SMT3000 No Input volatage

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMT3000 No Input volatage
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-07 11:42 PM . Last Modified: ‎2024-02-29 11:47 PM

0 Likes
5
3191
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:42 PM . Last Modified: ‎2024-02-29 11:47 PM

SMT3000 No Input volatage

I have an APC SmartUPS SMT3000.  The device has batteries from July 2017 and have a charge.  The onscreen menu reports there is no input voltage - I've used my voltmeter to check the plug (it's 120V, 30A circuit).  Is there any type of fuse or anything I can replace?

Besides the "no input voltage", the device passes self tests and reports the batteries have about 80% capacity.  The fan runs, can cycle through the on-screen menu just fine, just can't charge the batteries (and it won't give any output voltage either).  

I bought this device from an auction (paid $70 for it) so do not know much history about it.  It was supposed to have passed several factory tests, but who knows how valid the sheet was that was in the box.

Any repair options?  I live in the midwest.  

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-07 11:42 PM . Last Modified: ‎2024-02-29 11:47 PM

0 Likes
0
3193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:42 PM . Last Modified: ‎2024-02-29 11:47 PM

I cant see the labelling on the board and I don't know the transformers you talked about in your earlier response that theyre being serviced by one (splited) fuse. But looking at the board there are two onboard transformers. One should be DC powered while the other will be AC powered.

The board working on battery is an indication that the DC onboard transformer is receiving voltage. Check and confirm that the AC powered onboard  transformer is receiving voltage.

That transformer powers an IC that tell the UPS that there's online voltage.

Do that check and let me know your findings.

Regards.

Sammie

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-07-07 11:42 PM . Last Modified: ‎2024-02-29 11:47 PM

0 Likes
0
3193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:42 PM . Last Modified: ‎2024-02-29 11:47 PM

If you can, trace the voltage from input and locate where it ends then try to know what's making it end where its ending. On the other hand, check F1 and F2 (fuse) and be sure they're intact. Those fuse sends voltage voltage to T1 and T2 (transformers).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-07 11:42 PM . Last Modified: ‎2024-02-29 11:47 PM

0 Likes
0
3193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:42 PM . Last Modified: ‎2024-02-29 11:47 PM

Any idea where the fuses are located?  I found one that is 100A 32V.  My voltmeter checks it out ok with the continuity test (i.e. - it beeps when I put a tester on on side and the other side of the fuse).  This fuse is for the transformers inside.

This fuse has two black wires that do a y-split and go to each transformer.  Assuming this fuse covers both transformers.

I've pulled the large circuit board out and have done a visual inspection.  I see a place on the board that talks about using fuses, but there is nothing on the board there.  

I've also examined the power supply board (where the electric comes in).  It checks out fine and seems to be supplying voltage the the main board.

There is another circuit board that accepts an expansion card.  I didn't see any fuses on it.  The expansion port should be empty (didn't check but it looks like a "blank" plastic insert is inside of it.)

Schematics would be nice.  I know these are not supposed to be user serviceable, but I doubt I have any warranty as I bought this from an auction (and now that I've taken some of the boards out.)

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-07 11:42 PM . Last Modified: ‎2024-02-29 11:47 PM

0 Likes
0
3193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:42 PM . Last Modified: ‎2024-02-29 11:47 PM

Send a clear snapshot of the board showing the label of the components let me see if I can explain somethings using the picture.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-07 11:42 PM . Last Modified: ‎2024-02-29 11:47 PM

0 Likes
0
3193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:42 PM . Last Modified: ‎2024-02-29 11:47 PM

Circuit boardIn6Hy1xfwXHVLNuonSkTrg%3D%3D.jpegIn6Hy1xfwXHVLNuonSkTrg%3D%3D.jpeg

https://imgur.com/a/brbvT

Hopefully this works.  I reduced the image size so it could upload.  The voltage in starts in the lower left of the circuit board.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-07 11:42 PM . Last Modified: ‎2024-02-29 11:47 PM

0 Likes
0
3194
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 11:42 PM . Last Modified: ‎2024-02-29 11:47 PM

I cant see the labelling on the board and I don't know the transformers you talked about in your earlier response that theyre being serviced by one (splited) fuse. But looking at the board there are two onboard transformers. One should be DC powered while the other will be AC powered.

The board working on battery is an indication that the DC onboard transformer is receiving voltage. Check and confirm that the AC powered onboard  transformer is receiving voltage.

That transformer powers an IC that tell the UPS that there's online voltage.

Do that check and let me know your findings.

Regards.

Sammie

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of