Hi everyone, new to this forum ... hope someone can help me out
My SMT 3000 appears to show an incorrect battery voltage. Now for example it shows 55,6 V where the batteries are only 49,2 V measured with my fluke .....
I have tried a couple of things like "brain dead"and "cold start" and even faking a battery replacement, but nothing will help.
Consequently, the unit thinks that the batteries are full and does not charge. (or rather, it applies 49,2 V and thinks it is drop charging)
Anyone any clue as where to look at ?
Many thanks ahead, Michael
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:58 AM . Last Modified: 2024-03-17 11:26 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:58 AM . Last Modified: 2024-03-17 11:26 PM
Hi Liam, thanks for reacting.
I did both, that is I measured both situations. Batteries in series but isolated from the unit, and connected. When connecting, the voltage does not change. The unit does discover the batteries and states a voltage that is around 6 Volts too high and says that the batteries are charged to 100%
What can be the case here? how does the unit measure the voltage of the batteries (and charger)
Thanks ahead, Michael
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:58 AM . Last Modified: 2024-03-17 11:26 PM
I had this and never found out why, in the end I replaced it.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:58 AM . Last Modified: 2024-03-17 11:26 PM
Hi Michael -
When you are checking the voltage with your fluke, are the batteries installed in the UPS or disconnected?
Liam
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:58 AM . Last Modified: 2024-03-17 11:26 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:58 AM . Last Modified: 2024-03-17 11:26 PM
Hi Liam, thanks for reacting.
I did both, that is I measured both situations. Batteries in series but isolated from the unit, and connected. When connecting, the voltage does not change. The unit does discover the batteries and states a voltage that is around 6 Volts too high and says that the batteries are charged to 100%
What can be the case here? how does the unit measure the voltage of the batteries (and charger)
Thanks ahead, Michael