SMT3000RMI2U frequently displays 'Faulty Battery'

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMT3000RMI2U frequently displays 'Faulty Battery'
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:15 AM

0 Likes
11
1325
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:15 AM

SMT3000RMI2U frequently displays 'Faulty Battery'

Hi, bit long winded this one but please bear with me.

We have a SMT3000RMI2U which frequently displays 'Faulty Battery' alerts.

The first time this happened I ran a self test from the Network Management interface, however the fault persisted.

After ringing APC support, they asked if I had run one from the front panel, to which I replied no, as I am not based on the same site as the UPS, support said that they would send me a replacement battery but would need my old battery back to test and if there was no fault, I may be charged for the replacement battery.


In the time between my phone call with support and the new battery turning up, I ran a self test from the front panel, and the error went away.

Spoke to support again, and they asked me to send the replacement battery back to them, which I did.


Since then, approximately once a fortnight, our UPS displays a faulty battery error along with an email every 2 minutes telling me that there is a fault until we run a front panel self test.

This morning however, the front panel self test failed, twice, and only a self-test initiated from the network management interface cleared the error.


Can anybody shed any light as to why our UPS frequently gets this problem?


Thanks in advance


Chris



Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:14 AM

0 Likes
0
1323
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:14 AM

Alrighty.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:15 AM

0 Likes
0
1323
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:15 AM

Could you post all the logs from the management card so we could review please? This includes data.txt, config.ini, and event.txt.

Instructions are here in the knowledge base (http://www.apc.com/site/support/index.cfm/faq/) and refer to article ID FA156131.

Also, in the UPS->About section of your management card, can you tell me your UPS firmware version too? Something like UPS 01.3 or in that format.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:15 AM

0 Likes
0
1323
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:15 AM

Hi Angela, thanks for the reply.

The firmware version is marked as: UPS 06.5 / MCU 11.0 / UBL 08.2 / MBL 11.0 (ID18)

Log files attached

Cheers

Chris

Attachments
config.ini.zip
event.txt.zip
data.txt.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:15 AM

0 Likes
0
1323
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:15 AM

I am seeing a few strange things in there - like the fact that two self tests are being done some types "via internal operation" within a few ours of each other. Not to mention the faulty battery issue.

Also, ID18's latest update is UPS 08.3 according to what I have. If it were me, I'd say we should update this UPS (as well as the management card if you'd like to).

As far as updating the UPS, it will require the power output to turn off on the UPS no matter how you do it which I imagine you might need to arrange for.

You have two options in order to complete the upgrade on the UPS itself.

1.) Via serial (or USB if supported - not sure off the top of my head on this model) as noted in article ID FA164737 in the knowledge base

2.) Via the network management card (so make sure the network management card's network connection isn't connected to a piece of networking equipment that turns off during the upgrade) as noted in the article FA170679. I can give you the image file you need for this method.

Let me know what you think as far as what I propose or if you have any questions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:15 AM

0 Likes
0
1323
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:15 AM

Hi Angela,

Thanks for the suggestion.

I agree that upgrading the firmware is probably a good idea, and you are quite right that it is something that I will need to arrange out of hours.

Our NMC2 is currently version 5.1.6 so I think upgrading it to the latest available version is also good idea.

I have read on one of the Knowledge Base articles that upgrading the NMC2 firmware does not affect the UPS and therefore I can do it while the UPS and all connected devices are online with no ill-effects. Can you confirm this?

Thanks

Chris

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:15 AM

0 Likes
0
1323
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:15 AM

Hi Chris,

Yes, updating NMC firmware does not affect the UPS - it will only reboot itself.

6.0.6 is the latest version and it is a major change from what you have now - I wrote up article ID FA167693 in the knowledge base to go over some of the key points on upgrading (and downgrading if you hate it).

I thought we had some cards online at testdrive.apc.com with it but i cannot get to them. maybe you can.

also, i don't think the NMC firmware has anything to do with the issue are seeing but i did see it was a few revisions older so I just mentioned it, if interested.

I blame the UPS solely for the battery faults smile

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:15 AM

0 Likes
0
1323
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:15 AM

I also blame the UPS, but it can't hurt for the NMC2 card to be on the latest.

I will update the NMC2 this morning and I have already uploaded the firmware image to the UPS ready for when I can negotiate some down time!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:15 AM

0 Likes
0
1323
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:15 AM

NMC2 updated.

Wouldn't update at first when running the update from the server (SBS 2011), got an error - Unable to verify current firmware version - however, when running it from my workstation, even accross the VPN it upgraded successfully.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:15 AM

0 Likes
0
1323
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:15 AM

Hi Angela,

I updated the firmware on the UPS last Saturday (22 June) and all seemed fine until this Saturday (29 June) when the UPS started to report a faulty battery again. frown

Logs attached.

Attachments
apc.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:15 AM

0 Likes
0
1323
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:15 AM

So under About->UPS, you show the updated UPS versions (UPS 08.3? If anything, seems like an intelligence issue some place (battery or UPS). Did you ever end up getting a replacement battery in there to try (i know you mentioned it initially when you spoke to support)?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:14 AM

0 Likes
0
1323
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:14 AM

1286_ups-about.jpg

The replacement battery never made it into the UPS as by the time it had arrived, the UPS was behaving itself, so we sent it back to avoid being charged for it.

I have been on to support this morning and sent them the logs. They said they would most likely send me another replacement battery, just awaiting a response to confirm.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:14 AM

0 Likes
0
1324
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:57 AM . Last Modified: ‎2024-03-13 12:14 AM

Alrighty.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of