SMT2200RMI2U AVR functionality

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMT2200RMI2U AVR functionality
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
oit1976
Crewman oit1976
Crewman

Posted: ‎2025-04-05 03:46 AM . Last Modified: ‎2025-04-05 05:12 AM

0 Likes
6
204
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-05 03:46 AM . Last Modified: ‎2025-04-05 05:12 AM

SMT2200RMI2U AVR functionality

Hi! I have an SMT2200RMI2U, s/n AS1834140244.

I have configured it to output a 220V voltage, but its output voltage is the same as the input.

Is it possible to configure this model to stabilize voltage? According to manual, it has an AVR.

oit1976_0-1743849765470.png

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Teken
Janeway Teken
Janeway

Posted: ‎2025-04-07 05:48 AM

0 Likes
2
181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-07 05:48 AM

If you’re looking for a fully regulated output voltage than a double conversion (On Line) UPS is the only option. 

As you noted your APC SMT (Line Interactive) UPS output follows the input voltage to a certain degree.

 

You can adjust the upper and lower transfer voltage for a tighter operating range. This is what impacts the AVR circuit in the system.

 

Lastly, just for clarity sake changing the power quality setting from normal to whatever option determines when the system will go into battery only mode.

 

This provides the cleanest output power while sacrificing battery longevity (service life).

 

Questions Ask - If not, and this answered your query please do mark this reply as a solution. So it may help the next person asking the same. 👍

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Teken
Janeway Teken
Janeway

Posted: ‎2025-04-07 05:48 AM

0 Likes
2
182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-07 05:48 AM

If you’re looking for a fully regulated output voltage than a double conversion (On Line) UPS is the only option. 

As you noted your APC SMT (Line Interactive) UPS output follows the input voltage to a certain degree.

 

You can adjust the upper and lower transfer voltage for a tighter operating range. This is what impacts the AVR circuit in the system.

 

Lastly, just for clarity sake changing the power quality setting from normal to whatever option determines when the system will go into battery only mode.

 

This provides the cleanest output power while sacrificing battery longevity (service life).

 

Questions Ask - If not, and this answered your query please do mark this reply as a solution. So it may help the next person asking the same. 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

oit1976
Crewman oit1976
Crewman

Posted: ‎2025-04-07 02:13 PM

In response to Teken
0 Likes
1
148
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-07 02:13 PM

Thank you for response, Teken.

Strange, but sua2200rmi2u seems to have such voltage regulation. is it a different type of ups? i always thought that it is also line-interactive. or did they remove voltage regulation from smt2200rmi2u?

oit1976_0-1744060380893.png

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Janeway Teken
Janeway

Posted: ‎2025-04-08 04:37 AM

In response to oit1976
0 Likes
0
147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-08 04:37 AM

Both systems are pure sine wave output but are also line interactive topology.

 

You’re correct some of the older hardware provided a tighter input / output voltage.


As noted the only option for you is to adjust the upper / lower transfer voltage which controls when the system will go into AVR mode.

 

Keep in mind when the system goes into AVR mode the output will not be whatever the line voltage would typically be say 220 / 230 / 240 in the UK / EU.

 

Upon AVR Trim / Boost expect to see a minimum of 10 VAC in change. All of which is within operating range of all electronics.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

oit1976
Crewman oit1976
Crewman

Posted: ‎2025-04-08 05:44 AM

0 Likes
1
136
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-08 05:44 AM

So, at present day the only choice we have is the on-line topology devices, if we want fully working AVR (in case of APC/SE at least), as you mentioned earlier.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Janeway Teken
Janeway

Posted: ‎2025-04-08 07:42 AM

In response to oit1976
0 Likes
0
134
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-08 07:42 AM

If your expectation and goal is to see (say a nominal input voltage of 220 VAC) and the same (220 VAC) at the output.

 

Then (Yes), a On Line Double Conversion UPS is required if the input swings high / low.

 

Show me the event, data, ups log for this specific unit. As I would like to see what the input vs output voltage is that’s giving you such concern?!?

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

oit1976
Crewman oit1976
Crewman

Posted: ‎2025-04-09 03:50 AM

0 Likes
0
107
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-09 03:50 AM

Thank you for clarifying the matter. You are right, in most cases there is probably no matter for concern. I just wanted to make sure the device was behaving correctly.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of