ups.mfr: American Power Conversion

ups.mfr.date: 2012/09/28

ups.model: Smart-UPS 750

ups.productid: 0002

ups.serial: AS??????????

ups.status: OL

ups.test.result: No test initiated

ups.timer.reboot: -1

ups.timer.shutdown: -1

ups.timer.start: -1

ups.vendorid: 051d

DiskStation>


I think it should have been supported out of the box but I'm positively surprised with the AP9620, especially the fact that it is hot pluggable.

I also note that even though the AP9620 protocol does not support all features, the UPS itself seems to function identically with and without the AP9620 plugged in, including green features.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:09 AM . Last Modified: ‎2024-03-05 11:52 PM

0 Likes
0
1769
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:09 AM . Last Modified: ‎2024-03-05 11:52 PM

• can you elaborate on how the UPS is connected to the Synology device currently where you see this "limited" information?
• can you let us know if the Synology device offers different connectivity methods? for example, some NAS and SAN devices support USB and SNMP connectivity versus just one over the other.
• how do we know this is a problem with the UPS versus what the Synology device supports? do you have other UPSs that provide more information? if so, please let us know which makes/models.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 02:09 AM . Last Modified: ‎2024-03-05 11:52 PM

0 Likes
0
1768
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:09 AM . Last Modified: ‎2024-03-05 11:52 PM

DiskStation> upsc ups
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 50
battery.runtime: 2760
battery.runtime.low: 120
battery.type: PbAc
battery.voltage: 27.3
battery.voltage.nominal: 24.0
device.mfr: American Power Conversion
device.model: Smart-UPS 750
device.serial: AS??????????
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 5
driver.parameter.port: auto
driver.parameter.productid: 0003
driver.version: SDS4-1-2012Q3branch-2664-121205
driver.version.data: APC HID 0.95
driver.version.internal: 0.37
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.firmware: UPS 08.3 / ID=18
ups.mfr: American Power Conversion
ups.mfr.date: 2012/09/29
ups.model: Smart-UPS 750
ups.productid: 0003
ups.serial: AS??????????
ups.status: OL
ups.timer.reboot: -1
ups.timer.shutdown: -1
ups.vendorid: 051d
DiskStation>


I don't think the shutdown features of the NAS supports SNMP, but if it was SNMP in addition to USB I could probable let the NAS log the data.
I would like to log line voltages and power usage among others which is why I chose a Smart UPS in the first place.

The Synology NAS uses standard NUT ([http://networkupstools.org/]) which are common Linux tools for handling UPSes.
I think the problem is that you haven't worked with the community to get support for the SMT line implemented.

This hurts me as a customer.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:09 AM . Last Modified: ‎2024-03-05 11:52 PM

0 Likes
0
1770
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:09 AM . Last Modified: ‎2024-03-05 11:52 PM

i believe this is a result of the UPS being micro-link based. if I understand you correctly, you are looking for more data points beyond what you listed in your post above? but the SAN can still do a shutdown based on whats provided by NUT in your current set up?

Please don't shoot the messenger - we don't officially support NUT (or the apcupsd alternative). However if all that is required is shutdown, and if the host can connect to the UPS via USB, NUT should work for that function. For the additional information you want from the UPS, I believe you'd need an AP9620 Legacy Communications Card because I believe you are looking for items that are either APC proprietary USB usages or just additional information we used to provide on older UPS models or via our own software but do not anymore via this type of UPS and NUT.

there is some information on AP9620 here -> http://www.apc.com/site/support/index.cfm/faq/ -> search for FA156172

please let me know if I have misunderstood. i also can understand you may not want to have to buy the added accessory either..

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore