SMT2200c w/AP9640 Simple Shutdown config help
So configuring a couple SMT2200c w/AP9640 and just want to confirm what we did to get a simple run all outlets until there is 30min runtime available and start to shutdown servers, restart after power is restored.
We set PCNS to shutdown on runtime exceeded and battery discharged with a delay of 300 seconds.
I followed an article by @BillP and hoping to validate without a lot of testing downtime.