Morning,
I have several SMT2200RM2UC (ID1015) SKUs I'm trying to update firmware on.
They are currently showing: Firmware Revision UPS 04.6 (ID1015). I'm trying to update using the latest firmware of SMT1015UPS_18-0.enc through the NMC3 but keep getting a refused message.
I'm assuming it's too large of a firmware jump but I'm having a hard time finding out what I need to update to first. Can someone please advise?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-30 05:50 AM
The ability to upgrade the UPS firmware via the NMC was disabled in v04.6. Your options are directly serial & USB.
https://download.se.com/files?p_File_Name=SMT1015_firmware_release_notes.pdf
Once the system has been updated to v18 the ability to upgrade the system via NMC will be restored.
You will also have the ability to enable / disable the communication method via the LCD Menu to offer stronger security protection.
Please read, follow, and understand all requirements and precautions before proceeding as outlined in this APC FAQ:
https://www.apc.com/us/en/faqs/FA164737/
Questions Ask . . . 👍
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-30 05:50 AM
The ability to upgrade the UPS firmware via the NMC was disabled in v04.6. Your options are directly serial & USB.
https://download.se.com/files?p_File_Name=SMT1015_firmware_release_notes.pdf
Once the system has been updated to v18 the ability to upgrade the system via NMC will be restored.
You will also have the ability to enable / disable the communication method via the LCD Menu to offer stronger security protection.
Please read, follow, and understand all requirements and precautions before proceeding as outlined in this APC FAQ:
https://www.apc.com/us/en/faqs/FA164737/
Questions Ask . . . 👍
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-30 11:59 AM
Thanks. I forgot about that.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of