SMT3000RM2UC error p.06

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMT3000RM2UC error p.06
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Jimbo99
Crewman Jimbo99
Crewman

Posted: ‎2022-08-20 03:27 AM

0 Likes
4
8675
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-20 03:27 AM

SMT3000RM2UC error p.06

I got a 3 month old SMT3000RM2UC that has an error p.06.  I disconnect the load and the power, still beeping. I held the off button to shut it down.  Added the power back; when turned on immediate p.06.  Any ideas?

 

Thanks...Jim

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
Jimbo99
Crewman Jimbo99
Crewman

Posted: ‎2022-08-25 06:02 AM

0 Likes
0
8602
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-25 06:02 AM

I guess this in not the place for support.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

JonPro
Commander JonPro Commander
Commander

Posted: ‎2022-08-25 06:13 AM

0 Likes
2
8598
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-25 06:13 AM

Hi @Jimbo99,

 

Thank you for using the SE Community.  Apologies for the late revert on this query.  I understand that your UPS is throwing a P.06 fault and you weren't able to recover from it after shutting it down.  Let me help you with this.

 

The P.06 fault on the UPS is also known as the AVR Relay Weld fault, would you happen to know if your site is having a fluctuating voltage that would cause the UPS to intermittently boost and/or trim the voltage?

 

You can perform a brain-dead and cold start on the UPS, to do this you may refer to the FAQ below that outlines the process.

 

How to perform a cold start and brain dead on Smart-UPS

  • Tags:
  • AVR Relay Weld
  • english
  • SMT3000RM2UC
Reply

Link copied. Please paste this link to share this article on your social media post.

Jimbo99
Crewman Jimbo99
Crewman

Posted: ‎2022-08-26 02:42 AM

In response to JonPro
0 Likes
1
8581
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-26 02:42 AM

Thanks for chiming in JonPro.  The site is remote for me so I will not be able to get there until Sunday.  I saw the video on the brain-dead and cold start. I'll give it a shot Sunday.

 

The building has had a lot of voltage fluctuating.  They have been flipping over to generator power, several time recently.  The mains coming in from the power company are being replaced and it's taking longer than expected.

 

I'll let you know how it goes.

 

Thanks...Jim

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

JonPro
Commander JonPro Commander
Commander

Posted: ‎2022-08-26 03:22 AM

In response to Jimbo99
0 Likes
0
8579
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-26 03:22 AM

Hi @Jimbo99 

 

Considering that the site does have unstable input voltage, might as well change the power quality/sensitivity of the UPS to a much lower setting.

 

To change these settings, please see the FAQs below.

What are the different sensitivity settings of a Smart-UPS? 

What are the Power Quality settings for an SMT or SMX Smart-UPS? 

  • Tags:
  • english
  • power quality
  • sensitivity
  • SMT3000RM2UC
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.