Hi, I have an SMT22001, the battery are 100% charged, actually the power in output is 158W, but the power consumed by the UPS il 330W.
Is this normal?
Thank you
Livio
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:34 AM . Last Modified: 2024-03-15 04:56 AM
Hi Livio,
That might be a little high but it would have a lot to do with environmental factors, another thing to note is that with the exception of backup UPSs then all UPS have much lower power efficiency at low loads. So in this case a smaller UPS would probably provide you with more efficiency.
-Gavan
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:34 AM . Last Modified: 2024-03-15 04:56 AM
Thank you.